Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Building Advisor Data Mixing Issues After Adding, Cloning, or Detaching a Top Server

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Advisor Data Mixing Issues After Adding, Cloning, or Detaching a Top Server
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Katha
    Katha

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
203 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Building Advisor Data Mixing Issues After Adding, Cloning, or Detaching a Top Server

Katha Troubleshooter
‎2026-09-03 11:15 PM

Issue

Server data may be combined in Building Advisor if a server connected to Building Advisor is cloned or detached without first disabling Cloud Connectivity (Cloud Plugin) and resetting its System ID. This can result in duplicate System IDs and incorrect data associations between servers.

Product Line

EcoStruxure Building Advisor, EcoStruxure Building Operation

Environment

  • EcoStruxure Building Operation Enterprise Server (ES)
  • Enterprise Central (EC)
  • EcoStruxure Building Advisor
  • Cloud Connectivity (Cloud Plugin)

Cause

Cloud Connectivity (Cloud Plugin) was not disabled, and the System ID was not reset before the server was cloned or detached.
As a result, the new server retained the original server's identification, which can lead to duplicate System IDs and combined server data in Building Advisor.

 

Resolution

 

Identifier terminology: In EcoStruxure Building Operation, the identifier is displayed as Server Id.
In the tracelog, the same identifier is shown as sysID. Because the tracelog provides the most accurate and current value, this article refers to it as the System ID.

The System identifier field shown in EcoStruxure Building Operation is a different value. Although it may be used when connecting a server to the Building Advisor Portal, it is not used in this cloning or detaching procedure.
Do not reset or modify the System identifier field for this process.

Before adding a new top server, cloning a server, or detaching a server connected to Building Advisor:

 

  1. If Cloud Agent is installed on the server, review the referenced article and complete the Cloud Agent removal procedure before continuing with the server modification activities
    How to remove Cloud Agent Components Before Performing Server Changes 

  2. Disable Cloud Connectivity (Cloud Plugin)
  3. Reset the Server Id shown in EcoStruxure Building Operation. This is the value identified as sysID in the tracelog and is referred to as the System ID in this article.

    Katha_1-1788448370781.png
    Figure 1. Reset the value labeled Server Id. Do not modify the System identifier field for this procedure.
  4. Perform the server architecture change, such as adding a new top server, cloning the server, or detaching the server.

 

Resetting the Server Id/System ID allows the new server to generate a unique identifier and establish its own Building Advisor registration. The System identifier field is not part of this procedure.

Following this procedure helps prevent duplicate System IDs and prevents data from multiple servers from being combined in Building Advisor. This is especially important when the servers belong to different customers.

If a server was cloned, detached, or a new top server was added before Cloud Connectivity was disabled and the System ID was reset, open a PSS ticket for assistance with separating the server data.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • KatharineVasquez26
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore