Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Question with APC BACK-UPS ES 500VA 230V

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: Question with APC BACK-UPS ES 500VA 230V
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2130
UnexpectedBill_apc
Captain UnexpectedBill_apc
88
voidstar_apc
Janeway voidstar_apc
83
Techie_apc
Admiral Techie_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
xtianemindfreak_apc
Crewman xtianemindfreak_apc
Crewman

Posted: ‎2021-06-29 04:19 AM

0 Likes
6
263
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 04:19 AM

Question with APC BACK-UPS ES 500VA 230V

This was originally posted on APC forums on 9/11/2010


I have bought my APC BACK-UPS ES 500VA 230V 2 months ago.,, the first month im using the ups is great but now im having problem w/ it

I need to use my PC around 6am after I plug the UPS and my additional extension to the outlet,
and after I turn on the UPS IT SIGNALS the "4 continuous beep every 30 seconds" it signs that the UPS is using battery power and is not plugged up in the socket
I'm trying to on and off it until it produces a snap sound indicating normal operation/ getting power from the socket

my question is why is the UPS signals that he using battery power and not/need to be plugged up to the utility socket while it is plugged up?
" the ulitity socket is working fine" A electric fan is also plugged up and running normaly



this is the exact UPS that im using at home
http://www.apc.com/resource/include/techspec_index.cfm?base_sku=BE500R-PH

Message was edited by: xtianemindfreak

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
xtianemindfreak_apc
Crewman xtianemindfreak_apc
Crewman

Posted: ‎2021-06-29 04:19 AM

0 Likes
0
263
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 04:19 AM

This was originally posted on APC forums on 9/12/2010


I have bought my APC BACK-UPS ES 500VA 230V 2 months ago.,, the first month im using the ups is great but now im having problem w/ it

I need to use my PC around 6am after I plug the UPS and my additional extension to the outlet,
and after I turn on the UPS IT SIGNALS the "4 continuous beep every 30 seconds" it signs that the UPS is using battery power and is not plugged up in the socket
I'm trying to on and off it until it produces a snap sound indicating normal operation/ getting power from the socket

my question is why is the UPS signals that he using battery power and not/need to be plugged up to the utility socket while it is plugged up?
" the ulitity socket is working fine" A electric fan is also plugged up and running normaly



this is the exact UPS that im using at home
http://www.apc.com/resource/include/techspec_index.cfm?base_sku=BE500R-PH

Message was edited by: xtianemindfreak

See Answer In Context

Reply
Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:19 AM

0 Likes
0
263
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 04:19 AM

This reply was originally posted by Jonathan on APC forums on 9/14/2010


You are welcome. In the event that you'll experience a problem with any of your APC units, feel free to call our Phillippine Support Team.

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:19 AM

0 Likes
0
263
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 04:19 AM

This reply was originally posted by Jonathan on APC forums on 9/13/2010


Hello Christian,

Whenever our BackUPS are turned on the unit performs a self-test first before going Online. Within this self-test period the UPS transfer to battery to test it after the self-test the unit should transfer back to Online. Do you need to unplug/replug the UPS multiple times to make it work? Let us check first if it lies with the self-test process.

I see from your profile that you are from the Philippines. Feel free to contact our Philippine Support Group at:
* Call us at toll free 1800 144 10535
* For Globe Subscribers, please \\ call +6346437 3288
* For Blackberry mobile users enter the numbers \\ directly into your mobile when calling the toll free number. Thank you.
* E-mail: asetech@apcc.com
* Business Hours: 9:00AM-6:00PM Monday-Friday

Reply
xtianemindfreak_apc
Crewman xtianemindfreak_apc
Crewman

Posted: ‎2021-06-29 04:19 AM

0 Likes
0
263
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 04:19 AM

This was originally posted on APC forums on 9/14/2010


thanks sir.,, Ive used it again today and its not like the other times that he is beeping up that signal its not plugged.,, ill just monitor it again maybe tomorrow
Ive also read the 16 seconds I called it POST "power on self test" and in my past experience while the UPS is performing the POST it is not beeping like the one that im
experiencing this past weeks

thanks again sir for the response

Reply
xtianemindfreak_apc
Crewman xtianemindfreak_apc
Crewman

Posted: ‎2021-06-29 04:19 AM

0 Likes
0
263
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 04:19 AM

This was originally posted on APC forums on 9/18/2010


Sir just want to consider what my Instructor said "He his a computer engineering instructor" I've told him also about my problem at the UPS
then he told that it is maybe the wire is loose.,E

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:19 AM

0 Likes
0
263
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 04:19 AM

This reply was originally posted by Jonathan on APC forums on 9/20/2010


The battery wire is the one that might get loose. A lot of things can happen on the unit. You can also check the APC Knowledge Base articles I have provided below.

* [A Back-UPS Product would not turn on|http://nam-en.apc.com/app/answers/detail/a_id/70/kw/Reasons%20a%20back-UPS%20Will%20Transfer%20to%20...]
* [Back-UPS Installation questions and answers|http://nam-en.apc.com/app/answers/detail/a_id/6788/kw/Reasons%20a%20back-UPS%20Will%20Transfer%20to%...]

Reply
xtianemindfreak_apc
Crewman xtianemindfreak_apc
Crewman

Posted: ‎2021-06-29 04:19 AM

0 Likes
0
264
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 04:19 AM

This was originally posted on APC forums on 9/12/2010


I have bought my APC BACK-UPS ES 500VA 230V 2 months ago.,, the first month im using the ups is great but now im having problem w/ it

I need to use my PC around 6am after I plug the UPS and my additional extension to the outlet,
and after I turn on the UPS IT SIGNALS the "4 continuous beep every 30 seconds" it signs that the UPS is using battery power and is not plugged up in the socket
I'm trying to on and off it until it produces a snap sound indicating normal operation/ getting power from the socket

my question is why is the UPS signals that he using battery power and not/need to be plugged up to the utility socket while it is plugged up?
" the ulitity socket is working fine" A electric fan is also plugged up and running normaly



this is the exact UPS that im using at home
http://www.apc.com/resource/include/techspec_index.cfm?base_sku=BE500R-PH

Message was edited by: xtianemindfreak

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc