Posted: 2026-02-26 06:31 AM
How do I reset the date from the front panel on an Smart UPS SMX1000C? I replaced the batteries. I can see the date in the configuration menu, but it will not give an option to change the date. I am not able to connect to it with a computer because I don't have one.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-02-26 08:01 AM
Disconnect the Anderson battery connector from the RBC. Wait for the system to declare a battery fault and wait another ten seconds.
Reconnect the Anderson battery connector and you should see the LCD prompt you to confirm if this is a new RBC.
Toggle from No to Yes then enter the month and year and hit save / enter.
Complete the process by manually initiating a self test and let pass and RBC return to 100% charge.
Finalize by manually initiating a battery calibration with a minimum of 30% attached load or more. Allow the process to complete and the RBC to recover to 100% (SOC) State of Charge.
This will allow the system to learn the current battery health and better reflect the operational runtime on the LCD, NMC, Power Chute, Smart Connect.
Questions Ask - If not and this answered your question please mark this reply as a solution to help the next person asking the same. 👍
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2026-02-26 08:01 AM
Disconnect the Anderson battery connector from the RBC. Wait for the system to declare a battery fault and wait another ten seconds.
Reconnect the Anderson battery connector and you should see the LCD prompt you to confirm if this is a new RBC.
Toggle from No to Yes then enter the month and year and hit save / enter.
Complete the process by manually initiating a self test and let pass and RBC return to 100% charge.
Finalize by manually initiating a battery calibration with a minimum of 30% attached load or more. Allow the process to complete and the RBC to recover to 100% (SOC) State of Charge.
This will allow the system to learn the current battery health and better reflect the operational runtime on the LCD, NMC, Power Chute, Smart Connect.
Questions Ask - If not and this answered your question please mark this reply as a solution to help the next person asking the same. 👍