i2 controllers firmware - Ecostruxure

Ask the Community

New users can ask questions related to our Communities, get tips and tricks on posting and commenting in forums, and solving challenges.

Solved
bwyatt
Crewman
Crewman
0 Likes
1
321

i2 controllers firmware - Ecostruxure

Hello,

 

I have run into some i2 controllers that seem to be stuck in bootloader mode (the version # reads 0). They fail when trying to "download all objects" giving me a BACnet module plugin error (they aren't BACnet controllers so I am lost on that). I would like to flash the firmware to see if I can get them back to normal operating capacity without having to replace the controllers all together, but I can't seem to find out how to flash firmware in Ecostruxure 2.0.4.83. These were all Andover Continuum sites with net controllers before a migration to Schneider AS-P controllers to replace the failing net controllers. 

 

Thank you,

 

BW


Accepted Solutions
CraigEl
Administrator Administrator
Administrator

Re: i2 controllers firmware - Ecostruxure

i2 firmware upgrade is not supported in EBO and it's not really a priority since no new i2 firmware has been released in over 10 years.

 

You can use the ROAM IO service tool to update i2 controllers one at a time. You may need to perform a hard reset on the i2 controller and then upgrade the firmware with ROAM IO.

See Answer In Context

Tags (1)
1 Reply 1
CraigEl
Administrator Administrator
Administrator

Re: i2 controllers firmware - Ecostruxure

i2 firmware upgrade is not supported in EBO and it's not really a priority since no new i2 firmware has been released in over 10 years.

 

You can use the ROAM IO service tool to update i2 controllers one at a time. You may need to perform a hard reset on the i2 controller and then upgrade the firmware with ROAM IO.