Configuring Access Expert to use PIV cards with AX-SSC using AC1 downstream devices

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Configuring Access Expert to use PIV cards with AX-SSC using AC1 downstream devices
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • AbeMeran
    AbeMeran

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
87 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Configuring Access Expert to use PIV cards with AX-SSC using AC1 downstream devices

Captain AbeMeran Captain
‎2025-11-02 06:50 PM

on ‎2025-11-02 06:50 PM

Issue

Guidance is needed to enable reading of PIV (FIPS-201) cards using the AX-SSC controller and AC1 downstream devices within EcoStruxure Access Expert.

Product Line

EcoStruxure Access Expert

Environment

AX-SSC

Cause

Sites migrating from Continuum systems require a clear, step-by-step process to ensure PIV cards are properly enrolled and recognized in Access Expert.

Resolution

What is FASC-N?

FASC-N stands for Federal Agency Smart Credential Number. It is a 25-byte (200-bit) identifier embedded in PIV cards, used to uniquely identify the cardholder across federal systems. It is composed of multiple fields, including:

  • Agency Code
  • System Code
  • Credential Number
  • Credential Series
  • Credential Issue
  • Person Identifier
  • Organizational Category
  • Organizational ID
  • Person Org Association

These fields are encoded using Packed Binary Coded Decimal (BCD) with odd parity, and together form a unique string used by access control systems to authenticate users.

Understanding the FASC-N Structure

In the Continuum Personnel object below, the fields highlighted are those that make up the FASC-N

AbePIVAnotated.JPG

The PIV enrollment tool generates a character string when a card is presented. For example:

32013733334894141152472674132011

This string is composed of the following FASC-N fields:

Field Value
Agency Code 3201
System Code 3733
Credential Number 334894
Credential Series 1
Credential Issue 4
Person Identifier 1152472674
Organizational Category 1
Organizational ID 3201
Person Org Association 1

Note: If no enrollment tool is available, manually concatenate these fields in the order shown to create the FASC-N string.


Configuration Steps

1. Card Format Setup

Configure the card format in Access Expert as follows:

  • Card Format Type: Standard
  • Bit Length: 128
  • Large Encoded Card Number: ✅ Checked
  • Convert 200 FASCN Bit to 128 Bit: ✅ Checked
  • Card Number Starting Bit: 0
  • Card Number Bit Length: 128

    CardFormat.JPG


2. AX-SSC Controller Configuration

  • Ensure Enable Large Encoded Card Number is checked.
  • Assign the card format created in Step 1 to the controller.

    AX-SSC.JPG


3. Person Object Configuration

  • Navigate to Add Card Assignments.

    Galileo2.JPG

  • Paste the full FASC-N string into the Display Card Number field. This will auto-populate the Encoded Card Number field.

  • Since the Encoded Card Number field is limited to 16 characters, truncate the string from the end until only 16 characters remain.

  • Paste the full FASC-N string into the Hex Value field.

    CardAssignment.JPG

    ⚠️ Although labeled "Hex Value", enter the string as decimal digits.

  • Save the Person object.


Additional Notes

  • Only the editors mentioned above require configuration for PIV card support.
  • Editors such as Reader, Access Level, etc., do not need special configuration for PIV cards.
Labels (1)
Labels:
  • EcoStruxure Access Expert
Tags (1)
  • Find more articles tagged with:
  • AbeMeran25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore