Please help, ES-350 won't keep computer on during power dip/outage

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: Please help, ES-350 won't keep computer on during power dip/outage
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-29 01:46 AM . Last Modified: β€Ž2024-03-22 03:06 AM

0 Likes
5
2092
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 01:46 AM . Last Modified: β€Ž2024-03-22 03:06 AM

Please help, ES-350 won't keep computer on during power dip/outage

My husband and I both have one of these, same model, same configurations. The power dips often where we are. Only difference is my UPS intervenes to keep my computer on and his doesn't.

We've tried the lamp test with his UPS unplugged - battery works a-ok.

I noticed tonight that he had the UPS connected to the computer via a powered USB hub that was not being powered by the UPS. Thinking "Ah Ha!" I plugged the hub into the UPS instead, but I was bitterly disappointed. It still failed to keep the computer on. So I connected the UPS directly into a USB slot in the back of the computer. No difference -- when I unplug the UPS his computer still goes off.

Husband runs XP home edition and the latest available powerchute personal edition. The only things plugged into the battery/surge sockets on the UPS are his cpu and monitor. The battery says it has 22 minutes' worth of charge and I've now officially run out of ideas. Can anyone help?

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Techie_apc
Sisko Techie_apc
Sisko

Posted: β€Ž2021-06-29 01:46 AM . Last Modified: β€Ž2024-03-22 03:06 AM

0 Likes
0
2092
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 01:46 AM . Last Modified: β€Ž2024-03-22 03:06 AM

Mary,

I did read what you wrote before. As I said in my earlier response that the UPS runtime depends upon the equipment power consumption which you plug into the battery backup outlets. Please view my above posts to know the UPS runtime at half and full load. You stated that that the unit did pass the load test. So it indicates that the battery is fine in the unit. In my opinion, there is no other advice available to get more runtime if the equipment power consumption is close to the Back UPS ES 350 full rated capacity.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Techie_apc
Sisko Techie_apc
Sisko

Posted: β€Ž2021-06-29 01:46 AM . Last Modified: β€Ž2024-03-22 03:06 AM

0 Likes
0
2092
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 01:46 AM . Last Modified: β€Ž2024-03-22 03:06 AM

Mary,

The Back UPS ES 350 UPS is basic backup model which can handle up to 200 Watts/350 VA on the battery backup outlets. The UPS runtime depends upon the load you plug into the Battery Backup outlets. This UPS estimated battery runtime is 9.7 minutes at 100 watts and 2.3 minutes at 200 Watts.

May I know the Power Consumption(Watts or Input current) of the CPU and Monitor? You can find these details on the equipment power specification or from the Manufacturer. How much runtime do you require in the event of power problems?

The correct runtime will not be calculated properly with the ES 350, unless the unit is on battery. After operating on battery for brief periods of time, it calibrates the UPS to reflect the runtime more accurately. Depending on the power factor of the computer system, the runtime may be a little lower than expected.

Secondly, Verify that your equipment plugged into the Battery Backup outlets does not exceed the VA rating or Watt rating by using APC's UPS Sizing Tool at www.apcc.com/sizing

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 01:46 AM . Last Modified: β€Ž2024-03-22 03:06 AM

0 Likes
0
2092
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 01:46 AM . Last Modified: β€Ž2024-03-22 03:06 AM

Thanks for replying so quickly. The LCD monitor's power consumption is 38W. I'm having trouble finding info for the computer and I really don't want to open it up. But judging from what I read about the P4 processor, it's got to be at least 275W. I should mention this computer used to be mine and is about 5 years old. When I had it it was hooked up to the same ES-350 I'm using now along with a big old CRT monitor, and I had no problems during power dips.

We don't require much runtime on the battery as outright lengthy power outages are not very common. It just needs to keep the computer running when the power dips, taking over for a few moments and then going back to AC power the way mine does. At the moment it's like taking the power cord for his computer out of the wall -- it just crashes in the middle of whatever he's working on.

I appreciate your help. As is the case with so many people right now, if it's at all possible we'd like to avoid throwing money we don't have at this. πŸ™‚

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: β€Ž2021-06-29 01:46 AM . Last Modified: β€Ž2024-03-22 03:06 AM

0 Likes
0
2092
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 01:46 AM . Last Modified: β€Ž2024-03-22 03:06 AM

Mary,

I suspect that the Back UPS ES 350 UPS is not capable of supporting your Computer and Monitor during power problems or blackout. Please be aware that the size of the UPS that you require depends upon the equipment power draw and your need. My suggestion for you is that purchase another higher VA rating UPS which can support your load. You may utilize the UPS selector tool to choose the correct model that suits your need.

If you want to check if the Back UPS ES 350 UPS battery is fine, then you may perform a pull plug test. Make sure that the battery is charged fully. And then connect a non critical load like a lamp, with a watt rating between 60-100 Watts. Then disconnect the UPS from the wall outlet and check the runtime manually. As such with 100 watts, it should provide a runtime of 9.7 minutes. This test will help you to determine if the issue lies with the battery or the equipment requires higher VA rating UPS. I hope that it helps.

Have a nice day!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 01:46 AM . Last Modified: β€Ž2024-03-22 03:06 AM

0 Likes
0
2092
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 01:46 AM . Last Modified: β€Ž2024-03-22 03:06 AM

Did you even read what I wrote? I said I'd already tried the plug test with a lamp and it passed.

I also said I used the same model UPS when the computer was mine and I was putting a higher load on it. It should work now.

Again, we are unable to afford to replace the UPS at this time. I would appreciate if you could offer some advice other than buy a new/more expensive one.

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: β€Ž2021-06-29 01:46 AM . Last Modified: β€Ž2024-03-22 03:06 AM

0 Likes
0
2093
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 01:46 AM . Last Modified: β€Ž2024-03-22 03:06 AM

Mary,

I did read what you wrote before. As I said in my earlier response that the UPS runtime depends upon the equipment power consumption which you plug into the battery backup outlets. Please view my above posts to know the UPS runtime at half and full load. You stated that that the unit did pass the load test. So it indicates that the battery is fine in the unit. In my opinion, there is no other advice available to get more runtime if the equipment power consumption is close to the Back UPS ES 350 full rated capacity.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore