Issue
Product Line
TAC IA SeriesEnvironment
- Building Operation Automation Server (AS, AS-P)
- MNL controller
- WorkPlace Tech Editor
- Building Operation WorkStation
Warning
Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support Services for assistance.
Cause
Resolution
Steps to Assign the Correct Application
-
Confirm Availability of the Correct Application Make sure the correct application file exists in the WorkPlace Tech Editor application list. If not, import or create it before proceeding.
-
Locate the MNL Device in the System Tree Expand the Building Operation System Tree to view the target MNL controller and its associated Application object.
-
Delete the Existing Application Right-click the Application object under the MNL controller and select Delete.
-
Assign the Correct Application
- Right-click the MNL controller.
- Navigate to MNL → Assign Application.
- Select the correct application from the WorkPlace Tech Editor application list.
-
Download the Application to the Controller
- Right-click the MNL controller again.
- Select MNL → Download Application to push the new application to the device.