SMC - How to get battery status from serial port

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

rbrglez
Cadet
0 Likes
3
631

SMC - How to get battery status from serial port

I have SMC1000IC. I can connect to UPS through Serial port or USB port with PowerChute Business Edition and I can get battery status from web interface.

In my application I can't use PowerChute. I need to get information if UPS is powered from Battery or AC and information if battery is empty. Is this possible?

 

 

 

Tags (1)
3 Replies 3
Ghoster
Crewman
Crewman
0 Likes
2
360

Re: SMC - How to get battery status from serial port

Enable advanced menu, then see if there is a Modbus function you can enable, if it's possible then you can communicate using Modbus RTU over the serial.

Tags (1)
BillP
Administrator Administrator
Administrator
0 Likes
1
328

Re: SMC - How to get battery status from serial port

@Ghoster 

 

SMC model UPS do not support Modbus. The SMT model Smart-UPS do.

 

See Schneider Electric "Modbus Implementation in APC Smart-UPS."

 

 

Tags (1)
rbrglez
Cadet
0 Likes
0
319

Re: SMC - How to get battery status from serial port

@BillP do you maybe know what kind of protocol does SMC1000IC use on Serial port(port next to Network port)?