Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

UPS Fault Logs - Backfeed Relay Hardware Fault

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • UPS Fault Logs - Backfeed Relay Hardware Fault
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
144
Techie_apc
Techie_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Related Products
product field
Schneider Electric
Smart-UPS

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS for Home and Office Forum
Start a Topic
IT-UPS
IT-UPS
Explorer

Posted: ‎2026-01-09 07:35 AM

0 Likes
3
394
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-01-09 07:35 AM

UPS Fault Logs - Backfeed Relay Hardware Fault

After a small power cut, I came back to the office to find our Smart-UPS X 3000 beeping away and not providing any power to our rack. After a reboot, the UPS has continued to work as normal but the UPS Fault Logs shows an Event Code of 135 and Event description stating: Backfeed Relay Hardware Fault. I've read up on the fault and understand the feature, but would this be an actual physical fault that needs a part replacing? How would I tell if so? Or will this just have been an unclean power input so the UPS decided to not power up any further? In the past, the UPS has stayed on battery until it sees a clean power input, then flips back to mains. 

Labels
  • Labels:
  • Home & Office - UPS & Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
Teken
Teken
Champion

Posted: ‎2026-01-12 04:04 AM

0 Likes
0
389
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-01-12 04:04 AM

What is the serial number and years of service on the unit?!?! Provide the following logs in their entirety minus any PI data for review: Event, Data, UPS, Diagnostics.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

IT-UPS
IT-UPS
Explorer

Posted: ‎2026-01-12 08:42 AM

0 Likes
1
379
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-01-12 08:42 AM

Hi!

 

The logs only go back to the morning after the power cut unfortunately.

 

The Events logs around the time are full of records that alert emails could not be sent out (because our firewall went down, so it couldnt talk out to the internet).

 

The Data logs are all consistent and nothing abnormal or different to its normal operation.

 

The UPS logs are the only place it states the Backfeed Relay Hardware fault (below):

 

Number Time (ms) Event Code EventNumber Time (ms) Event Code Event

UPS Transfer Logs
1 821085121940 8 Acceptable Input 
2 821085120675 4 rapid change of input 
3 821085097079 8 Acceptable Input 
4 821085095571 4 rapid change of input 
5 821084852138 8 Acceptable Input 
6 821084850663 4 rapid change of input 
7 817763203297 8 Acceptable Input 
8 817755171307 3 distorted input 
9 817414785604 8 Acceptable Input 
10 817414778677 3 distorted input 
 
UPS Fault Logs
1 821085121940 135 Backfeed Relay Hardware Fault 
2 0 0 None 
3 0 0 None 
4 0 0 None 
5 0 0 None 
6 0 0 None 
7 0 0 None 
8 0 0 None 
9 0 0 None 
10 0 0 None 

 

The model details are below:

 

Model:Smart-UPS X 3000
SKU:SMX3000RMHV2UNC
Serial Number:AS1608155561
Firmware Revision:UPS 07.4 (ID1003)
Manufacture Date:27.02.2016
 
Apparent Power Rating:3000 VA
Real Power Rating:2700 W
 
Internal Battery SKU:APCRBC117
External Battery SKU:APCRBC118

 

I also changed the battery over in 2020 and it states its recommended to be replaced Aug 2024. Appreciate it may need a new one (under the recommendations) but I don't know enough to say if its related to this particular fault. Its back on mains power as normal and the front panel on the unit states its as full battery capacity and has the same amount of time left as its always shown, if it failed over to battery (about 2.5 hours on current load). 

 

Thanks for replying and any help you can give!

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: ‎2026-01-13 05:11 AM

In response to IT-UPS
0 Likes
0
373
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-01-13 05:11 AM

Based on the information you have provided here I would probably say the RBC needs to be replaced.

 

The average service life is 2-5 years based on usage, temperature, and environmental conditions.

 

The following action item(s) will need to be scheduled during the next maintenance window to help identify root cause and narrow down the problem.

 

There are two basic tests that should be completed so report the outcome and results here:

 

Static Test: Disconnect the Anderson connector from all of the RBC if there are external packs installed.

 

The only thing that should happen is the system will declare a RBC disconnected fault but will continue to run.

 

Should the unit drop the load and turn off you have an internal hardware fault.

 

Dynamic Test: The following test simply requires you to remove AC Mains from the unit while the RBC is in place.

 

The expected outcome is the unit will continue to operate on battery only power.


Should the system turn off immediately or within a few seconds / minutes which is outside the expected operational runtime than the RBC is EOL and expired and needs to be replaced / rebuilt.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore