Posted: β2026-10-28 01:22 PM
I have a new BN1500M2. It chirps every 2 seconds which is a signal that the battery is disconnected. Before I open and try to re-seat the battery, is it possible that this chirping is expected in a new unit - maybe until the battery is charged? All diagnostics appear to be fine.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2026-11-01 01:34 PM
Following up again, I tested different configurations and discovered that the beep I heard only happened when the display interface is turned on. When off, there was no sound. I don't actually need the interface on for day-to-day use, and the sound is not that loud anyway. Unless someone is interested in the logs, I will call this solved. It is just a little strange, but the device appears to be working fine.
Thanks for your follow ups.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2026-10-29 12:43 AM
I would confirm both battery terminals (Positive Red & Negative Black) are fully seated and firmly in place. Next, document what the front LCD indicates as the battery (RBC) charge level is and battery voltage. If the unit is connected to a computer running APC Power Chute Software (PCSS / PCPE) then share the logs from the system and upload the same to the APC Forum for review:
https://www.se.com/ca/en/faqs/FA159672/
NOTE: The system should be allowed to fully charge for a minimum of 24 hours or ideally 72 hours without any connected loads. Please also confirm the battery (RBC) installation date via PCSS and provide the serial number for the (UPS) unit you have on hand.
Questions Ask . . . π
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2026-10-29 02:46 AM
Teken,
Thanks for responding. I have re-seated the battery, and the chirp has stopped. That appears to have been the issue. But now I hear an internal beep every 5 seconds. I hear it even if I mute the system. It is a bit annoying since I am in a small office.I did not hear that sound in my previous APC UPS. Do you have any idea if that will stop?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2026-10-30 03:07 AM
As stated previously the RBC must be allowed to fully charge for a minimum of 24 hours if the battery is partially discharged.
If the RBC is fully discharged it may take up to 72 hours for it to be fully charged. Connect the unit to a computer running APC Power Chute Software (PCSS / PCPE) and screen capture what the system indicates as the current battery voltage and state of charge (SOC).
There will also be a data tab which should display the battery voltage gradually increasing over time in SOC.
Confirm this is indeed the case . . .
The front of the LCD Menu should also indicate the RBC SOC and battery voltage confirm what it says.
Lastly, if after 72 hours you still hear this none documented beeping than proceed to complete a brain dead reset as outlined by this APC FAQ 2 times:
https://www.se.com/us/en/faqs/FA158947/
NOTE: Please screen capture the battery installation date and serial number from PCSS. Seeing the logs from PCSS would be helpful in determining the current state of health and active fault / error code.
Questions Ask . . . π
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2026-10-31 10:42 AM
Teken,
I have started all over. I disconnected all devices and have the unit running now, and there is no beeping. I will let it charge for a while and then introduce devices one by one to see if something triggers the annoying sound.
The unit came almost fully charged, and the instructions did not indicate that I should charge it first, but per your suggestion, I am doing it in the proper order.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2026-11-01 01:34 PM
Following up again, I tested different configurations and discovered that the beep I heard only happened when the display interface is turned on. When off, there was no sound. I don't actually need the interface on for day-to-day use, and the sound is not that loud anyway. Unless someone is interested in the logs, I will call this solved. It is just a little strange, but the device appears to be working fine.
Thanks for your follow ups.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2026-11-03 05:28 AM
Great to hear Rock On . . . π€
Link copied. Please paste this link to share this article on your social media post.
Youβve reached the end of your document