My new Back-UPS 1500 smells

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • My new Back-UPS 1500 smells
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 01:44 AM . Last Modified: ‎2024-03-27 03:24 AM

0 Likes
7
3192
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:44 AM . Last Modified: ‎2024-03-27 03:24 AM

My new Back-UPS 1500 smells

I purchased a new Back-UPS 1500 to supplement my 6-year-old one, for which I purchased a new battery at the same time. Unfortunately the new unit has a very strong smell. I thought it would perhaps burn off and have had the unit on for about ten days now, but the smell is  as strong as ever.

I never had this problem with the old one, and the new battery is also fine, but the new unit stinks to the point that it is unusable. What can I do?

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • bad
  • smell
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 01:44 AM . Last Modified: ‎2024-03-27 03:19 AM

0 Likes
0
3191
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:44 AM . Last Modified: ‎2024-03-27 03:19 AM

I agree some "new electronics smell" may be normal the first few days but it shouldn't be bothersome and last for a long time. I'd contact technical support and see if they will provide you with a replacement of further steps that you can do to about the smell (though I can't imagine we can offer anything beyond a replacement).

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 01:44 AM . Last Modified: ‎2024-03-27 03:19 AM

0 Likes
0
3191
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:44 AM . Last Modified: ‎2024-03-27 03:19 AM

I also have a similar experience here. I purchased 1500 XS from OfficeMax and out of the box it had a really nasty smell. I plugged it I and the smell is filling up the whole room. I can't describe the smell other than a strong and rather sickening electrical fried circuit board type of smell.. If this smell does not to go away in a couple of days, then it is heading back to the store. My previous model, Xs 1000 did not do that. This model is slightly larger and has a built in fan that kicks in when battery mode is activated.

See Answer In Context

  • Tags:
  • 1500xs
  • smell
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 01:44 AM . Last Modified: ‎2024-03-27 03:19 AM

0 Likes
0
3192
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:44 AM . Last Modified: ‎2024-03-27 03:19 AM

I agree some "new electronics smell" may be normal the first few days but it shouldn't be bothersome and last for a long time. I'd contact technical support and see if they will provide you with a replacement of further steps that you can do to about the smell (though I can't imagine we can offer anything beyond a replacement).

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 01:44 AM . Last Modified: ‎2024-03-27 03:19 AM

0 Likes
0
3192
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:44 AM . Last Modified: ‎2024-03-27 03:19 AM

I also have a similar experience here. I purchased 1500 XS from OfficeMax and out of the box it had a really nasty smell. I plugged it I and the smell is filling up the whole room. I can't describe the smell other than a strong and rather sickening electrical fried circuit board type of smell.. If this smell does not to go away in a couple of days, then it is heading back to the store. My previous model, Xs 1000 did not do that. This model is slightly larger and has a built in fan that kicks in when battery mode is activated.

  • Tags:
  • 1500xs
  • smell
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 01:44 AM . Last Modified: ‎2024-03-27 03:18 AM

0 Likes
0
3191
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:44 AM . Last Modified: ‎2024-03-27 03:18 AM

I know this post is quite old... Did this smell ever go away?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 01:44 AM . Last Modified: ‎2024-03-27 03:18 AM

0 Likes
0
3191
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:44 AM . Last Modified: ‎2024-03-27 03:18 AM

No it didn't. We ended up returning the unit. I found that getting a replacement battery for my old unit works just fine, but for some reason the new units have a real stink. I guess it doesn't bother some people. We couldn't live with it. . .

  • Tags:
  • Stinky
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 01:44 AM . Last Modified: ‎2024-03-27 03:18 AM

0 Likes
0
3191
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:44 AM . Last Modified: ‎2024-03-27 03:18 AM

Thanks for the response. Take a look at this post before they delete it smile. Same issue and returned it as well. I am looking for an alternative. This UPS worked great as a mosquito killer, I swear!

http://forums.apc.com/spaces/4/back-ups-surge-protectors/forums/general/12058/apc-ups-br1500va/1#555...

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 01:44 AM . Last Modified: ‎2024-03-27 03:18 AM

0 Likes
0
3191
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:44 AM . Last Modified: ‎2024-03-27 03:18 AM

Hi, The new link you added doesn't go anywhere so I guess they deleted it!

Reply

Link copied. Please paste this link to share this article on your social media post.

mitsmith_apc
Lt. Commander mitsmith_apc
Lt. Commander

Posted: ‎2021-06-28 01:45 AM . Last Modified: ‎2024-03-27 03:18 AM

0 Likes
0
3191
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:45 AM . Last Modified: ‎2024-03-27 03:18 AM

Hi Gopa,

Try clicking the hyperlink below. The post is up. 

link to post

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of