New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
SMC1500I-2UC - changing static ip address
APC UPS for Home and Office Forum
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Search in
Improve your search experience:
Exact phraseโUse quotes " "(e.g., "error 404")
WildcardโUse * for partial words(e.g., build*, *tion)
AND / ORโCombine keywords(e.g., login AND error, login OR signโin)
Keep it shortโUse 2โ3 relevant words, not full sentences
FiltersโNarrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2024-04-0609:10 AM
SMC1500I-2UC - changing static ip address
I need to change the static address assigned to this UPS. I cannot find any reference on how to do this in the Operation Manual; I have tried to do it on a pc running linux using the arp method described elsewhere in the forum without success. My (Netgear) managed switch does not allow me to associate its MAC with a new ip address. I also cannot find any method to do a factory reset which would give me a DHCP address which would be acceptable. Any help gratefully received please.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2024-04-0808:49 AM
Depending upon the firmware installed on the system you have two choices. If the firmware is 4.1 or greater. At the LCD go to Configuration -> Menu Type -> select Advanced.
Then using the down arrow scroll to UPS IP Address Settings and press enter. From the UPS IP Address Setting menu you can change from DHCP to Manual and enter a static IP address, subnet mask, gateway, and DNS.
If the UPS firmware is below 4.1 the IP Address must be changed on the router / firewall appliance.
Almost every consumer grade router allows DCHP and MAC Reservations (Static IP) assignment.
Please report back what you observe and the outcome. If the information helps resolve the issue please do mark this as solved. ๐
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2024-04-0808:49 AM
Depending upon the firmware installed on the system you have two choices. If the firmware is 4.1 or greater. At the LCD go to Configuration -> Menu Type -> select Advanced.
Then using the down arrow scroll to UPS IP Address Settings and press enter. From the UPS IP Address Setting menu you can change from DHCP to Manual and enter a static IP address, subnet mask, gateway, and DNS.
If the UPS firmware is below 4.1 the IP Address must be changed on the router / firewall appliance.
Almost every consumer grade router allows DCHP and MAC Reservations (Static IP) assignment.
Please report back what you observe and the outcome. If the information helps resolve the issue please do mark this as solved. ๐