Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Smart 1500 X UPS Overvoltage alert

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: Smart 1500 X UPS Overvoltage alert
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
148
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:18 AM . Last Modified: ‎2024-03-21 05:01 AM

0 Likes
5
2114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:18 AM . Last Modified: ‎2024-03-21 05:01 AM

Smart 1500 X UPS Overvoltage alert

Hi,

We have many number of UPSs within our organization and almost all the UPSs have the following metioned issue.

The UPS generates alerts stating that a high input voltage is detected and the high transfer voltage configured in the UPS is 257 V.
according to the event log, the input voltage is around 250 V at all times.

but whenever the input voltage level is checked using a multimeter ( True RMS ), the Voltage is shown as 240 V ( or less ).

I am not sure the exact reason for this and expect your help to resolve this.
The UPS which I am currently testing has the latest firware ( v 5.1.6 )

Thanks,
Kumara

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:18 AM . Last Modified: ‎2024-03-21 05:01 AM

0 Likes
0
2113
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:18 AM . Last Modified: ‎2024-03-21 05:01 AM

Hi Kumaraw,

It's our pleasure to help you with your concern.

I would suggest you to call our hotline number 800-800-4272. Our technical support engineers should be able to assist you with the upgrade.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:18 AM . Last Modified: ‎2024-03-21 05:01 AM

0 Likes
0
2113
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:18 AM . Last Modified: ‎2024-03-21 05:01 AM

Hi juangele,

Sorry for the late response.
Actually I live in Australia and contacted APC support centre here and they provided me the firmware upgrade tool.

Now the UPS is running on version 3.8.

but still I experience the issue which I had earlier
( i.e - the input voltage displayed in the UPS ( 250 V ) is always higher than the voltmeter reading ( 240 V ) )

So I am not sure the reason for this and I believe that the voltmeter is functioning properly
( checked with two different multimeters )

Is there a debugging mode in the UPS that I can use to troubleshoot this further ?

In addition, when we purchase new UPSs and NMCs, wer receive them with old fimware revisions and we always have to upgrage them manually.

Is this normal for all the purchases or can I ask our local vendor to ship them with the latest firmware version ?

Thanks,
Kumaraw

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 07:18 AM . Last Modified: ‎2024-03-21 05:01 AM

0 Likes
0
2113
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:18 AM . Last Modified: ‎2024-03-21 05:01 AM

if you believe the UPS is not measuring properly then it is possible it could require a voltage calibration. this would require your UPS replaced since a user cannot do that. i think that verifying with the voltmeter (or two) is the only thing that you could do to rule out the UPS or the wrong input voltage. if you had another UPS, you could install it and try it in the same location too to be 110% sure it is this particular UPS that is not measuring properly.

NMCs are flashed at the factory with the latest firmware possible. sometimes vendors have older stock and sometimes firmwares are web release only. i am not sure if your vendor can update to the latest but it is doubtful. these can be mass upgraded by using the tools here ->http://nam-en.apc.com/app/answers/detail/a_id/8522 if you have a lot of cards. otherwise, you will just need to update on your own since there is generally a delay in when the latest version cards get to the end users since they go through distribution, etc

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:18 AM . Last Modified: ‎2024-03-21 05:01 AM

0 Likes
0
2113
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:18 AM . Last Modified: ‎2024-03-21 05:01 AM

Hi Kumaraw,

Kindly provide the exact model number of the unit?

When you say 516 firmware version, are you looking on the NMC. Kindly check the UPS FW of the UPS via the NMC or thru the LCD.

I would also like to share this kbase to you. - [Answer ID 11333|http://nam-en.apc.com/app/answers/detail/a_id/11333/kw/High%20Input%20voltage]

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:18 AM . Last Modified: ‎2024-03-21 05:01 AM

0 Likes
0
2113
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:18 AM . Last Modified: ‎2024-03-21 05:01 AM

Hi juangele ,

Thanks a lot for your prompt response.

The model of the UPS is - Smart-UPS X 1500 and the firmware version is - ID11UPS 03.1 .
Do I need to contact APC customer care centre to get the fimware or can I download it from APC website ?

Thanks,
Wipua.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:18 AM . Last Modified: ‎2024-03-21 05:01 AM

0 Likes
0
2114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:18 AM . Last Modified: ‎2024-03-21 05:01 AM

Hi Kumaraw,

It's our pleasure to help you with your concern.

I would suggest you to call our hotline number 800-800-4272. Our technical support engineers should be able to assist you with the upgrade.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore