AS-B upgrade intermittently fails with timeout and download errors
Select a Country
  • AS-B upgrade intermittently fails with timeout and download errors
  • Jonas_Brissman
    Jonas_Brissman
Jonas_Brissman Champion
‎2026-08-20 02:46 PM
on ‎2026-08-20 02:46 PM
During upgrades of AS-B controllers, some controllers upgrade successfully while others fail multiple times before eventually succeeding. Reported errors include timeout messages, download failures and connection loss during file transfer. In some cases, the controller became unresponsive after a failed upgrade and required recovery before another upgrade attempt.
Automation Server Bundled(AS-B)
Finding from the investigation was that a process timed out because an operation on the AS-B side was taking too long to complete.
Recommendation if similar issues is seen.
  • Perform a power cycle of the AS-B before the upgrade.
  • Running the upgrade with the AS-B disconnected from the network and field bus connections where possible.
  • If an upgrade fails, restore a backup taken before the upgrade and retry the process. .