Done

Archives: Power Management Systems

Solved
sesa101974_brid
Schneider Alumni (Retired)
Schneider Alumni (Retired)

Done


Done


Accepted Solutions
Kevin_Huang
Spock Spock
Spock

Re: Backup, Restore Data PME 8.1, 8.2

Before you restore a PME database backup, you will have to first stop all PME services which includes all the ApplicationModules services and ION services.  You can restart the services again after database restore is done.

If you have the .bak file, you can right click on Databases and then select Restore Files and Filegroups... in SQL Management Studio

Here is a Microsoft Doc on how to restore a database backup.  Restore a Database Backup Using SSMS | Microsoft Docs

NOTE: above covers only restoring PME database backups from the same server.  If you are restoring PME database backups from a different server, system may not work after the database restored.



Kevin Huang
PME Global Offer Manager

Click here to learn more on how PME helps you improve electrical safety, power reliability, operation efficiency and regulation compliance of your facility.

See Answer In Context

8 Replies 8
sesa101974_brid
Schneider Alumni (Retired)
Schneider Alumni (Retired)
0 Likes
0
24

Re: Backup, Restore Data PME 8.1, 8.2

Help me? Please

Kevin_Huang
Spock Spock
Spock

Re: Backup, Restore Data PME 8.1, 8.2

[PME8.2][Tool] Configuration Manager 2.1.0 backs up and restores PME configuration including databases. 

If you have backups of your SQL databases (.bak files), you can restore them in SQL Management Studio.



Kevin Huang
PME Global Offer Manager

Click here to learn more on how PME helps you improve electrical safety, power reliability, operation efficiency and regulation compliance of your facility.
sesa101974_brid
Schneider Alumni (Retired)
Schneider Alumni (Retired)
0 Likes
5
24

Re: Backup, Restore Data PME 8.1, 8.2

Hi Huang,

Thanks for your support.

So, If i backed up SQL database. Can you instruction for me step by step or share documents restore in SQL Management Studio

Thanks Huang

Kevin_Huang
Spock Spock
Spock

Re: Backup, Restore Data PME 8.1, 8.2

Before you restore a PME database backup, you will have to first stop all PME services which includes all the ApplicationModules services and ION services.  You can restart the services again after database restore is done.

If you have the .bak file, you can right click on Databases and then select Restore Files and Filegroups... in SQL Management Studio

Here is a Microsoft Doc on how to restore a database backup.  Restore a Database Backup Using SSMS | Microsoft Docs

NOTE: above covers only restoring PME database backups from the same server.  If you are restoring PME database backups from a different server, system may not work after the database restored.



Kevin Huang
PME Global Offer Manager

Click here to learn more on how PME helps you improve electrical safety, power reliability, operation efficiency and regulation compliance of your facility.
sesa101974_brid
Schneider Alumni (Retired)
Schneider Alumni (Retired)
0 Likes
2
24

Re: Backup, Restore Data PME 8.1, 8.2

Hi Huang,

Thanks very much. You really great.

But You can instruction back up in SQL to create file .bak

Thanks Huang.

Kevin_Huang
Spock Spock
Spock

Re: Backup, Restore Data PME 8.1, 8.2

Create a Full Database Backup (SQL Server) | Microsoft Docs

You may also use the Configuration Manager Tool to back up your entire system (configuration and databases).  I think the tool creates .bak files from the PME databases.



Kevin Huang
PME Global Offer Manager

Click here to learn more on how PME helps you improve electrical safety, power reliability, operation efficiency and regulation compliance of your facility.
sesa101974_brid
Schneider Alumni (Retired)
Schneider Alumni (Retired)
0 Likes
0
24

Re: Backup, Restore Data PME 8.1, 8.2

Hi Huang,

Hi. Thanks Huang, You are pro.

sesa101974_brid
Schneider Alumni (Retired)
Schneider Alumni (Retired)
0 Likes
0
24

Re: Backup, Restore Data PME 8.1, 8.2

Hi Huang,

I restore same instruction of you. But Fault appear with image below

Can you help me?

Restore Database Fail.PNG

Stop Service.PNG