Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner
  • companyImpact

Proper voltage to Yamaha digital piano with Line-R

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: Proper voltage to Yamaha digital piano with Line-R
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2130
UnexpectedBill_apc
Captain UnexpectedBill_apc
88
voidstar_apc
Janeway voidstar_apc
83
Techie_apc
Admiral Techie_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Zeke77_apc
Crewman Zeke77_apc
Crewman

Posted: ‎2021-06-29 08:03 PM

0 Likes
3
294
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 08:03 PM

Proper voltage to Yamaha digital piano with Line-R

This was originally posted on APC forums on 7/6/2009


Hi,

I am using an international Yamaha digital Piano that has a selectable voltage switch. The four voltage positions are 110, 127, 220, and 240 volts.

My home voltage in Nevada as confirmed with a meter nominally runs at 122 volts.

I purchased an APC Line-R 1200 with user selectable input voltages of 110, 120, and 127 volts to see if I could better control the voltage into the piano.

I set the input voltage to 127 volts, to match the piano's 127v position, however, the output from the Line-R remains at 122 volts, no voltage boost. The Line-R voltage display on the front displays "green" normal and the piano works fine. Will the slightly lower output voltage from Line-R harm the piano?

I also tried setting the input voltage to 110 volts on the Line-R. In this mode the unit does in fact step down the voltage to 110 volts (confirmed by meter) however, a yellow light appears on the front indicating high input voltage. The piano now receiving spot on input voltage with it's selector switch set to 110v. I guess my question is this, will it hurt to have the Line-R run in it's corrective state for a long period of time? The unit is running very cool and all appears to be normal other than the yellow light indicating high input voltage.

Lastly, is it a problem to just set the Line-R to 120 volts and set the piano to 110 volts? I am a little worried of running 122 volts into a 110 volt transformer.

Thank you, just trying to protect a $3500 piano.

Message was edited by: Zeke77

Message was edited by: Zeke77

Labels
  • Labels:
  • Universal Transfer Switch
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Zeke77_apc
Crewman Zeke77_apc
Crewman

Posted: ‎2021-06-29 08:03 PM

0 Likes
0
294
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 08:03 PM

This was originally posted on APC forums on 7/7/2009


Thank you for the reply's and thanks for the info on digital power supply sensitivity. That eases my mind a bit. I do have the Line-R plugged into a 4000 joule surge protector. I think I will set everything to 127 volts since it is closest to my home voltage. I knew the Line-R output voltage regulation wasn't very tight before buying but was surprised to see no boost at all on 127 but spot on trim at 110. However, it is in fact operating within spec. Thanks again!

See Answer In Context

Reply
Share
Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:03 PM

0 Likes
0
294
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 08:03 PM

This reply was originally posted by Angela on APC forums on 7/7/2009


i just know it boosts or trims the voltage by a certain percentage, noted in the manual:

http://www.apcmedia.com/salestools/ASTE-6Z7V37_R0_EN.pdf

Reply
Share
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-29 08:03 PM

0 Likes
0
294
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 08:03 PM

This was originally posted on APC forums on 7/7/2009


Digital power supplies aren't very sensitive to the input voltage. I think you'll be fine with the piano set to 127, line voltage at 122, and a good surge protector to keep the $3500 investment safe. The Line-R set to 120 would work fine as a surge protector. I'm not sure if there's any issues with setting it to 110... perhaps someone else here knows more.

Reply
Share
Zeke77_apc
Crewman Zeke77_apc
Crewman

Posted: ‎2021-06-29 08:03 PM

0 Likes
0
295
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-06-29 08:03 PM

This was originally posted on APC forums on 7/7/2009


Thank you for the reply's and thanks for the info on digital power supply sensitivity. That eases my mind a bit. I do have the Line-R plugged into a 4000 joule surge protector. I think I will set everything to 127 volts since it is closest to my home voltage. I knew the Line-R output voltage regulation wasn't very tight before buying but was surprised to see no boost at all on 127 but spot on trim at 110. However, it is in fact operating within spec. Thanks again!

Reply
Share
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc