Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PC shutting off while plugged into BackUPS ES 750 battery outlets

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: PC shutting off while plugged into BackUPS ES 750 battery outlets
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2151
Teken
Teken
156
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:39 AM . Last Modified: ‎2024-03-22 03:12 AM

0 Likes
1
1314
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:39 AM . Last Modified: ‎2024-03-22 03:12 AM

PC shutting off while plugged into BackUPS ES 750 battery outlets


Hey everyone, Ive run into an issue with my BackUPS ES 750 unit. Ive only had it for a few months and up until today, its been working flawlessly (switched over to battery a few times for short intervals and worked like a charm). Today, my pc started to just shut off after only a couple of minutes. After some testing, I narrowed it down to happening only if the pc is plugged into one of the battery outlets on the APC. If I move it to the surge outlets, it runs fine. Ive had this pc plugged into the battery outlets the whole time up to this point, so it isnt a new addition.

The light on the apc stays a solid green the whole time this happens, not reacting as if it has switched to battery or anything. I also have my monitor on a battery backup outlet and it remains on when the pc shuts off, so the issue seems limited to the pc. I also tried unplugging the apc from the wall and letting it just run on battery. I then plugged the pc back into a battery outlet and ran it. It seemed to run a little longer, but it shut off after a short time (there was still about 10 minutes left before shut down indicated by the PowerChute software). Looking at the log in PowerChute shows nothing out of the ordinary just before the crash.

The PC is using a Seasonic SS-430HB power supply (430W Active PFC) and I did read about the PFC issue these units can have, so Im wondering if that could be causing this. If it is, then its obvious that this apc is inadequit for the pc right? The only reason I would question that is since it has handled the pc fine for months and only now shows an issue. Can this problem occur after a time or would this issue happen immediately usually? Im trying to rule out that the apc is defective for whatever reason. If it is a PFC issue, would I be right in assuming that I would need to get a back up unit capable of handling ~540W? (430x1.25)

Thanks for the help.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Techie_apc
Techie_apc
Contributor

Posted: ‎2021-06-29 01:39 AM . Last Modified: ‎2024-03-22 03:11 AM

0 Likes
0
1314
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:39 AM . Last Modified: ‎2024-03-22 03:11 AM

Rick,

I assume that you are using the BE750G(Back UPS ES 750) UPS to protect your PC and Monitor. Let me collect some more information from you to understand what is going on with the UPS. How long does the UPS run the PC after it is started? Is the PC hard shutting down or shutting down gracefully? What is the UPS runtime showing on software? If possible, could you please perform a pull plug test again and provide us the result?

1. Please make sure that the PC and Monitor are plugged into the battery backup outlets(FYI..Master Controlled outlets are not Battery outlets).
2. Stimulate a Power Failure by unplugging the UPS from the wall.
3. And then check if the PC works fine when the UPS transfers from On line to On Battery.

The BE750G UPS can support up to 450 Watts / 750 VA on the battery backup outlets. If the equipment connected to the UPS exceeds its capacity, it will be overloaded. If it is overloaded, the unit will emit a constant beep with Solid Power On LED-ON.

Secondly, I always refer the below document to our Customers in order to size proper UPS for Computers with active PFC Power Supplies.
http://www.apcmedia.com/salestools/RMUZ-7DTKRC_R1_EN.pdf

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
Techie_apc
Techie_apc
Contributor

Posted: ‎2021-06-29 01:39 AM . Last Modified: ‎2024-03-22 03:11 AM

0 Likes
0
1314
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:39 AM . Last Modified: ‎2024-03-22 03:11 AM

Rick,

I assume that you are using the BE750G(Back UPS ES 750) UPS to protect your PC and Monitor. Let me collect some more information from you to understand what is going on with the UPS. How long does the UPS run the PC after it is started? Is the PC hard shutting down or shutting down gracefully? What is the UPS runtime showing on software? If possible, could you please perform a pull plug test again and provide us the result?

1. Please make sure that the PC and Monitor are plugged into the battery backup outlets(FYI..Master Controlled outlets are not Battery outlets).
2. Stimulate a Power Failure by unplugging the UPS from the wall.
3. And then check if the PC works fine when the UPS transfers from On line to On Battery.

The BE750G UPS can support up to 450 Watts / 750 VA on the battery backup outlets. If the equipment connected to the UPS exceeds its capacity, it will be overloaded. If it is overloaded, the unit will emit a constant beep with Solid Power On LED-ON.

Secondly, I always refer the below document to our Customers in order to size proper UPS for Computers with active PFC Power Supplies.
http://www.apcmedia.com/salestools/RMUZ-7DTKRC_R1_EN.pdf

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore