Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Firmware distribution does not match target device platform...

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: Firmware distribution does not match target device platform...
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2151
Teken
Teken
156
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2022-07-14 04:44 AM

0 Likes
6
22091
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-14 04:44 AM

Firmware distribution does not match target device platform...

Hi,

 

when I saw the problems with the batteries I thought it would also be the right time to update firmwares.

 

One UPS got a AP9630 and the other a AP9631.  Both seem to have the same firmware file named "apc_hw05_aos708_sumx708_bootmon109.exe".  Currently we are still running SUMX 6.5.0, AOS 6.5.0 and Boot Monitor 1.0.8 on both of them.

 

When I run the upgrade utility I get these messages on both UPS:

 

[Date-Time]  Unable to update device IP with Boot Monitor, stopping all further processing of this device!

[Date-Time]  Uploading firmware file 1 of 3: Boot Monitor to IP, please wait...

[Date-Time]  Firmware distribution does not match target device platform; this could be due to a corrupt distribution.

[Date-Time]  NMC Firmware Update Utility v1.0.4 initialized.

 

Am I using the wrong firmware version?  This is the version that I found and I believe that this is for a AP9630 in a SMT3000RMI2U and a AP9631 in a SMX3000RMHV2U (web site said it is for Smart-UPS and Galaxy 3500).  Am I wrong?  What else might have happend here?

 

The firmware for the SMX3000RMHV2U is UPS 07.4 (ID1003) and for the SMT3000RMI2U it is UPS 09.3 (ID18).  Are these the actual versions or should I upgrade these, too?  Where do I get updated firmware from?  I did not find any.

 

Thanks a lot!

pompfe

 

Labels
  • Labels:
  • Home & Office - UPS & Software
  • Tags:
  • english
  • SMX3000RMHV2U SMT3000RMI2U
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2022-07-26 12:20 PM

1 Like
1
21985
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-26 12:20 PM

After comparing configs, I found it was because the protocol selected for updates was disabled on device in question. After switching the protocol (or enabling the protocol in the NMC2) the updates proceeded. Make sure you have FTP/SCP connectivity using an external client or checking the config before trying the update utility. Hope this helps.

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Anonymous user
Not applicable

Posted: ‎2022-07-26 12:13 PM

0 Likes
0
21988
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-26 12:13 PM

I have the same issue but across 20 UPS I only have 3 or 4 that have the issue. They are the same model and hardware revision (AP9630) and I'm using apc_hw05_aos708_sumx708_bootmon109) and some can update and others cannot. Very strange. Did you find a solution?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2022-07-26 12:20 PM

1 Like
1
21985
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-07-26 12:20 PM

After comparing configs, I found it was because the protocol selected for updates was disabled on device in question. After switching the protocol (or enabling the protocol in the NMC2) the updates proceeded. Make sure you have FTP/SCP connectivity using an external client or checking the config before trying the update utility. Hope this helps.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

robincm
robincm
Explorer

Posted: ‎2023-02-08 04:36 AM

In response to Anonymous user
0 Likes
0
20601
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-02-08 04:36 AM

Yes, this is exactly what it was for me - SSH was disabled. Thank you!

Reply

Link copied. Please paste this link to share this article on your social media post.

Zack
Zack
Explorer

Posted: ‎2024-08-03 06:34 PM

0 Likes
0
13193
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-03 06:34 PM

I discovered that my APC PD8841 was outdated to the point that I needed to configure my SSH settings to use specific ciphers and key exchange algorithms for the firmware update tool to work correctly. Follow the steps below to determine if this issue affects you.

 

1. Attempt to SSH into the APC unit with SSH enabled on the device:

ssh apc@IP_OF_DEVICE

 

2. If you receive an error like "no matching key exchange method found. Their offer: diffie-hellman-group-exchange-sha1,diffie-hellman-group1-sha1" add one of the key exchange algorithms offered to your SSH command and try again:

ssh -o KexAlgorithms=+diffie-hellman-group1-sha1 apc@IP_OF_DEVICE

 

NOTE: If you do not receive an error and instead see a password prompt or an option to add the device fingerprint to your known_hosts, this solution may not resolve your issue.


3. If you then receive another error stating "no matching cipher found. Their offer: aes256-cbc,3des-cbc,blowfish-cbc,arcfour" add one of the ciphers offered to your SSH command and try again. Otherwise, skip to step 4:

ssh -o KexAlgorithms=+diffie-hellman-group1-sha1 -c aes256-cbc apc@IP_OF_DEVICE

 

4. You should now be able to SSH into the device. If successful, create an SSH configuration file named config with no file extension in your user folder $HOME\.ssh. This example assumes you are using Windows, but the process is similar on Linux:

Host IP_OF_DEVICE
    KexAlgorithms +diffie-hellman-group1-sha1
    Ciphers aes256-cbc

 

NOTE: Ensure the file has no file extension; otherwise, SSH will not recognize it. To confirm, open a terminal in the .ssh folder and list the files using ls or dir, depending on your OS.

 

5. Open a new terminal and try to SSH into the device without using any command line arguments. If your SSH configuration file is recognized, you should be able to connect without specifying additional options. If successful, proceed to step 6. If not, further troubleshooting is required:

ssh apc@IP_OF_DEVICE

 

6. With SSH now automatically using these options for your device, try the firmware update utility again. You should now be able to update the firmware.

 

7. After updating the firmware, it is highly recommended that you remove the SSH configuration for this device by deleting the SSH configuration options or file you created in the steps above. If you decide not to remove this, you will continue using outdated ciphers and key exchange algorithms, which pose a security concern.

 

8. The new firmware should now accept the default secure key exchange algorithms and ciphers. To test this, try to SSH into the device again using the standard command with the custom options for this device removed from the SSH configuration file:

ssh apc@IP_OF_DEVICE

 

NOTE:  If you still encounter key exchange or cipher errors, the device will still require the custom SSH configuration options until another firmware update adds support for them.


I hope this helps someone else who encounters a similarly outdated APC unit.

  • Tags:
  • ap8841
  • apc pdu
  • firmware update error
  • firmware update errors
Reply

Link copied. Please paste this link to share this article on your social media post.

bitsnbytes
bitsnbytes
Explorer

Posted: ‎2025-06-27 03:50 AM

0 Likes
0
7454
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-27 03:50 AM

Hello,

i had the same problem. Searched 3 days. No help from the hotline. They just told me this solution posibility here in the user forum. Thats support of a premium manufacturer. Holy...

My Solution was, to use the only the superuser "apc", not selfmade users, even if they are with administration right. The Failure messages are completly wrong and missleading in my case.

A simple hint in the software itself, could save ours of peoples life. "Only use Superuser apc for the Updates". I hate this kind of sloppiness in the complete IT.

I hope it helps someone and saves time.

Best regards,

Reply

Link copied. Please paste this link to share this article on your social media post.

gabriEL13
gabriEL13
Explorer

Posted: ‎2025-12-21 08:20 AM

0 Likes
0
4085
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-12-21 08:20 AM

I found that the best way to upgrade the AP9630 is via CONSOLE cable. APC has a official documentation or  just search TubeYou "Recovering & Uploading Firmware on APC Network Management Card 2 | Schneider Electric Support". It works even with bricked card. Console updating process ,worked for me everytime. 

 

 NMC Firmware Update Utility bricked every AP9630 which I tried to update. Even though I downloaded NMC FUU straight from the official webpage i.e. APC_SUMX_EN-7.2.2.zip for APC SmartUPS SMT750IC

 

. If the NMC FUU complains about "Firmware distribution does not match target device platform" DO NOT CONTINUE THE UPDATE PROCESS IF you don't have console cable at hand or the card is at remote location.

 

Obnova a nahranie firmvéru na kartu APC Network Management Card 2 | Podpora Schneider Electric
 
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore