Dear community
since beginning of october every two weeks around 13:30h our windows server is shut down. In the event log I see event 1074
10/02/26 13:32:09 "PowerChute Business Edition has initiated a system shutdown."
10/16/26 13:31:26 "PowerChute Business Edition has initiated a system shutdown."
and after we upgraded
10/30/26 13:30:40 "PowerChute Serial Shutdown has initiated a system shutdown."
In the UPS event log I see:
| 10/30/26 | 12:30:40 | PowerChute Agent outlet turning off (by external entity) |
| 10/30/26 | 12:30:32 | Self Test Initiated |
| 10/30/26 | 12:30:31 | On Line (Green Mode) - Exited |
| 10/16/26 | 13:37:29 | https://www.se.com/pcss |
| 10/16/26 | 13:36:29 | Communication Established |
| 10/16/26 | 13:36:29 | Monitoring Started |
| 10/16/26 | 13:31:25 | Monitoring Stopped |
| 10/16/26 | 13:31:25 | PowerChute Agent outlet turning off (by external entity) |
| 10/15/26 | 22:38:27 | https://www.se.com/pcss |
| 10/15/26 | 22:37:27 | Self Test Initiated |
| 10/15/26 | 22:37:26 | On Line (Green Mode) - Exited |
| 10/15/26 | 22:37:26 | On Line (Green Mode) - Entered |
| 10/15/26 | 22:37:26 | Communication Established |
| 10/15/26 | 22:37:26 | Monitoring Started |
| 10/15/26 | 22:35:37 | Monitoring Stopped |
| 10/15/26 | 22:35:14 | https://www.se.com/pcss |
| 10/15/26 | 22:34:13 | Self Test Initiated |
| 10/15/26 | 22:34:13 | On Line (Green Mode) - Exited |
| 10/15/26 | 22:34:13 | On Line (Green Mode) - Entered |
| 10/15/26 | 22:34:12 | Communication Established |
| 10/15/26 | 22:34:13 | Monitoring Started |
| 10/15/26 | 22:32:01 | Monitoring Stopped |
| 10/2/26 | 13:32:09 | Monitoring Stopped |
| 10/2/26 | 13:32:09 | PowerChute Agent outlet turning off (by external entity) |
| 10/2/26 | 13:31:57 | Self Test Initiated |
| 10/2/26 | 13:31:57 | On Line (Green Mode) - Exited |
The first time the self test was set to run every two weeks but after the first incident I set this to "never". But the UPS still apears to start a self test. Maybe when the server with PowerChute Serial Shutdown is started after a server (re)start?
The last Self test was after the shutdown. That's the Diagnostics page of the UPS webserver:
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-11-02 09:24 AM
I suggest you schedule a maintenance window where you can complete a static and dynamic load test on the system. In the interim call out the UPS SKU, Serial Number, and RBC Installation Date.
Provide the full diagnostic logs for the system and upload the same for review.
NOTE: The displayed operational runtime of 118 minutes has absolutely no meaning as to the RBC state of health.
Questions Ask . . . 👍
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-11-03 11:54 PM
It's a SMT1000I, S/N AS1148222399,
Firmware UPS 06.5/MCU 11.0(18-6)
Battery installed Oct 2021
Where do I upload the diagnostic log? Or do I paste it in this answer field?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-11-04 05:05 AM
If the information you have provided here is accurate. The most likely scenario I suspect is the RBC is end of life (EOL) and needs to be replaced. Worst case scenario is the UPS is failing and needs to be replaced.
Based on the serial number it was produced in 2011 48th week. Which is 15 plus years old with a RBC installed on October 2021 or five years old.
The RBC has a service life of 2-5 years based on usage, temperature, and environmental conditions.
The cells that make up a RBC Pack are designed to provide up to 260 cycles subject to the same caveats as above.
You may copy and paste the logs or upload them.
In the interim you may schedule a maintenance window and complete the following action items and report back the results and behaviour.
Replace the connected load with a resistive load such as a heater or worst case a fan so you don’t place the server(s) in harms way.
Load & System Test:
Static: Disconnect the Anderson cable from the RBC. The expected outcome is the system will continue to operate and support the connected load but will immediately alert you the RBC has been disconnected.
Leave the unit like this for a minimum of 30 - 60 minutes then reconnect the Anderson cable. The system should indicate the RBC is connected and no other active faults / alerts should be present. If you observe any other conditions please call it out.
Dynamic: Disconnect AC Mains from the wall outlet. The expected behaviour is the system will immediately transfer to battery only (inverter) mode. The system will declare an active fault (Loss of AC Mains) and beep.
If the RBC is EOL or expired the possible outcomes are these:
1. Immediate shutdown and dropped load.
2. The system will operate for under 2 minutes or less than shutdown and drop the load.
3. The system will operate for more than five minutes than shutdown and drop the load.
NOTE: The operation runtime is subject to many factors such as load, RBC Health, Temperature etc. You will notice the operational runtime displayed on the LCD will more than likely drop erratically which doesn’t reflect the actual runtime.
Track and call this out . . .
Questions Ask . . . 👍
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-11-13 03:19 AM
Management bought a new UPS. It looks like the batteries in the old unit were done (installed 2021).
Thanks for the help anyway. I learned a lot.
Link copied. Please paste this link to share this article on your social media post.