Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Unable to install PowerChute Serial Shutdown software

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: Unable to install PowerChute Serial Shutdown software
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2151
Teken
Teken
156
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
atleast2characterslong
atleast2characterslong
Explorer

Posted: ‎2025-06-18 01:38 PM

0 Likes
2
2974
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-18 01:38 PM

Unable to install PowerChute Serial Shutdown software

I'm trying to install the software to use with a brand new APC Back-UPS 600. When I run the setup file, after accepting the terms, the setup doesn't do anything. It's still running in task manager. Here's what I get in the install log.

 

2025-06-18 15:44:25 --- Installing PowerChute Serial Shutdown 1.3.0.301
2025-06-18 15:44:25 --- .onInit
2025-06-18 15:44:27 --- CacheOSLanguage: OS language cached: 1033
2025-06-18 15:44:27 --- Setting up CommandLineConfigEditor tool
2025-06-18 15:44:27 --- CustomGUIInit
2025-06-18 15:44:27 --- PowerChute Serial Shutdown is not installed
2025-06-18 15:44:27 --- CheckJapaneseOS: OS language identifier detected: 1033
2025-06-18 15:44:27 --- Checking if PowerChute Business Edition is installed
2025-06-18 15:44:27 --- PowerChute Business Edition is not installed
2025-06-18 15:44:27 --- Microsoft Visual C++ 2017 Redistributable Package (x64) is already installed
2025-06-18 15:44:27 --- PowerChute Personal Edition is not installed
2025-06-18 15:44:32 --- UPS connected, checking hardware id before installing APCUPS driver
2025-06-18 15:44:33 Error installing APC NPM driver, return code -2

 

The device does show up under devices when I connect it to my computer. I also see the driver added to device manager. I've tried uninstalling the driver before attempting the install again which does not help. Nor does updating the driver in the device manager. I've also tried restarting the computer and the UPS as well as trying to install without it plugged in.

 

Any other ideas why the setup could be getting stuck?

Labels
  • Labels:
  • Home & Office - UPS & Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
fredkm
fredkm Troubleshooter
Troubleshooter

Posted: ‎2025-06-19 10:59 PM

1 Like
1
2959
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-19 10:59 PM

PowerChute Serial Shutdown installs a so called null-driver (named 'APC UPS') which replaces the plug-and-play driver (named 'HID UPS Battery'). The purpose of the null-driver is disabling native power management on the OS for the UPS. I.e. you want PowerChute Serial Shutdown to protect your computer during power failures, and you don't want a Windows power plan interfering with this.

 

From the installation logs I can see that null-driver installation fails. This will occur if there is no UPS connected to a USB port during installation. Obviously that's not the case for you as you state you have the UPS connected. Error code -2 means the hardware ID of your UPS did not match any of the known APC UPS hardware IDs. Not sure why the installer hangs at this point.

 

Some things you could try:

- Make sure you've got latest Windows updates installed (early Win 11 versions had issues with USB devices).

- Try a different USB port.

 

If it doesn't work then could you please provide some additional information to help us troubleshooting your issue:

  • Your UPS model which you can find on sticker at the back or bottom of the UPS (it should be different from the generic 'Back-UPS 600' name you already provided).
  • Your Windows version and build.
  • The UPS hardware Id. You can find this through 'Control Panel - Device Manager'. Right-click the 'HID UPS Battery' device and select  'Properties' from the context menu. Open 'Details' tab and in the dropdown select 'Hardware Ids'
    fredkm_0-1750398947115.png

     

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
fredkm
fredkm Troubleshooter
Troubleshooter

Posted: ‎2025-06-19 10:59 PM

1 Like
1
2959
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-19 10:59 PM

PowerChute Serial Shutdown installs a so called null-driver (named 'APC UPS') which replaces the plug-and-play driver (named 'HID UPS Battery'). The purpose of the null-driver is disabling native power management on the OS for the UPS. I.e. you want PowerChute Serial Shutdown to protect your computer during power failures, and you don't want a Windows power plan interfering with this.

 

From the installation logs I can see that null-driver installation fails. This will occur if there is no UPS connected to a USB port during installation. Obviously that's not the case for you as you state you have the UPS connected. Error code -2 means the hardware ID of your UPS did not match any of the known APC UPS hardware IDs. Not sure why the installer hangs at this point.

 

Some things you could try:

- Make sure you've got latest Windows updates installed (early Win 11 versions had issues with USB devices).

- Try a different USB port.

 

If it doesn't work then could you please provide some additional information to help us troubleshooting your issue:

  • Your UPS model which you can find on sticker at the back or bottom of the UPS (it should be different from the generic 'Back-UPS 600' name you already provided).
  • Your Windows version and build.
  • The UPS hardware Id. You can find this through 'Control Panel - Device Manager'. Right-click the 'HID UPS Battery' device and select  'Properties' from the context menu. Open 'Details' tab and in the dropdown select 'Hardware Ids'
    fredkm_0-1750398947115.png

     

Reply

Link copied. Please paste this link to share this article on your social media post.

atleast2characterslong
atleast2characterslong
Explorer

Posted: ‎2025-06-27 05:25 AM

In response to fredkm
1 Like
0
2880
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-27 05:25 AM

I was able to install it on a different computer without an issue. I still have not been able to install it on my computer, but since this UPC was purchased for a coworker's computer and it is working, I am not going to try and further diagnose the problem. I appreciate the quick and detailed response. Thanks for your help.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore