Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

regarding the storage of hundreds of units of a variety of APC batteries..

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: regarding the storage of hundreds of units of a variety of APC batteries..
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2151
Teken
Teken
152
Techie_apc
Techie_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
BillP
BillP Leader
Leader

Posted: ‎2021-06-30 12:09 AM . Last Modified: ‎2024-03-20 12:22 AM

0 Likes
2
1037
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:09 AM . Last Modified: ‎2024-03-20 12:22 AM

regarding the storage of hundreds of units of a variety of APC batteries..

I'm a logistician working for the US Army and we have a serious concern regarding the storage of hundreds of units of a variety of APC batteries, and we need an authoritative answer directly from the source. Because of scheduling issues, many of our batteries will not be deployed to where they need to go in time.  We're aware that these batteries lose their charge while sitting idle, and can permanently degrade after about 6 months with no charging. We're trying to avoid the catastrophe of having these batteries go bad before they're deployed.


So, could you please tell us what you know about the following:


1)  Do you have any more information (aside from what's stated on the website) regarding long-term battery storage?  (6-12 mos and possibly beyond.)

2)  We're aware that after about 6 months in normal temperatures, batteries should be "topped-off".  So, we're looking for means to charge them as easily as possible. 

To do so, is it required that they be placed/installed into the chassis that is designed for them?  Or, does APC offer (or know about) some sort of external charging solution that we can utilize to top off these batteries periodically while they are in storage?

If it helps, some of the batteries we have are:

Symmetra PX

RT192V RM Battery Pack 2 Rows

#143 / SMX120BP

#133

#43

Labels
  • Labels:
  • Universal Transfer Switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 12:09 AM . Last Modified: ‎2024-03-20 12:22 AM

0 Likes
0
1037
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:09 AM . Last Modified: ‎2024-03-20 12:22 AM

I work at a large Canadian University and deal with this issue myself. Angela N is correct there is a requirement to utilize the model of UPS these battery modules are manufactured for as a "charging base"; I don't know of any portable battery charging system that puts out the exact voltages required for the battery strings inside these models Eg 216 volts for the RT's and PX's, 48 volts or 136.5 volts for the SMX's etc. What I could suggest is that it would make the job of charging the SMX and RT modules in the field a bit easier if you purchased battery extender cables for the external battery cabinets for each model of UPS/RBC that you are dealing with, or have some custom cables made up for the individual modules using the correct flavor of Anderson connectors. That could allow you to avoid having to remove the external battery cabinets or even the modules themselves from their shipping cartons and/or at the very least maybe you won't have to install them inside the UPS. Cables for the external cabinets that are as long as 15 feet are available - see below. Also if you could come up with a way of bolting the smallest/lightest model of the particular UPS's required that use a particular model of replacement battery module and mount it to a caster base - or an upright dolley ? - with a long extension cord affixed so it could be rolled into place near the battery stock. APC actually makes an equipment cart for the RT UPS's that would be useful for that: http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=SURT013

Extender Cables for the SMX ups are here: http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=SMX040

Extender Cables for the RT ups are here: http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=SURT008

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
BillP Leader
Leader

Posted: ‎2021-06-30 12:09 AM . Last Modified: ‎2024-03-20 12:22 AM

0 Likes
0
1037
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:09 AM . Last Modified: ‎2024-03-20 12:22 AM

Hi!

I assume you meant you reviewed this knowledge base? -> http://www.schneider-electric.com/support/index?page=content&country=US〈=en&id=FA156516 I just wanted to provide it in case it was not what you found.

I found some information on charging regimen here in a white paper -> http://www.apc.com/whitepaper/?wp=39

As far as how to charge, it is recommended to use the particular UPS just because we know what the charging parameters are (charger wattage, voltage, etc) and that they will be OK with that particular battery. You could certainly use your own charger but then that'd require likely finding out what the charger voltage is on each UPS and then making sure you can find a charger that could accept different values for that (which we don't have any specific recommendations unfortunately), but you would be on your own in terms of support for setting all of that up and using the external charger.

Let me know if you have any further questions.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 12:09 AM . Last Modified: ‎2024-03-20 12:22 AM

0 Likes
0
1038
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:09 AM . Last Modified: ‎2024-03-20 12:22 AM

I work at a large Canadian University and deal with this issue myself. Angela N is correct there is a requirement to utilize the model of UPS these battery modules are manufactured for as a "charging base"; I don't know of any portable battery charging system that puts out the exact voltages required for the battery strings inside these models Eg 216 volts for the RT's and PX's, 48 volts or 136.5 volts for the SMX's etc. What I could suggest is that it would make the job of charging the SMX and RT modules in the field a bit easier if you purchased battery extender cables for the external battery cabinets for each model of UPS/RBC that you are dealing with, or have some custom cables made up for the individual modules using the correct flavor of Anderson connectors. That could allow you to avoid having to remove the external battery cabinets or even the modules themselves from their shipping cartons and/or at the very least maybe you won't have to install them inside the UPS. Cables for the external cabinets that are as long as 15 feet are available - see below. Also if you could come up with a way of bolting the smallest/lightest model of the particular UPS's required that use a particular model of replacement battery module and mount it to a caster base - or an upright dolley ? - with a long extension cord affixed so it could be rolled into place near the battery stock. APC actually makes an equipment cart for the RT UPS's that would be useful for that: http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=SURT013

Extender Cables for the SMX ups are here: http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=SMX040

Extender Cables for the RT ups are here: http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=SURT008

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore