Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84713members
354108posts

Overload Protector button stays out and no power

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

Solved
PappaYeti_apc
Cadet
0 Likes
3
189

Overload Protector button stays out and no power

This was originally posted on APC forums on 1/26/2011


I have a problem with a SUA750XL with an extra battery option.
The unit is "new" to me but has been in use for a few years I guess.

As far as I can tell it will work on battery when it is turned on but external power will not reach the unit (=Power is never indicated).
I notice that the Overload Protector button in the rear is out and cannot be reset to "in" position.

Does anyone have an idea how to get the UPS working? Do I need a new "button" and if so where do I get one?
This is a private project so I would very much like to have the thing working without spending a fortune so ideas are really appreciated.

Message was edited by: PappaYeti

Message was edited by: PappaYeti


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
189

Re: Overload Protector button stays out

This reply was originally posted by Angela on APC forums on 1/26/2011


well i would assume you tried multiple outlets? also, do you see a green sensitivity LED illuminated when you have the UPS connected to a known good outlet? there is a little white button next to the LED that you can push to see if the LED comes on. that would indicate the UPS sees incoming power.

See Answer In Context

3 Replies 3
BillP
Administrator Administrator
Administrator
0 Likes
0
189

Re: Overload Protector button stays out

This reply was originally posted by Angela on APC forums on 1/26/2011


how far out is the overload protector sticking out? i believe this is for the output and not the input so it should not prevent incoming power from reaching the unit, only output power.

it is normal for the button to be sticking out about 1/4" and be a little "loose" if you touch it. if it is actually tripped, it should be out 1 1/4"

PappaYeti_apc
Cadet
0 Likes
0
189

Re: Overload Protector button stays out

This was originally posted on APC forums on 1/26/2011


Thank you.
It sticks out some 5-6 mm (=approx 1/4 inch) so it should be OK then.

I still have to figure out why my input 220V is not indicated. All I see is that it runs on battery and that the battery is low.

Guess I have to open the box and try to follow the leads to see if I get some bright ideas.

BillP
Administrator Administrator
Administrator
0 Likes
0
190

Re: Overload Protector button stays out

This reply was originally posted by Angela on APC forums on 1/26/2011


well i would assume you tried multiple outlets? also, do you see a green sensitivity LED illuminated when you have the UPS connected to a known good outlet? there is a little white button next to the LED that you can push to see if the LED comes on. that would indicate the UPS sees incoming power.