Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Citect 7.2 sp5

AVEVA Plant SCADA Forum

A support forum for AVEVA Plant SCADA (formerly Citect SCADA). Share new and exciting product information, connect, learn, and collaborate with the ecosystem of Plant SCADA Users. AVEVA Plant SCADA a reliable, flexible and high-performance Supervisory Control and Data Acquisition software solution for industrial process customers. This forum is to connect, share, learn and collaborate new and exciting product information. Feel free to join and share to your Ecosystem of Plant SCADA Users.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Industrial Automation
  • AVEVA Plant SCADA Forum
  • Re: Citect 7.2 sp5
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
olivier_vallee
olivier_vallee
39
Oncom
Oncom
6
stuartm
stuartm
2
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to AVEVA Plant SCADA Forum
Start a Topic
Smm206
Smm206
Explorer

Posted: ‎2024-06-07 10:54 PM

0 Likes
7
4140
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-07 10:54 PM

Citect 7.2 sp5

Hello

I am using Citect version 7.2 service pack 5 and Windows 7.

I have created a project. Currently, the project on the server is running without any issues. On the client side within the web browser, there are no problems and it runs in local mode. By local mode, I mean the local mode of the internal network. However, now I want to use two modems with public IPs as a bridge between these two systems. I have made the settings and set the modem on the server side to DMZ mode. The network is established and the two computers, the server and the client, can see each other. But when I run the project through the browser client, the project files are loaded and the project is executed. However, live data is not received and it operates offline. And after a few moments, it gives a hardware lock error. The firewall is turned off in Windows and on the modems. All ports are open.

I really don't know where the problem lies because the project works in local network mode without any special settings.

Please advise if someone has experience in this area.

Labels
  • Labels:
  • Plant SCADA Studio
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 7
olivier_vallee
olivier_vallee
Mentor

Posted: ‎2024-06-10 10:07 PM

0 Likes
1
4123
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-10 10:07 PM

Hi @Smm206 ,

This is a very interesting scenario. I'd suggest the following as a start:

1. Test you can ping IP address from both ends.

2. Telnet from client to server side on specific ports (2080, 2082, 2084, 2085 are default ports for Citect)

3. Use Wireshark in local, then try in the modem setup and see if any obvious differences with packet traffic.

4. Make sure to use IP Address in your project, as name resolution might not work over this type of network.

 

Also, see the Web Client help here:

https://gcsresource.aveva.com/plantscada/WebHelp/vijeo720/default.htm#Using_the_Web_Client.html

 

Wishing you the best of luck getting this working.


Kind regards

Olivier

Reply

Link copied. Please paste this link to share this article on your social media post.

Smm206
Smm206
Explorer

Posted: ‎2024-06-11 11:00 PM

In response to olivier_vallee
0 Likes
0
4093
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-11 11:00 PM

Hello

Thank you very much for your response.

I have rechecked these issues. The server modem is set to DMZ mode, and I have also disabled the firewalls on both the modem and the server to ensure a completely open path. Both the server and client systems can ping each other. I can even access the server via Remote Desktop from the client system, and I have shared a folder between the two systems.

Interestingly, when I make changes to the graphical pages in the server's Citect project, refreshing the project page in the client browser shows the latest graphical updates. However, no live data is displayed, and after a short while, a hardware lock error appears.

I have installed Telnet Client on the client side and Telnet Server on the server side. When I run:
```
telnet (Server IP)
```
from the client, the screen goes black, indicating that the connection is OK. The same happens for ports 2082 and 2085. However, for ports 2080 and 2084, I get the following error, even though the settings are the same and all firewalls are off:
```
Connecting To (Server IP)...Could not open connection to the host, on port 2080: Connect failed
```
I have even restarted the Telnet service on the server.

In a local network setting, there are no errors (software or hardware lock) between the server and client. When connected locally to the server, I enter the IP address (which is within the server's network range) in the browser without any issues. But when I try to do this through the modem network, I have to enter the modem's SIM card IP (which is in DMZ mode and port-forwarded to the server's local IP). I wonder if the issue is that the Citect software itself cannot establish a connection with the server, even though the network connection is fine.

Is there a specific configuration needed in Citect.ini? Because it works perfectly with the same settings in a local setup between the server and client. Or is there a particular setting required in IIS? Since the latest project update downloads on the client side, but no live data is displayed.

I apologize for the lengthy explanation; I really need to resolve this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

olivier_vallee
olivier_vallee
Mentor

Posted: ‎2024-06-12 08:36 PM

0 Likes
1
4068
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-12 08:36 PM

Hi @Smm206,

I'd recommend checking on the Server side, to make sure the expected ports are open. E.g. if running a RATIO system, make sure ports for Report, Alarm, Trend and IO are each open and in listening state (see info on "netstat" command on Google for help to do it).

I definitely think this is a networking issue, where the client process, doesn't know how to communicate with the Server as definied in the the project.

Please see this section of the help for informaiton on Address Forwarding:

https://gcsresource.aveva.com/plantscada/WebHelp/vijeo720/default.htm#../Subsystems/ParametersVijeoH...

I believe you need to configure this on the Citect.ini file on the Client side, and define the appropriate IP/Port that will allow any communications to go through to the Server side.

Let me know how you go.

Kind regards

Olivier

Reply

Link copied. Please paste this link to share this article on your social media post.

Smm206
Smm206
Explorer

Posted: ‎2024-06-15 08:49 PM

In response to olivier_vallee
0 Likes
0
4006
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-15 08:49 PM

scenario.png

 

Hello,

Thank you for your response.

I have checked everything. In the above picture, I have two scenarios:

1. In Scenario 1, the project works perfectly fine in the web client mode and communicates with the server effortlessly, without any additional configurations on the server, client, IIS, or modem.

2. However, in Scenario 2, when the communication between the client and server happens through two modems, unfortunately, the connection between the client and server becomes incomplete. The project downloads on the client-side, but it fails to establish a connection with the server.

Here are the steps I have taken:

- All firewalls on the server, client, and both modems are turned off.
- There are no restrictions between the client and server.
- I tested with Remote Desktop and shared folders between both systems, and there were no issues.
- I can ping between the two systems.
- The default ports for Citect are open, even with the firewalls turned off.

The only issue is the live communication between the client and server.

Please provide a solution to resolve this problem based on the picture.

Thank you.

Reply

Link copied. Please paste this link to share this article on your social media post.

olivier_vallee
olivier_vallee
Mentor

Posted: ‎2024-06-17 10:07 PM

0 Likes
0
3992
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-17 10:07 PM

Hi @Smm206,

It is difficult for me to suggest the solution, without deeper understanding of the network routing between the two sides. When you ping 192.168.8.3 from the client, you get a response? Could you also try TraceRT command from command prompt, to see what hops the route takes?

I've not personally setup a system like this, but if there is any Network Address or Port mapping that is going on, the Address Forwarding citect.ini parameter should help. But you would need to better understand the end IP and Port, that the Client should request, and set the parameters accordingly.

Finally, further clarity may be gained by running Wireshark on the client side. To understand what packets are being sent, and what is happening (e.g. is a connection being made or no ACKs coming back?).

I assume you also have 192.168.8.1 set as the Default Gateway on the client?

Kind regards

Olivier

Reply

Link copied. Please paste this link to share this article on your social media post.

Smm206
Smm206
Explorer

Posted: ‎2024-06-18 07:38 AM

0 Likes
1
3971
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-18 07:38 AM

Hello,

Thank you for your response.

In the local mode, the project runs without any issues by entering the IP address defined in the server project.

In the public network mode, I have placed the server-side modem in DMZ mode, so the server computer is identified on the public network with the public IP of the SIM card.

On the client computer browser in local mode, I enter the IP 192.168.8.3, and since the client computer's IP is in the same range as the server's IP, the connection is established easily.

However, in the public network mode, to access the server computer, I have to enter the public modem's IP on the server side. Due to the DMZ mode on the server-side modem, all traffic is directed to IP 192.168.8.3.

I feel that the problem is here because I am entering an IP from a different range, and while the IIS service sends the latest project update, the internal project source on the client side still works with IP 192.168.8.3, whereas the requests enter the server system via IP 110.50.30.9.

Perhaps I need to configure some settings in the IIS service on the server side or use the URLREWRITE service to redirect the requests to the address 192.168.8.3?

Please provide an example for address forwarding.

Reply

Link copied. Please paste this link to share this article on your social media post.

olivier_vallee
olivier_vallee
Mentor

Posted: ‎2024-06-19 09:39 PM

In response to Smm206
0 Likes
0
3961
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-19 09:39 PM

Hi @Smm206,

As previously communicated, you would need to define address forwarding parameters in the citect.ini on the Client side, with the following format:

[AddressForwarding]
<Cluster>.<ServerName>=<ipaddress>:<port>

So assuming you have the following defined in your project:
Cluster Name: Cluster1

I/O Server Name: IOServer1

Alarm Server Name: AlarmServer1

Report Server Name: ReportServer1

Trend Server Name: TrendServer1

 

You could try the following setting in your citect.ini on the client:

[AddressForwarding]
Cluster1.IOServer1=110.50.30.9:2082

Cluster1.AlarmServer1=110.50.30.9:2080

Cluster1.ReportServer1=110.50.30.9:2084

Cluster1.TrendServer1=110.50.30.9:2085

 

You could also try defining the machine name in the project configuraiton, for the network address (instead of IP Address). Then use an LMHOST file to direct to the IP 110.50.30.9.

Please also give Wireshark a try, it will help you understand what is happening at the packet level.

Kind regards

Olivier

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore