Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Which UPS will be the best for my system?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase โ†’ Use quotes " " (e.g., "error 404")
  • Wildcard โ†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR โ†’ Combine keywords (e.g., login AND error, login OR signโ€‘in)
  • Keep it short โ†’ Use 2โ€“3 relevant words , not full sentences
  • Filters โ†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Which UPS will be the best for my system?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2151
Teken
Teken
154
Techie_apc
Techie_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: โ€Ž2021-06-28 10:53 PM . Last Modified: โ€Ž2024-03-22 04:36 AM

0 Likes
6
2392
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 10:53 PM . Last Modified: โ€Ž2024-03-22 04:36 AM

Which UPS will be the best for my system?

Hi everybody,

I'm new to UPS since I heard about them and if I'd buy one, it would be APC for sure. I'm mostly a gamer than a computer worker. So my question is : what is the model that will suit this computer specs if power is loss?

Intel Quadcore Q6600 @ 3.0GHz, 1.2375V
2x 8800gtx (around 60A total on 12V+ rails)
Corsair 1000W powersupply
Samsung 2693HM monitor
And a cheap router D-Link WBR-1310

Do I have to calculate the max load on the 120V line?

Please send me some light on this.. I am very new to these kinds of things.
Regards, Guillaume

p.s.: sorry for my bad english ^^

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • firmware
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: โ€Ž2021-06-28 10:53 PM . Last Modified: โ€Ž2024-03-22 04:35 AM

0 Likes
0
2392
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 10:53 PM . Last Modified: โ€Ž2024-03-22 04:35 AM

Well, the only thing that can demage a memory module in the situation you described is static electricity in your own body. Even if the motherboard were energized, not working, but only energyzed by the PSU, chances are that the module would not suffer anything. I've done that many times and nothing happened.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Anonymous user
Not applicable

Posted: โ€Ž2021-06-28 10:53 PM . Last Modified: โ€Ž2024-03-22 04:35 AM

0 Likes
0
2392
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 10:53 PM . Last Modified: โ€Ž2024-03-22 04:35 AM

My english is not the best either! ๐Ÿ™‚

In my opinion, you need something above 1000VA, I would recommend you at least a 1500VA unit. Those of the LCD series, the BR1500LCD or BX1500LCD would be a good option, but there are other models.

Since your power supply has the potential of drawing 1000W, a big UPS is recommended or you might end up having an overloading unit, specially when you're starting your PC and when the UPS transfers to battery,

Message was edited by: rau

Reply

Link copied. Please paste this link to share this article on your social media post.

EZ_Button_apc
EZ_Button_apc
Contributor

Posted: โ€Ž2021-06-28 10:53 PM . Last Modified: โ€Ž2024-03-22 04:35 AM

0 Likes
0
2392
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 10:53 PM . Last Modified: โ€Ž2024-03-22 04:35 AM

Yes, you'll be looking at what the max draw can be. Your power supply is 1000 watts, which is pretty substantial. Do you have any idea how much of that your system will actually use at it's peak? The reason I say that is because this could be the difference between a 15 amp 1500 (limited to 980 watts as the load) or a 20 amp 2200 (limited to 1980 watts) in terms of capacity.

http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SUA1500

http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SUA2200

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-28 10:53 PM . Last Modified: โ€Ž2024-03-22 04:35 AM

0 Likes
0
2392
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 10:53 PM . Last Modified: โ€Ž2024-03-22 04:35 AM

I really doubt his computer drawns 1000W when operating normally, even if he's playing a game.

The only time his PSU would draw 1000W would be when it starts, for a few miliseconds or when it transfers to battery.

If his power supply drawns 1000W and since it is 80% efficient, it means it acctually drawns 1200W from the wall outlet.

And also, since his PSU has active power factor correction, it means a 1500VA unit is capable of supply close to 1500Watts, not 980Watts. This would be for load with .6 power factor, which is not the case of his PSU. His PSU has a .98 or .99 PF.


Message was edited by: rau

Message was edited by: rau

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-28 10:53 PM . Last Modified: โ€Ž2024-03-22 04:35 AM

0 Likes
0
2392
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 10:53 PM . Last Modified: โ€Ž2024-03-22 04:35 AM

sorry to bother you, but last night i forgot to unplug the power cord between the computer and the UPS;
my "Back UPS CS 650 VA" was OFF, so have I fried the DDR2 modules?
(I removed them from the sockets). Everything seems to work just fine, now,
but I wonder was there any voltage on the MotherBoard with the UPS OFF, and the power cable still connected?
thancks in advance.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-28 10:53 PM . Last Modified: โ€Ž2024-03-22 04:35 AM

0 Likes
0
2392
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 10:53 PM . Last Modified: โ€Ž2024-03-22 04:35 AM

When I'm working (with trembling hands) inside the PC case, I usually take care. It seems that nothing wrong has happened, this time also. It was just a nagging thought.
Did I or not make the wrong move? It seems everything is OK, the system is just fine.
Thancks a lot for your solid-experience-rooted response.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-28 10:53 PM . Last Modified: โ€Ž2024-03-22 04:35 AM

0 Likes
0
2393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-28 10:53 PM . Last Modified: โ€Ž2024-03-22 04:35 AM

Well, the only thing that can demage a memory module in the situation you described is static electricity in your own body. Even if the motherboard were energized, not working, but only energyzed by the PSU, chances are that the module would not suffer anything. I've done that many times and nothing happened.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 

Youโ€™ve reached the end of your document

WHATโ€™S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore