Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PCPE 3.1 Power Consumption Threshold [AUTO RESET]

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: PCPE 3.1 Power Consumption Threshold [AUTO RESET]
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
147
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS for Home and Office Forum
Start a Topic
fcouperus
fcouperus
Explorer

Posted: ‎2022-11-25 08:36 AM

0 Likes
5
1947
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-25 08:36 AM

PCPE 3.1 Power Consumption Threshold [AUTO RESET]

The default power consumption threshold of the Master Outlet used to trigger on/off of the secondary outlets defaults to 25w.  However, when the laptop enters a non-sleep low power state (below 25w) the secondary outlets of external monitor and  Dell Thunder Dock are powered off.  Setting the power consumption threshold to 10w overcomes the problem but is silently and unpredictably restored to 25w by unknown events or causes.  Can't find where the setting is stored in either the Win10 registry or .inf files.

 

Where is the setting stored and what events cause it to be reset 

Labels
  • Labels:
  • Home & Office - UPS & Software
  • Tags:
  • english
  • pcpe
  • threshold
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 5
JonPro
JonPro Troubleshooter
Troubleshooter

Posted: ‎2022-12-12 11:13 PM

0 Likes
4
1839
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-12-12 11:13 PM

Hi @fcouperus 

 

Thank you for reaching out to the SE Community, my name is Jon and I will assist you with this query.  Apologies for the inconvenience this has caused.

 

I have not encountered this kind of issue with our UPSs that have the Master Control feature.  May I please know if the PowerChute software was running when the threshold was restored?

 

I do not have access to PowerChute software but I believe there are files that can be found inside the installation folder.

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

fcouperus
fcouperus
Explorer

Posted: ‎2023-10-23 11:44 PM

In response to JonPro
0 Likes
3
1634
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-10-23 11:44 PM

Didn't get a notice that you had replied.

 

Powerchute likely was running or starting while booting.  I suspect that when I reboot and return to operating the resident machine in a docked state (where the UPS (model BR1000G) is detected active on a connected USB port) powerchute resets to the default power consumption threshold value of 25W for the BR1000G model.

 

Just can' find where this is in the decision logic of the powershute code but it is registry stored at:

[HKEY_LOCAL_MACHINE\SOFTWARE\WOW6432Node\APC\PowerChute Personal Edition\3.1.0\Settings]
"ClientLoadThreshold"=dword:00000019

 

Reply

Link copied. Please paste this link to share this article on your social media post.

WatchObservatory
WatchObservatory
Explorer

Posted: ‎2023-10-25 04:45 AM

In response to fcouperus
0 Likes
2
1609
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-10-25 04:45 AM

I have the same problem - my earlier reply that never made it on the server:

PCPE 3.1 Power Consumption Threshold
Hello, this occurs to me too. PowerChute personal edition 3.1.0. The ACP is a Back-UPS XS 1500G, firmware 866.L9.D. Despite setting the level to 10W from 25W, it goes back to the 25W setting eventually. I have not found when, but it can be as quick as a few minutes, to weeks. When it does occur, its most annoying as when the laptop batteries are fully charge, the current used drops under 25W causing the APC to shut power to the utility plug, and on a multi-display setup windows moves all apps to the laptop screen, resizing all, not to mention the loss of other devices from the power down.

Reply

Link copied. Please paste this link to share this article on your social media post.

fcouperus
fcouperus
Explorer

Posted: ‎2024-02-19 09:38 AM

In response to WatchObservatory
0 Likes
1
1437
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-19 09:38 AM

in Win10 I have a ".reg" file which I run to reset the PowerChute personal edition 3.1.0 system registry value back to "10".  The registry file has one line in it:

 

[HKEY_LOCAL_MACHINE\SOFTWARE\WOW6432Node\APC\PowerChute Personal Edition\3.1.0\Settings]
"ClientLoadThreshold"=dword:0000000a

Reply

Link copied. Please paste this link to share this article on your social media post.

WatchObservatory
WatchObservatory
Explorer

Posted: ‎2024-02-20 04:52 AM

In response to fcouperus
0 Likes
0
1428
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-20 04:52 AM

Thanks for reg.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore