Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PowerChute Serial Shutdown 1.5 – Outlet Restart Delay Limit (300s) Too Restrictive

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • PowerChute Serial Shutdown 1.5 – Outlet Restart Delay Limit (300s) Too Restrictive
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
144
Techie_apc
Techie_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
NotOnSugarMountain
NotOnSugarMountain
Explorer

Posted: ‎2026-06-28 04:06 PM

0 Likes
3
115
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-06-28 04:06 PM

PowerChute Serial Shutdown 1.5 – Outlet Restart Delay Limit (300s) Too Restrictive

I am using PowerChute Serial Shutdown v1.5 with an APC SRT2200 XLA UPS over USB.

The maximum “Outlet Group Off Time” when utility power is restored of 300 seconds is insufficient for me because:

  • The UPS battery is deeply discharged before shutdown
  • My utility power is unstable 
  • Systems require recharge buffer before safe restart

I think the old Business Edition allowed significantly longer delays. Why set a maximum of 5 minutes before powering the UPS outlets? The UPS battery needs more time to recharge before handling my workstation load again. 

 

Is there a workaround?

 

Labels
  • Labels:
  • Home & Office - UPS & Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Teken
Teken
Champion

Posted: ‎2026-07-02 03:26 AM

In response to NotOnSugarMountain
0 Likes
0
91
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-07-02 03:26 AM

Yes, the LCD Menu will need to be changed from Standard to Advanced.

 

You may refer to the full users manual here:

 

https://download.schneider-electric.com/files?p_enDocType=User+guide&p_File_Name=JGNY-9U4AMZ_R1_EN.p...

 

Turn on with delay has a maximum duration of 30 minutes but may be enough time for your personal environment.

 

Minimum return runtime offers you up to 546 minutes of adjustment. I suggest you play with a combination of the following to see how it works and if it meets your requirements.

 

In some installations we only use specific features such as delay, minimum return, load shed. Other environments we use a combination of 2-3 of these to meet specific goals and targets.

 

The only thing I can’t stress enough is to test and validate the settings actually work in your environment.

 

Keep in mind if you have extended battery packs connected. You’ll really need to put pen to paper and discuss what is realistic for the business vs uptime etc.

 

Questions Ask . . . 👍

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Teken
Teken
Champion

Posted: ‎2026-06-30 05:31 AM . Last Modified: ‎2026-06-30 06:16 AM

0 Likes
0
112
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-06-30 05:31 AM . Last Modified: ‎2026-06-30 06:16 AM

I would define the Minimum Return Runtime via Outlet Group Configuration instead on the UPS. Then disable the Power Chute Option and test / validate this meets your needs.

 

You’ll obviously need to balance, document and communicate the new behaviour. As the clients may vary well freak out thinking whatever is connected to the UPS is dead.

 

When in fact the system is simply waiting to achieve the user defined charged value. This is exacerbated by the fact when the RBC is nearing EOL the time to achieve the defined charged value level will fluctuate.

 

Meaning it can take minutes to hours to achieve the user defined charge level before the outputs will engage.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

NotOnSugarMountain
NotOnSugarMountain
Explorer

Posted: ‎2026-07-01 04:25 PM

0 Likes
1
95
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-07-01 04:25 PM

Teken, I like your idea, but...

 

While in PCSS, I can configure Outlet Group 1 and 2 independently in its Windows browser UI. But when I go to the SRT UPS Display, neither the Control menu nor the Config menu display either Outlet Group 1 or 2 submenus. That's probably why I can't find "Minimum Return Runtime" anywhere?
As a sidenote, in Control > UPS, neither "Turn On Immediately" nor "Turn On With Delay" are displayed. I was thinking that "Turn On With Delay" could be a 2nd best substitute for your "Minimum Return Runtime"
Is there an "Advanced" menu I need to unlock, or what is going on?

My firmware is 16.5 ID:1043, as displayed in the About menu.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: ‎2026-07-02 03:26 AM

In response to NotOnSugarMountain
0 Likes
0
92
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-07-02 03:26 AM

Yes, the LCD Menu will need to be changed from Standard to Advanced.

 

You may refer to the full users manual here:

 

https://download.schneider-electric.com/files?p_enDocType=User+guide&p_File_Name=JGNY-9U4AMZ_R1_EN.p...

 

Turn on with delay has a maximum duration of 30 minutes but may be enough time for your personal environment.

 

Minimum return runtime offers you up to 546 minutes of adjustment. I suggest you play with a combination of the following to see how it works and if it meets your requirements.

 

In some installations we only use specific features such as delay, minimum return, load shed. Other environments we use a combination of 2-3 of these to meet specific goals and targets.

 

The only thing I can’t stress enough is to test and validate the settings actually work in your environment.

 

Keep in mind if you have extended battery packs connected. You’ll really need to put pen to paper and discuss what is realistic for the business vs uptime etc.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore