Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

UPS permanently reports 0W / 0VA / 0A / 0% load

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • UPS permanently reports 0W / 0VA / 0A / 0% load
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
144
Techie_apc
Techie_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS for Home and Office Forum
Start a Topic
obiserver
obiserver
Explorer

Posted: ‎2026-07-04 01:17 PM

0 Likes
3
102
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-07-04 01:17 PM

UPS permanently reports 0W / 0VA / 0A / 0% load

After SmartConnect automatically updated the firmware of my Smart-UPS SMT1500I, the UPS permanently reports 0W / 0VA / 0A / 0% load on the LCD and via USB HID. Before the firmware update the load values were correct. The UPS still powers the equipment and switches to battery normally. Factory reset and complete power removal (including battery disconnect) did not resolve the issue.

Model: Smart-UPS_1500
Firmware: UPS 18.0 / ID=1015

Labels
  • Labels:
  • Home & Office - UPS & Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
Teken
Teken
Champion

Posted: ‎2026-07-07 01:10 AM

0 Likes
0
97
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-07-07 01:10 AM

Complete the following action items in sequence and report the outcome.

 

Brain Dead: Complete this procedure three times as outlined in this APC FAQ:

 

https://www.se.com/ca/en/faqs/FA156611/

 

Date: Update the battery installation date via LCD, NMC, Power Chute. If the system incorporates a NMC insure the date and time is correct along with DST if applicable. 

Self Test: Manually initiate a self test via the following methods LCD, NMC, Power Chute and let pass.

 

Calibration: Manually initiate a battery calibration with a minimum of 30% connected load or higher via LCD, NMC, Power Chute. 

Once complete allow the RBC to fully charge to 100% SOC. Report the final outcome and provide the following logs for review: Event, Data, UPS, Diagnostics 

 

Power Chute logs can be obtained following this APC Resource Link:

 

https://www.se.com/us/en/faqs/FA159672/


If the system incorporates a NMC you may retrieve the logs following the steps below:

 

NMC: About -> Support-> Technical Support Debug -> Generate Logs -> Download.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

obiserver
obiserver
Explorer

Posted: ‎2026-07-08 11:51 AM

0 Likes
1
64
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-07-08 11:51 AM

I have already completed the Brain Dead procedure several times, performed a Factory Reset, and fully disconnected AC power and the battery. The UPS still reports 0W / 0VA / 0A / 0% on the LCD while powering a server and monitor correctly.

 

Since the UPS reports 0% load, I am unable to satisfy the 30% load requirement for a runtime calibration because the UPS does not detect any connected load.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: ‎2026-07-09 02:52 AM

In response to obiserver
0 Likes
0
58
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-07-09 02:52 AM

As noted in my initial post all of the action items posted should be completed in sequence.

 

NOTE: If the system indicates the 30% minimum connected load has not been satisfied by indicating a calibration failure.

 

You may remove AC Mains from the wall outlet and let the system automatically drain and shutdown.


Any cables connecting to a computer / network relating to APC Power Chute Software must be disconnected during this scheduled maintenance window.

 

You will connect any resistive load to satisfy the 30% minimum load or (Higher) whether it be a load center, heater, fan, etc.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore