b3 program stopped at line E but not go back to the specify line

Archives: Building Automation and Control

YangboLIU
Commander Commander
Commander
0 Likes
6
94

b3 program stopped at line E but not go back to the specify line

An issue puzzled me for a long time, the b3 program stopped at line E, but not go back to the specify line, the program code like below

Numeric input A

Numeric output B

line 1

if A is on then B=on else B=off

......

.......

Line E

state=enabled

go to 1

I guested the program go to line E because write value to another 3rd party device,  the program should go to line 1 but stopped at line E, the program state is enabled and status is running.

I never encountered this issue with Continuum b3 program, but do that with SBO b3 script program. .

Anyone can comments why the program does not go back?

Regards

Yangbo

6 Replies 6
Shannon_Balch
Schneider Alumni (Retired)
Schneider Alumni (Retired)
0 Likes
1
61

Re: b3 program stopped at line E but not go back to the specify line

Is this a fall-thru program or looping?

YangboLIU
Commander Commander
Commander
0 Likes
0
61

Re: b3 program stopped at line E but not go back to the specify line

It is a Looping program

Shannon_Balch
Schneider Alumni (Retired)
Schneider Alumni (Retired)
0 Likes
3
61

Re: b3 program stopped at line E but not go back to the specify line

Please reference the code below:

Numeric input A

Numeric output B

line 1

if A is on then B=on else B=off

Go to E

Line E

state=enabled

go to 1

You can change "Go to E" to "Go to 1" if you require the execution to be different.

YangboLIU
Commander Commander
Commander
0 Likes
2
61

Re: b3 program stopped at line E but not go back to the specify line

Hi

Thanks for reply, But I do not understand why "Go to E" is necessary? I think the program will go to line E  in default when there is a fault at any line.

AbeMeran
Commander Commander
Commander

Re: b3 program stopped at line E but not go back to the specify line

Not need for goto E, that happens automatically when the PE interpreter encounters an error.

Not need for state=enabled either, line E keeps the program from getting disabled, that's its purpose

The program appears to be stopped at line E, because if the condition that causes to go to E persists then it will constantly jump to E, typically you want to have a delay in E

Line E:

If ts > 30 then goto 1

YangboLIU
Commander Commander
Commander
0 Likes
0
61

Re: b3 program stopped at line E but not go back to the specify line

Thank you ,Abraham, I will have a try and change the code.

B.R

Yangbo