Model BE500Y-IN: Dies after 4-5 min with no low battery warning

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

Solved
arupmi_apc
Cadet
0 Likes
2
82

Model BE500Y-IN: Dies after 4-5 min with no low battery warning

This was originally posted on APC forums on 8/13/2008


I have purchased a UPS Model BE500Y-IN last week. After initial charging for one day, I tried it out -- the UPS transfers to battery without problems, but after about 4 min, it shuts down without any low battery warning. After this, the status LED flashes red and green alternately each second. Can anyone please tell me why this is happening?

Once utility power becomes available, the UPS automatically does the self test successfully. If the power goes off again, it can again function for 4-5 min. and then shuts down abruptly. Currently, I have just connected a DSL modem to the UPS outlet, and working with a laptop connected to the surge-protection only outlet.


Accepted Solutions
TheNotoriousKMP_apc
Sisko
Sisko
0 Likes
0
82

Re: Model BE500Y-IN: Dies after 4-5 min with no low battery warning

This was originally posted on APC forums on 8/13/2008


Hello,

What is the Watt consumption of the DSL modem? Based on what you're describing, it may be less than 50W. A Back-UPS will not operate on battery with less than a 50W load, as the UPS will not sense it is powering anything, and power itself off.

See Answer In Context

2 Replies 2
TheNotoriousKMP_apc
Sisko
Sisko
0 Likes
0
83

Re: Model BE500Y-IN: Dies after 4-5 min with no low battery warning

This was originally posted on APC forums on 8/13/2008


Hello,

What is the Watt consumption of the DSL modem? Based on what you're describing, it may be less than 50W. A Back-UPS will not operate on battery with less than a 50W load, as the UPS will not sense it is powering anything, and power itself off.

arupmi_apc
Cadet
0 Likes
0
82

Re: Model BE500Y-IN: Dies after 4-5 min with no low battery warning

This was originally posted on APC forums on 8/13/2008


Thanks a ton!!! You were right on the dot.

I connected my laptop as well to the battery backup outlet so that the load is over 50W, and now it's working fine -- I just tested it.

Thanks again and regards.