Smart-UPS SC 620: Clicking, Beeping, keeps switching off - battery?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Smart-UPS SC 620: Clicking, Beeping, keeps switching off - battery?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
119
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:26 AM . Last Modified: ‎2024-03-21 11:10 PM

0 Likes
1
1192
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:26 AM . Last Modified: ‎2024-03-21 11:10 PM

Smart-UPS SC 620: Clicking, Beeping, keeps switching off - battery?

I have a Smart-UPS SC 620 and an issue which isn't covered in the troubleshooting section of the manual.

Lately I've noticed that if I plug the TV into another wall socket (not where the UPS is) it trips the UPS and the UPS loses all power, even though it's plugged in. All the lights go off on the UPS and all I get is a regular beep every 5 or so. The connected equipment is immediately powered off.

Previously when this happened I switched it off and switched it back on again and it seemed ok.

Now if I try to switch it back on the green light comes on on the top, then when it goes into self-test mode all the lights go off again, power goes off, and it beeps every 5 seconds again.

Is the battery dead? If so, shouldn't it maintain power to my equipment? When this happens my connected equipment loses power (the UPS stops interrupts its uninteruptable supply).

Is the UPS faulty or is it just a dead battery?

Thanks.

EDIT: While all the above happens it sometimes also keeps clicking, every 1-3 seconds.

Message was edited by: planck_length

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:26 AM . Last Modified: ‎2024-03-21 11:10 PM

0 Likes
0
1191
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:26 AM . Last Modified: ‎2024-03-21 11:10 PM

i have a couple of questions for you..

1.) Is the wall socket you are plugging the TV into on the same circuit? it may not be the same socket/outlet but i suspect it is the same circuit.

2.) How much load is on the UPS currently? have to changed the attached load recently? added more to the UPS?

3.) If you have the UPS up and running normally, does it provide runtime for your attached equipment on battery. if so, do you know how long it runs?

my initial thought, which may change based on the info i asked above is that you are connected the TV to the same circuit the UPS load is on. the TV has a little bit if inrush current, similiar to when you power on a vacuum, air conditioner, or other high current device and the lights dim a bit, so the UPS sees that disturbance on the circuit, and tries to transfer over to battery but either the battery is bad AND the load is too high or the battery is just old an cannot support the attached load like it used to. thus, you may see it go straight to a load battery condition with the beeping, as you described.

can you provide the first several digits of your UPS serial number? such as QS0643? has the battery ever been replaced?

thanks!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:26 AM . Last Modified: ‎2024-03-21 11:10 PM

0 Likes
0
1192
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:26 AM . Last Modified: ‎2024-03-21 11:10 PM

i have a couple of questions for you..

1.) Is the wall socket you are plugging the TV into on the same circuit? it may not be the same socket/outlet but i suspect it is the same circuit.

2.) How much load is on the UPS currently? have to changed the attached load recently? added more to the UPS?

3.) If you have the UPS up and running normally, does it provide runtime for your attached equipment on battery. if so, do you know how long it runs?

my initial thought, which may change based on the info i asked above is that you are connected the TV to the same circuit the UPS load is on. the TV has a little bit if inrush current, similiar to when you power on a vacuum, air conditioner, or other high current device and the lights dim a bit, so the UPS sees that disturbance on the circuit, and tries to transfer over to battery but either the battery is bad AND the load is too high or the battery is just old an cannot support the attached load like it used to. thus, you may see it go straight to a load battery condition with the beeping, as you described.

can you provide the first several digits of your UPS serial number? such as QS0643? has the battery ever been replaced?

thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore