Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

What is shutting down my Server?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: What is shutting down my Server?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2151
Teken
Teken
156
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS for Home and Office Forum
Start a Topic
Ritscha
Ritscha
Explorer

Posted: ‎2026-10-30 07:12 AM

0 Likes
4
151
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-10-30 07:12 AM

What is shutting down my Server?

Dear community

since beginning of october every two weeks around 13:30h our windows server is shut down. In the event log I see event 1074

10/02/26 13:32:09 "PowerChute Business Edition has initiated a system shutdown."

10/16/26 13:31:26 "PowerChute Business Edition has initiated a system shutdown."

and after we upgraded

10/30/26 13:30:40 "PowerChute Serial Shutdown has initiated a system shutdown."

 

In the UPS event log I see:

 

     
10/30/26 12:30:40 PowerChute Agent outlet turning off (by external entity)
10/30/26 12:30:32 Self Test Initiated
10/30/26 12:30:31 On Line (Green Mode) - Exited

 

10/16/26 13:37:29 https://www.se.com/pcss
10/16/26 13:36:29 Communication Established
10/16/26 13:36:29 Monitoring Started
10/16/26 13:31:25 Monitoring Stopped
10/16/26 13:31:25 PowerChute Agent outlet turning off (by external entity)
10/15/26 22:38:27 https://www.se.com/pcss
10/15/26 22:37:27 Self Test Initiated
10/15/26 22:37:26 On Line (Green Mode) - Exited
10/15/26 22:37:26 On Line (Green Mode) - Entered
10/15/26 22:37:26 Communication Established
10/15/26 22:37:26 Monitoring Started
10/15/26 22:35:37 Monitoring Stopped
10/15/26 22:35:14 https://www.se.com/pcss
10/15/26 22:34:13 Self Test Initiated
10/15/26 22:34:13 On Line (Green Mode) - Exited
10/15/26 22:34:13 On Line (Green Mode) - Entered
10/15/26 22:34:12 Communication Established
10/15/26 22:34:13 Monitoring Started
10/15/26 22:32:01 Monitoring Stopped

 

10/2/26 13:32:09 Monitoring Stopped
10/2/26 13:32:09 PowerChute Agent outlet turning off (by external entity)
10/2/26 13:31:57 Self Test Initiated
10/2/26 13:31:57 On Line (Green Mode) - Exited

 

The first time the self test was set to run every two weeks but after the first incident I set this to "never". But the UPS still apears to start a self test. Maybe when the server with PowerChute Serial Shutdown is started after a server (re)start?

The last Self test was after the shutdown. That's the Diagnostics page of the UPS webserver:

Diagnostics

Self Test Status

October 30, 2026, 12:41:21 PM CET
Aborted

Runtime Calibration Status

Unknown
Unknown

Initiate Diagnostics

Schedule Self Test

                    
 
I'm a bit confused about the events that occur and what actually is causing the server shutdown. The batteries are somewhat old, I have to say, but current runtime is given as 118 min.
 
Any help is highly appreciated.
Roger
Labels
  • Labels:
  • Home & Office - UPS & Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Next Topic
Replies 4
Teken
Teken
Champion

Posted: ‎2026-11-02 09:24 AM

0 Likes
2
150
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-11-02 09:24 AM

I suggest you schedule a maintenance window where you can complete a static and dynamic load test on the system. In the interim call out the UPS SKU, Serial Number, and RBC Installation Date.

 

Provide the full diagnostic logs for the system and upload the same for review.

 

NOTE: The displayed operational runtime of 118 minutes has absolutely no meaning as to the RBC state of health. 

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Ritscha
Ritscha
Explorer

Posted: ‎2026-11-03 11:54 PM

In response to Teken
0 Likes
1
119
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-11-03 11:54 PM

It's a SMT1000I, S/N AS1148222399,

Firmware UPS 06.5/MCU 11.0(18-6)

Battery installed Oct 2021

Where do I upload the diagnostic log? Or do I paste it in this answer field?

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: ‎2026-11-04 05:05 AM

In response to Ritscha
0 Likes
0
114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-11-04 05:05 AM

If the information you have provided here is accurate. The most likely scenario I suspect is the RBC is end of life (EOL) and needs to be replaced. Worst case scenario is the UPS is failing and needs to be replaced.

 

Based on the serial number it was produced in 2011 48th week. Which is 15 plus years old with a RBC installed on October 2021 or five years old.

 

The RBC has a service life of 2-5 years based on usage, temperature, and environmental conditions.

 

The cells that make up a RBC Pack are designed to provide up to 260 cycles subject to the same caveats as above.

 

You may copy and paste the logs or upload them.

 

In the interim you may schedule a maintenance window and complete the following action items and report back the results and behaviour.

 

Replace the connected load with a resistive load such as a heater or worst case a fan so you don’t place the server(s) in harms way.

 

Load & System Test:

 

Static: Disconnect the Anderson cable from the RBC. The expected outcome is the system will continue to operate and support the connected load but will immediately alert you the RBC has been disconnected.

 

Leave the unit like this for a minimum of 30 - 60 minutes then reconnect the Anderson cable. The system should indicate the RBC is connected and no other active faults / alerts should be present. If you observe any other conditions please call it out.

 

Dynamic: Disconnect AC Mains from the wall outlet. The expected behaviour is the system will immediately transfer to battery only (inverter) mode. The system will declare an active fault (Loss of AC Mains) and beep.

 

If the RBC is EOL or expired the possible outcomes are these:

 

1. Immediate shutdown and dropped load.

 

2. The system will operate for under 2 minutes or less than shutdown and drop the load.

 

3. The system will operate for more than five minutes than shutdown and drop the load.

 

NOTE: The operation runtime is subject to many factors such as load, RBC Health, Temperature etc. You will notice the operational runtime displayed on the LCD will more than likely drop erratically which doesn’t reflect the actual runtime.

 

Track and call this out . . .  

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Ritscha
Ritscha
Explorer

Posted: ‎2026-11-13 03:19 AM

0 Likes
0
34
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-11-13 03:19 AM

Management bought a new UPS. It looks like the batteries in the old unit were done (installed 2021).

Thanks for the help anyway. I learned a lot.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore