[PME8.1][Hotfix] VIP

Archives: Power Management Systems

JanetM
Janeway Janeway
Janeway

[PME8.1][Hotfix] VIP

This hot fix addresses the following VIP issues. It is for PME 8.1 only.

1. The VIP Data Monitor module events were processd incorrectly. Both ON and OFF transitions generate independent alarms visible in the Active Alarms page in the Alarms web application. The hotfix reverts the VIP Data monitor module back to pre-PME8 behaviour, i.e. the Data Monitor module transitions are not treated like alarms, but rather as simple unary events

.

2. The VIP Database Import module would time out on queries that take longer than 30 seconds. The VIP now uses the IONConnectionTimeout registry setting to set the timeout (60 seconds by default)

3. The VIP would interpret large 16 bit values coming from an OPC client incorrectly. The VIP will now interpret these values correctly.