Welcome to the new Schneider Electric Community
It's your place to connect with experts and peers, get continuous support, and share knowledge.
Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
82504members
350096posts
Unbalanced load correction through Symmetra PX UPS.
Archives: Power Distribution
Adam_Harding
Crewman
Crewman
What is the expected correction through a Symmetra PX UPS for an extreme unbalanced load seen downstream of the UPS.
As an example using a 250kW Symmetra PX equipped with 225kW of power modules it was noted that imbalance of 0%, 0%, 25% (A,B,C phases) saw correction occur only on the A and C phase upstream of the UPS.
Similar results were recorded for 50%,50%,100% (A,B,C phases).
When one phase is loaded considerably heavier, is it expected that the correction through the UPS (double conversion) would be shared mostly between 2 phases and not corrected equally across 3 phases?
Thanks!
Adam Harding
Arup - Hong Kong
3 Replies 3
AlexandreBoulet
Administrator Administrator
Re: Unbalanced load correction through Symmetra PX UPS.
@AldebaranLopez  can you help with this question?
Alexandre Boulet
Schneider Electric - Exchange Launch Leader
Commander Commander
Commander
@Adam_Harding ,
Sorry for any delay in responding to your post but if this is specifically a UPS question, this forum is not the best place to look for help. If you need immediate help with a 3 phase UPS, I always suggest contacting your local support directly. If you still want forum help, I suggest using the
3 phase section in the APC forums here:
https://forums.apc.com/
more specifically:
https://forums.apc.com/spaces/8/data-center-facility-3-phase-ups/overview
If the UPS itself is not seeing an issue or if the question is more about how DCE, DCO, ITE, or ITA are seeing this asset, then please be more specific about how we can assist with those softwares as this forum is more specific to those products. Also, if it is specific to the monitoring software, please make sure you indicate how the UPS would appear to be working OK but how the software would appear to be working improperly.
Thank you,
Steve.
AldebaranLopez
Ensign Ensign
Ensign
Hello Adam,
see a FAAT test made on SymPX300kVA with 2 phases at 50% and one at 100%. Upstream, at the input  the current is almost balanced.
Alejandro Aldebaran Lopez
Channel Director, Commercial & Industrial; Secure Power Division