Connecting a C20 Camera and 13ZD lens to a NET5401T Encoder

Archives: Industrial Automation and Control

Solved
alex_murray
Crewman
Crewman
0 Likes
3
145

Connecting a C20 Camera and 13ZD lens to a NET5401T Encoder

Hi All,

I am trying to connect a Pelco C20-DW-5X analogue camera with a 13ZD6X10P lens to a NET5401T Encoder. We have a coaxial cable between the NET5401T Encoder and the camera/lens (no separate RS422 or Pelco P/D available) so we need to use coaxitron to communicate between the NET5401T and the camera/lens.

My understanding of Coaxitron is that you can only communicate to one device (i.e. only NET5401T to camera, not NET5401T to multiple cameras) so if we install a ERD2000 to control the lens we would loose the ability to communicate with the camera, is this correct? Also the lens has zoom and focus presets which we would like to utilize, is the CX9000 receiver capable of controlling lens presets?

If neither the ERD2000 or CX9000 is suitable, is there any solution that would allow us to control both the C20-DW-5X camera and 13ZD6X10P lens via Coaxitron only and have access to the lens Zoom and Focus presets too?

Any help would be much appreciated.


Accepted Solutions
Kly
Sisko
Sisko

Re: Connecting a C20 Camera and 13ZD lens to a NET5401T Encoder

Hi, again. You can control Presets through CX9000. In your case CX9000 is the only solution. You will be able to control Lens and Pan/Tilt system if you use it, but Camera Menus problem still exists. I didnt try CX9000 by myself so i dnt know whether you will be able to run Camera menus.

You need Pelco Support Team answer for this.

See Answer In Context

3 Replies 3
Kly
Sisko
Sisko

Re: Connecting a C20 Camera and 13ZD lens to a NET5401T Encoder

Hi, again. You can control Presets through CX9000. In your case CX9000 is the only solution. You will be able to control Lens and Pan/Tilt system if you use it, but Camera Menus problem still exists. I didnt try CX9000 by myself so i dnt know whether you will be able to run Camera menus.

You need Pelco Support Team answer for this.

alex_murray
Crewman
Crewman
0 Likes
1
63

Re: Connecting a C20 Camera and 13ZD lens to a NET5401T Encoder

I'll get in contact with Pelco and let you know what they say.

Thanks Sergij

alex_murray
Crewman
Crewman
0 Likes
0
63

Re: Connecting a C20 Camera and 13ZD lens to a NET5401T Encoder

According to Pelco Tech Support, we can't both control a C20-DW-5X analogue camera and 13ZD6X10P lens at the same time with coaxitron.

Apparently you can only control the camera, or the lens via the same coaxial cable.

See email trail below:

"

On Thu, May 16, 2013 at 3:44 PM, Singh, Rajender <rajender.singh@schneider-electric.com> wrote:

    Hi Alex,

    

    Please see the response from Peter as below; thanks, Raj

    

    From: Gorey, Peter

    Sent: Thursday, May 16, 2013 3:18 PM

    To: Singh, Rajender

    Subject: RE: SR# 2-100111914 Customer Care on Pelco.com

    

    Hi Raj,

    

    The Coaxitron will be sent to the IRD/ERD to provide voltage outputs to drive any pan/tilt device or attached lens.

    

    It should not pass Coaxitron through to the C20 itself, otherwise when navigating the camera menus, it would also trigger the pan/tilt and lens actions and vice versa.  It is not an integrated camera solution like our Esprit platform for example where the pan/tilt/zoom system knows the camera is in the menu and deactivates all motorised control until the menu is exited.

    

    Therefore, to access the C20 menus if connected to an IRD/ERD, the user would need to press the buttons on the rear of the camera.

    

    Cheers,

    

    ____________________________________________________________________________________

    

    Peter Gorey  | Pelco by Schneider Electric   |   Australia-New Zealand  |   National Applications Sales Engineer

    Phone: +61-2-9125 9310  |   Fax: +61-2-9889-4327  |   Direct: +61-2-9125 9316  |   Mob: +61 414 088 666

    Email: peter.gorey@schneider-electric.com   |   Site: www.pelco.com  |   Address: Level 3 / 78 Waterloo Road, Macquarie Park, NSW 2113 AUSTRALIA

    *** Please consider the environment before printing this e-mail

    

    

    

    From: Singh, Rajender

    Sent: Thursday, 16 May 2013 2:30 PM

    To: Gorey, Peter

    Subject: FW: SR# 2-100111914 Customer Care on Pelco.com

    

    Hi Peter,

    

    Can you please help with this? Thanks, Raj

    

    Sent: Thursday, May 16, 2013 2:30 PM

    To: Singh, Rajender

    Subject: Re: SR# 2-100111914 Customer Care on Pelco.com

    

    Hi Raj,

    Thanks for the response.

    The C20 camera has an inbuilt menu that is accessible via coaxitron to control things such as contrast, lightness, iris, etc. I am concerned that if I connect the camera and lens to a ERD2000/2200 that I may not be able to access the camera menus.

    Will I be able to both control the 13ZD lens, and access the C20 camera menus at the same time using the ERD2000?

    Thanks,

    Alex

    

    

    On Thu, May 16, 2013 at 1:45 PM, Singh, Rajender <rajender.singh@schneider-electric.com> wrote:

    Hi Alex,

    

    My sincere apologies for the late response, the use of the ER2000/2200 will work fine as coaxitron needs video signals in order to work. This means that there is no “loss of control” over the C20 camera because the C20 camera is NOT controllable (PTZ) camera.

    

    Thanks, Raj

    +61 448520191

    

    

    From: Technical Support Internet e-mail

    Sent: Wednesday, May 15, 2013 12:53 AM

    Cc: Technical Support Internet e-mail; Wang, Robin; Singh, Rajender; Fong, Raymond

    Subject: RE: SR# 2-100111914 Customer Care on Pelco.com

    

    Hello Alex,

    

       Your contact requests have been received and the links you have been using on Pelco.com to create requests are still valid. Each and every one of your requests have been received and reviewed and our team in Australia have been notified.

    

       Due to the way in which Technical Support through Schneider Electric is structured, each region has a Technical Support office for proper support. At this time, I do not know why you have not received word back from Pelco Australia, but, I can tell you that your requests are in their hands at this time.

    

    

    Pelco Australia,

    

       May you please assist Alex with his request for support of the 13ZD lens control through a NET5401T?

    

    

    Best regards,

    

    

    Katie Rutherford | Technical Support Specialist

    Pelco by Schneider Electric | 3500 Pelco Way | Clovis | California

    Tel: 1-800-289-9100 | TechSupport@pelco.com

    

    This message may contain privileged and confidential information intended only for the use of the addressee named above. If you are not the intended recipient of this message you are hereby notified that any use, distribution or reproduction of this message, partial or in its entirety, is prohibited.

    

    

    From: newsalert@schneider-electric.com [mailto:newsalert@schneider-electric.com]

    Sent: Monday, May 13, 2013 5:16 PM

    To: Technical Support Internet e-mail

    Cc: Webmaster

    Subject: Customer Care on Pelco.com

    

    URL feedback about specific webpage: http://www.pelco.com/sites/global/en/sales-and-support/faq/open_support.page Product feedback about specific Pelco product: Open a Support Case This is regarding: I want to report a bad link or a link that is not working properly Feedback: I have lodged many support requests through the Pelco website and no one has responded to any of them, is it still working? It was been over a week for some of the support requests!



"