Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

SURTA3000XL SN JS0734016596 Failed

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase โ†’ Use quotes " " (e.g., "error 404")
  • Wildcard โ†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR โ†’ Combine keywords (e.g., login AND error, login OR signโ€‘in)
  • Keep it short โ†’ Use 2โ€“3 relevant words , not full sentences
  • Filters โ†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: SURTA3000XL SN JS0734016596 Failed
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
150
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS for Home and Office Forum
Start a Topic
dposmondsr
dposmondsr
Explorer

Posted: โ€Ž2026-07-26 11:41 AM

0 Likes
6
329
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2026-07-26 11:41 AM

SURTA3000XL SN JS0734016596 Failed

I have a pair of SURTAS3000XL units in a short rack.  They have been operating for years with only needing battery changes.  Yesterday one of the units was beeping.  Not sure for how long.  I pulled the batteries and the unit will still not power on (no fan, no leds, nothing).  Any idea?

Labels
  • Labels:
  • Home & Office - UPS & Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
Teken
Teken
Champion

Posted: โ€Ž2026-07-27 02:25 AM

0 Likes
4
325
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2026-07-27 02:25 AM

If memory serves this legacy device requires a working RBC to turn on. You can test and validate this by inserting the RBC from the other unit after you power it down safely.

 

Youโ€™ll want to perform both static & dynamic tests to insure the unit is fully operational without any connected load.

 

The same two tests will also be completed to ensure the system is truly functional.

 

Static: AC Mains must be connected to the wall outlet. Insert RBC and power on the system. It should complete the POST and Self Test if all is well.

 

Dynamic: The RBC should be at 100% SOC (State of Charge) before proceeding. While the unit is off and AC Mains is disconnected. Initiate the following action item (Cold Start)

press and hold the Test button to power up the UPS and connected equipment.

 

The UPS will emit two beeps. During the second beep, release the button.

 

NOTE: The cold start process must be performed with & without connected loads to validate the system is fully operational. Connect only resistive loads such as a heater, incandescent lamp, hair dryer etc.


Questions Ask . . . ๐Ÿ‘

Reply

Link copied. Please paste this link to share this article on your social media post.

dposmondsr
dposmondsr
Explorer

Posted: โ€Ž2026-08-02 12:07 PM

In response to Teken
0 Likes
3
285
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2026-08-02 12:07 PM

Neither of these units have an RBC (Remote Battery Charger).  The failing unit with commercial power applied does not do anything (with and without internal batteries attached).  

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: โ€Ž2026-08-03 04:00 AM

In response to dposmondsr
0 Likes
2
281
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2026-08-03 04:00 AM

RBC = Replacement Battery Cartridge 

 

Have you swapped the (RBC) from a known good unit to the problem one???

 

A brain dead reset of the unit should be the next action item to complete.

 

Report the outcome of both action items along with the RBC voltage disconnected from the main unit.

 

Questions Ask . . . ๐Ÿ‘

Reply

Link copied. Please paste this link to share this article on your social media post.

JamesOConnor
JamesOConnor
Contributor

Posted: โ€Ž2026-08-04 08:33 AM

0 Likes
0
245
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2026-08-04 08:33 AM

Yeah, this is exactly the scenario I talk about in my book Hyper-Power. Nineteen years on a Smart-UPS RT is nowhere close to normal service life, and only swapping batteries the whole time masks that the rest of the unit is aging right along with them.

 

On the no power, no fan, no LED symptom after pulling batteries: that's usually not a battery problem at all. It typically points to the main control board, the PFC section, or an internal fuse that finally let go. The beeping before it died was likely a fault condition, not just a low battery warning. On a unit that old, electrolytic capacitors on the PFC and inverter boards are well past their rated life even if the batteries were always fresh. Heat cycling in a rack over almost two decades does not do those components any favors.

 

You can check for a blown internal fuse if you want to confirm the failure mode, but honestly at 19 years old I would not sink time into board level diagnosis or repair. Parts availability for something this old is thin and getting thinner, and the SURTA3000XL line itself was discontinued as of October 2025, with end of service life set for October 2027. So even if you found a way to fix this one, you would be maintaining a product APC itself is walking away from.

 

This is the liability tail in action. The unit did its job for a long run, but every year past that 10 year mark adds risk a battery swap does not address: aging power electronics, no manufacturer support, and no path to spare parts. I would treat this as the trigger to replace both units in that rack rather than just the one that failed. Look at a modern double conversion online UPS sized for your load, and if this pair is protecting anything client facing or revenue related, get the second one on a replacement schedule now instead of waiting for it to fail on its own timeline.

 

I wrote a book on this exact liability tail problem.


James OConnor
Strategic IT Advisor
Hypertec Solutions Partner | hypertecsp.com
D:(480) 626-9010 | W: 1.866.787.0426 x4202 |
E: joconnor@hypertec.com
8655 E Via De Ventura, Ste. G161, Scottsdale, AZ 85258
Free Book: Hyper-Power: https://tinyurl.com/Hyper-Power
Reply

Link copied. Please paste this link to share this article on your social media post.

dposmondsr
dposmondsr
Explorer

Posted: โ€Ž2026-08-06 04:24 AM

In response to Teken
0 Likes
1
221
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2026-08-06 04:24 AM

I have good set of RBCs available.  Question is, the unit should power up without RBC installed.  So, what is the step for "A brain dead reset of the unit should be the next action item to complete."  I saw the comment about the age of the unit.  No argument there but I would like to see what I can do before I need to replace it.  Thx

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: โ€Ž2026-08-06 11:15 AM

In response to dposmondsr
0 Likes
0
218
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2026-08-06 11:15 AM

Please refer to this APC Resource Link as it relates to completing a Brain Dead Reset:

 

https://www.se.com/ca/en/faqs/FA156611/

 

Once complete you can test the unit with the other working RBC to see if the unit will power on normally. If the hardware supports *Cold Starting* you may also try this out to validate how the system behaves while in this condition.

 

Both dynamic and static tests must be performed with and without connected loads to validate the hardware is fully operational and working as expected.

 

Questions Ask . . . ๐Ÿ‘

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 

Youโ€™ve reached the end of your document

WHATโ€™S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.