Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Power-factor-corrected (PFC) inrush question based on power supply specs

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Power-factor-corrected (PFC) inrush question based on power supply specs
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
101
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 02:27 AM . Last Modified: ‎2024-03-22 02:31 AM

0 Likes
7
2444
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:27 AM . Last Modified: ‎2024-03-22 02:31 AM

Power-factor-corrected (PFC) inrush question based on power supply specs

As I understand it, when calculating the power requirement for a power-factor-corrected (PFC) power supply, you consider the maximum rating of the power supply as briefly being required from the UPS during power on.

For example, I have an Antec Earthwatts EA-380. Its rated power is 380 W, and it is PFC. That means it could require 380 W / (power factor) / (efficiency) from the UPS. The efficiency specification I read on the box is "Up to 85%", and there is an "80 Plus Certified" label on the box. So let's say the efficiency is 80%. Power factor is claimed "Up to 99%". So let's say the power factor is 96%. Therefore the calculation would be:
380 W / 0.96 / 0.8 = 495 W.

However, among the specifications on the box are these items:
Inrush current: 60 A @ 115 V, 120 A @ 230 V
Input current: 6 A @ 115 V, 3 A @ 230 V

This is confusing to me. I would be using this in a 115 V AC environment, so we can skip the 230 V specs. The "Input current" results in 6 A * 115 V = 690 VA. That seems quite different from the 495 W calculated above. Furthermore, the "Inrush current" results in ten times that amount, or 6900 VA -- and I was thinking of the 495 W as representing the brief inrush upon power-on.

Given these specs and calculations, what is the best way to approach this for UPS sizing?

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 02:28 AM . Last Modified: ‎2024-03-22 02:31 AM

0 Likes
0
2443
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:28 AM . Last Modified: ‎2024-03-22 02:31 AM

As I understand it, when calculating the power requirement for a power-factor-corrected (PFC) power supply, you consider the maximum rating of the power supply as briefly being required from the UPS during power on.

For example, I have an Antec Earthwatts EA-380. Its rated power is 380 W, and it is PFC. That means it could require 380 W / (power factor) / (efficiency) from the UPS. The efficiency specification I read on the box is "Up to 85%", and there is an "80 Plus Certified" label on the box. So let's say the efficiency is 80%. Power factor is claimed "Up to 99%". So let's say the power factor is 96%. Therefore the calculation would be:
380 W / 0.96 / 0.8 = 495 W.

However, among the specifications on the box are these items:
Inrush current: 60 A @ 115 V, 120 A @ 230 V
Input current: 6 A @ 115 V, 3 A @ 230 V

This is confusing to me. I would be using this in a 115 V AC environment, so we can skip the 230 V specs. The "Input current" results in 6 A * 115 V = 690 VA. That seems quite different from the 495 W calculated above. Furthermore, the "Inrush current" results in ten times that amount, or 6900 VA -- and I was thinking of the 495 W as representing the brief inrush upon power-on.

Given these specs and calculations, what is the best way to approach this for UPS sizing?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:28 AM . Last Modified: ‎2024-03-22 02:31 AM

0 Likes
0
2444
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:28 AM . Last Modified: ‎2024-03-22 02:31 AM

Your original calculation should be fine. That 60A inrush doesn't make much sense, considering your 120v outlet will have a 15A (20A tops) breaker.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-29 02:28 AM . Last Modified: ‎2024-03-22 02:31 AM

0 Likes
0
2444
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:28 AM . Last Modified: ‎2024-03-22 02:31 AM

There is one electronic component inside computer PSUs that is called thermistor. The purpose of a thermistor is to limit the inrush current of the power supply when it is energized. A thermistor works by limiting the current when it is cold and rapidly heats up allowing current to pass through it freelly, it is a temperature variable resistor so to speak. Without the function of a thermistor the inrush current could reach those 60 to 120A figures we can usually see on the psu data sheet and it can acctually reach those figure for a very short time when there is a brief power cut, let's say, 60 miliseconds. When the power returns the thermistor didn't have the time to cool itself down for a moment, so as to return to its initial current limiting state that only kicks in when the PSU is de-energized for a few seconds to one minute. The good news is an UPS will never allow the PSU to be more than 10ms without power, so the inrush current will never be above the maximum input current, which in the given exemple is 6A @ 115V.

Current surges is one of the causes of death of power supplies. When the power goes out for let's say 60 miliseconds and comes back on after that, a huge current surge can happen and blow the fuse inside a PSU or damage it completly and can also cause a circuit breaker in the braker panel to trip. So it is unlikely you'll ever see a 60A inrush current when your computer PSU is plugged to an UPS. To me that's the main protection one UPS can give to a PSU since the thermistor inside all of them is not capable of limiting the current when the PSU not allowed to cool down for a few seconds before the it is re-energized.

All ATX PSU is required to be self sufficient for 16.6ms without power running @ full load. So let's say it is running @ half load, the 16.6ms figure will now be something like 33ms. So, the longer the brief powercuts are, the bigger the inrush curren can be. There is a limit for that, since a 20 seconds power cut can be enough for the thermistor to cool itself down a bit, enough to limit the initial current to a safe value. The "danger" zone would be the "milisecond zone" without power.

Message was edited by: rau

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-29 02:28 AM . Last Modified: ‎2024-03-22 02:31 AM

0 Likes
0
2444
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:28 AM . Last Modified: ‎2024-03-22 02:31 AM

So you are saying that the duration of power cuts that represents the maximum transfer times of typical UPS units (around 10 mS) would result in only the input current (6 A) demanded by the PSU, but not some higher amount up to the inrush current (60 A)?. If that is the case, then how does one know the time frame involved for which the actual inrush current applies? In other words, if I understand you correctly:

- if there is no power outage, the PSU's demand current is just its typical demand, namely the typical load plus some overhead for the PSU

- if there is a short power outage to the PSU, < 10 mS due to the presence of a UPS, you say the PSU will demand something less than its specified input current, 6 A in this case.

- if there is a longer power outage to the PSU, 60 mS to a few seconds, the PSU will demand current up to its specified inrush current, 60 A in this case.

- if a power outage to the PSU is longer than a few seconds, the thermistor will limit its input current, so when power returns to the PSU its current demand will be low and increase gradually.

It seems that my choices are to find either a UPS that can handle the full input current at 6 A * 115 V = 690 VA (and which does not necessarily have overload protection for inrush currents), or choose something like a SmartUPS that is smaller (than the seemingly oversized 690 VA for just a 380 W power supply) -- but large enough to handle average power loads -- because the SmartUPS would have some form of overload protection to deal with the large input current. Is that correct?

Message was edited by: Theorem

Message was edited by: Theorem

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-29 02:28 AM . Last Modified: ‎2024-03-22 02:31 AM

0 Likes
0
2444
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:28 AM . Last Modified: ‎2024-03-22 02:31 AM

The maximum inrush current depends on many things. It depends on the technical project of the PSU, the characteristics of its current limiting system, it depends on the discharging characteristics of the PSU bulk capacitors, the load on the PSU and even the returning point of the sinewave. If for exemple the returning point of the sinewave entering the PSU capacitors is exactly the peak of the sinewave, then the possibility for a big inrush current to happen is high. The 60A maximum inrush current of your PSU is what the manufacturer has found its PSU is capable of drawing very briefly at the worst case scenario, which will never happen if you have a UPS since 10ms of transfer time, which is usually lower than that, is not enough for fully discharging the PSU bulk capacitor.
How these numbers and times are defined I can't tell you for sure, but I have some documents here that show a few charts of inrush current X time caracteristcs of electronics like TV, monitors and computer PSUs and 10ms is not enough time for causing big inrush currents.

@ www.innovolt.com you can find current surge and voltage surge protectors that limit the current surges no matter what at about 10A maximum in the event of very brief power cuts. And no, I have nothing to do with them, I just found their product when I was searching on google about inrush current a couple of years ago.

Message was edited by: rau

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-29 02:28 AM . Last Modified: ‎2024-03-22 02:31 AM

0 Likes
0
2444
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:28 AM . Last Modified: ‎2024-03-22 02:31 AM

Inrush current is the peak current drawn by the power supply when it is plugged in and internal capacitors are charged.

When you try to cold start from a UPS, it may cause the UPS to trip, or the UPS might just provide less than the power supply will draw during the start up surge and work just fine. If the source can continue to provide lower current without tripping, the power supply should work fine.

Motor loads on other hand may not start if the source can't provide enough inrush current. For example, an air conditioner may run at 6A, but require 30A inrush. The compressor probably couldn't start up against the refrigerant pressure if the source can only provide 10A.

Message was edited by: KVAr

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-29 02:28 AM . Last Modified: ‎2024-03-22 02:31 AM

0 Likes
0
2444
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:28 AM . Last Modified: ‎2024-03-22 02:31 AM

The goal is to select a UPS that is not over-sized for a mere 380 W power supply in a computer, and which does not shut down due to inrush current demand from the power supply. As you state, "...UPS might just provide less than the power supply will draw during the start up surge and work just fine" -- which is what most people who are running computer systems would find useful.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-29 02:28 AM . Last Modified: ‎2024-03-22 02:31 AM

0 Likes
0
2444
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:28 AM . Last Modified: ‎2024-03-22 02:31 AM

As I understand it, when calculating the power requirement for a power-factor-corrected (PFC) power supply, you consider the maximum rating of the power supply as briefly being required from the UPS during power on.

For example, I have an Antec Earthwatts EA-380. Its rated power is 380 W, and it is PFC. That means it could require 380 W / (power factor) / (efficiency) from the UPS. The efficiency specification I read on the box is "Up to 85%", and there is an "80 Plus Certified" label on the box. So let's say the efficiency is 80%. Power factor is claimed "Up to 99%". So let's say the power factor is 96%. Therefore the calculation would be:
380 W / 0.96 / 0.8 = 495 W.

However, among the specifications on the box are these items:
Inrush current: 60 A @ 115 V, 120 A @ 230 V
Input current: 6 A @ 115 V, 3 A @ 230 V

This is confusing to me. I would be using this in a 115 V AC environment, so we can skip the 230 V specs. The "Input current" results in 6 A * 115 V = 690 VA. That seems quite different from the 495 W calculated above. Furthermore, the "Inrush current" results in ten times that amount, or 6900 VA -- and I was thinking of the 495 W as representing the brief inrush upon power-on.

Given these specs and calculations, what is the best way to approach this for UPS sizing?

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of