Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Refurbed unit with site wiring fault

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: Refurbed unit with site wiring fault
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
150
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS for Home and Office Forum
Start a Topic
JCDinPGH
JCDinPGH
Explorer

Posted: ‎2026-09-01 11:51 PM

0 Likes
3
93
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-09-01 11:51 PM

Refurbed unit with site wiring fault

I purchased a refurbed SMT1500RM2U from Newegg and after setting it up, it has a site fault error. I tested the plug with a multimeter and it does not appear to have any issues. I tested

hot neutral (120v)

Hot ground (120v)

Neutral ground (0v). 

Status via SSH says "Online, site wiring fault" which I also see in the log. The error only appears once and does not seem to repeat unless I unplug the UPS and plug it back in. There is no load on it at all right now. 

So a few questions:

Does this mean it is faulty and shipped broken?

Is it still  useable? 

Besides returning it, is there anything I can do to try and fix it? 

Pretty unhappy that a "new to me" UPS has errors. 

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Home & Office - UPS & Software
  • Tags:
  • english
  • smt1500rm2u
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
Teken
Teken
Champion

Posted: ‎2026-09-02 09:52 AM

0 Likes
0
89
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-09-02 09:52 AM

If you haven’t reviewed these APC FAQ and resource guide do so now:

 

https://www.se.com/us/en/faqs/FA158817/

 

To be more specific besides measuring the voltage on all connections. You’ll want to verify all connections are tight and the ground is present, connected at the outlet and breaker.

 

As a sanity check you can move the unit to other outlets in the home and repeat the test. If the problem goes away that outlet / branch circuit needs to be inspected until you identify the root cause.

 

If however all outlets in the home show the same problem then the possibility of a actual fault is present. You can rule this out by installing the unit at another location for a quick test.

 

Ask a neighbor to borrow a outdoor outlet and power the unit from there. If the problem remains then it’s more likely the unit is defective with a couple caveats.

 

That would be the the system is in a unknown state. If so complete a brain dead reset following this APC FAQ:

 

https://www.se.com/th/en/faqs/FA334795/

If the problem is resolved move on. If the problem is (NOT) solved by completing a brain dead reset then the last remedy is to update the UPS Firmware.

 

Assuming it’s not on the latest firmware release. Keeping in mind this procedure should not be initiated unless the device is under warranty!

 

Given, this device is used and refurbished the serial number will reflect a out of warranty period (3) years from the date of purchase.

 

If you want to throw caution to the wind and proceed anyways you may follow all the steps and requirements as outlined in this UPS Firmware Guide:

 

https://www.se.com/us/en/faqs/FA164737/

 

The only procedure you’ll follow and use is via direct connection with the supplied APC Proprietary RJ50 -> DB9 Serial cable.

 

The UPS ID can be viewed and confirmed via LCD About. If there’s a NMC the About UPS. In Power Chute the same information is available.

 

Lastly, the UPS ID is imprinted on MCU chip on the main board. It will also indicate what the factory UPS Firmware was at the time of production and release.

 

Lastly, if a cursory validation as outlined above shows the same wiring fault. Save your time and return the hardware for another.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

JCDinPGH
JCDinPGH
Explorer

Posted: ‎2026-09-07 07:02 AM

0 Likes
1
47
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-09-07 07:02 AM

Well I did test the unit by plugging into a different plug in the house which is on a different circuit breaker and it had the same error. I also took my multimeter and tested both plugs for any signs of voltage irregularities, and both plugs were 100% clean. It definitely looks like the unit is faulty. I contacted Newegg and they have started the refund process as I am returning the unit. I did a factory reset on it but hopefully the vendor doesn't try to resell it again to someone else. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: ‎2026-09-08 05:24 AM

In response to JCDinPGH
0 Likes
0
43
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-09-08 05:24 AM

If you decide to purchase a similar unit let me know the final outcome.

 

Lastly, if the previous replies helped in resolving the issue even if it wasn’t a positive outcome please mark it as a solution to help the next person asking the same.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore