SURT5000XLI and SURT10000XLI Wont Power UP

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

Solved
blackAces_apc
Commander
Commander
0 Likes
3
109

SURT5000XLI and SURT10000XLI Wont Power UP

This was originally posted on APC forums on 5/1/2013


Hi Guys, just want to verify if the battery module of SURT is below 100Vdc ( 98.9Vdc to be specific) it can't power up the unit right, even the UPS was plug to the AC source?

thanks


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
109

Re: SURT5000XLI and SURT10000XLI Wont Power UP

This reply was originally posted by Jonathan on APC forums on 5/3/2013


You are welcome BlackAces.

See Answer In Context

3 Replies 3
BillP
Administrator Administrator
Administrator
0 Likes
0
108

Re: SURT5000XLI and SURT10000XLI Wont Power UP

This reply was originally posted by Jonathan on APC forums on 5/2/2013


Hello BlackAces,

Our SmartUPS RT 3kVA and above units uses a 192V dc system, this 192V dc uses pairs of 96V dc battery packs and the minimum voltage that is required for it to be recognized as good is ~85V dc.

blackAces_apc
Commander
Commander
0 Likes
0
108

Re: SURT5000XLI and SURT10000XLI Wont Power UP

This was originally posted on APC forums on 5/3/2013


Hi Jon P

Thank you for the clarification...

BillP
Administrator Administrator
Administrator
0 Likes
0
110

Re: SURT5000XLI and SURT10000XLI Wont Power UP

This reply was originally posted by Jonathan on APC forums on 5/3/2013


You are welcome BlackAces.