Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Can BACnet/IP Use TCP and what Firewall Whitelisting is Required

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Can BACnet/IP Use TCP and what Firewall Whitelisting is Required
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
266 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Can BACnet/IP Use TCP and what Firewall Whitelisting is Required

RobertAndriolo Champion
‎2026-07-12 05:40 PM

on ‎2026-07-12 05:40 PM

Issue

Clarification is required on whether BACnet/IP communication for MP-C, AS-P, and EcoStruxure Building Operation can use TCP instead of UDP, and which devices must be whitelisted in firewall configurations.

There may also be uncertainty regarding BACnet/SC support and communication paths for BACnet/IP Controllers, such as the MP-C, RP-C range of devices, and third-party devices.

Product Line

EcoStruxure Building Operation

Environment

  • EcoStruxure Building Operation (EBO) 3.2 or later

  • Automation Servers

  • BACnet/IP, BACnet/SC, BACnet MS/TP
  • SpaceLogic MP‑C / MP‑C Pro / MP‑V
  • SpaceLogic RP‑C / RP‑C Pro / RP‑V

Cause

BACnet/IP communication runs over UDP and does not support TCP. BACnet/SC is a separate communication method that uses TCP-based secure connections. Additionally, standard EcoStruxure Building Operation communication routes MP-C traffic through the AS-P rather than directly to the Enterprise Server.

Resolution

BACnet/IP must remain UDP-based and cannot be changed to operate over TCP. If TCP-based communication is required, BACnet/SC must be used as it provides TLS-encrypted WebSocket communication over TCP and requires certificate-based trust between devices.

For firewall configuration:

  • For BACnet/SC: All devices that need to communicate with the BACnet/SC hub must be allowed through the firewall, as communication uses a hub-and-spoke architecture with outbound connections to the hub.
  • For standard EcoStruxure Building Operation communication (non-BACnet/SC), MP-C devices communicate via the AS-P, so only the AS-P needs to be whitelisted on the Enterprise Server firewall.

If a third-party device does not support BACnet/SC, it cannot participate in BACnet/SC communication.

 

Other considerations: 

Before recommending firewall rules or BACnet/SC adoption, ensure the customer's complete network and security requirements are understood. Requests for "whitelisting" or replacing UDP with TCP can sometimes indicate a broader network segmentation or security requirement rather than a BACnet protocol limitation.

Consider gathering additional information regarding:

  • The overall system architecture and communication paths.
  • The specific security or compliance requirement driving the request.
  • Whether network segmentation, isolation, or traffic restriction is the primary objective.

Alternative approaches that may satisfy the requirement include:

  • Network switch-based access controls, such as MAC address filtering, port security, or other switch-level whitelisting mechanisms.
  • VLAN segmentation to isolate BACnet/IP networks, including secondary or site-specific BACnet networks.
  • Deploying edge servers with multiple network interfaces, where a secondary BACnet network can be connected through a dedicated interface or VLAN.
  • Isolating the Building Management System (BMS) / Operational Technology (OT) network within the network infrastructure rather than relying solely on host-based firewall restrictions.

Understanding the customer's full architectural requirements helps ensure the most appropriate network design is recommended rather than focusing only on protocol-level configuration options.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • RobertAndriolo26
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore