Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Difference between Backup-UPS and Smart-UPS?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: Difference between Backup-UPS and Smart-UPS?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
150
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:35 PM . Last Modified: ‎2024-03-21 03:36 AM

0 Likes
3
26091
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:35 PM . Last Modified: ‎2024-03-21 03:36 AM

Difference between Backup-UPS and Smart-UPS?

I have a real simple questions for all of you in the know.

What is the differnece between SmartUPS and the BackupUPS.

This is probally answered someplace but for the live of me could not find it...

Thanks a lot

Gary

Labels
  • Labels:
  • Universal Transfer Switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Cap1_apc
Cap1_apc
Contributor

Posted: ‎2021-06-29 06:35 PM . Last Modified: ‎2024-03-21 03:36 AM

0 Likes
0
26072
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:35 PM . Last Modified: ‎2024-03-21 03:36 AM

Hi,

The main difference between the BackUPS and SmartUPS is the UPS topology they are built on.
BackUPS = standby
SmartUPS (SUA units) = line interactive
SmartUPS (SURT units) = double conversion online

Please see the following kbase for a deeper discussion on this:
http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=727&p_created=1010390400&p_...

For simplicity's sake SmartUPS are generally favorable (yet pricier) for the following reasons:
- Faster transfer time to battery
- AVR (automatic voltage regulation) - all SmartUPS have boost and trim features to enhance the quality of utility electric without switching to battery. Note: The BR and BX BackUPS lines also have this
- Better reliability (hence smartups are aimed at server applications, while backups are aimed at workstation computing)
- Higher compatibility w/ generator use
- Ease of interpretation, configuration (all SmartUPS have several LED charts to indicate current status, load, battery charge etc.)

Of course there could be a much more in depth discussion here, but I hope I started you in the right direction

Message was edited by: Cap1

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Cap1_apc
Cap1_apc
Contributor

Posted: ‎2021-06-29 06:35 PM . Last Modified: ‎2024-03-21 03:36 AM

0 Likes
0
26073
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:35 PM . Last Modified: ‎2024-03-21 03:36 AM

Hi,

The main difference between the BackUPS and SmartUPS is the UPS topology they are built on.
BackUPS = standby
SmartUPS (SUA units) = line interactive
SmartUPS (SURT units) = double conversion online

Please see the following kbase for a deeper discussion on this:
http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=727&p_created=1010390400&p_...

For simplicity's sake SmartUPS are generally favorable (yet pricier) for the following reasons:
- Faster transfer time to battery
- AVR (automatic voltage regulation) - all SmartUPS have boost and trim features to enhance the quality of utility electric without switching to battery. Note: The BR and BX BackUPS lines also have this
- Better reliability (hence smartups are aimed at server applications, while backups are aimed at workstation computing)
- Higher compatibility w/ generator use
- Ease of interpretation, configuration (all SmartUPS have several LED charts to indicate current status, load, battery charge etc.)

Of course there could be a much more in depth discussion here, but I hope I started you in the right direction

Message was edited by: Cap1

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:35 PM . Last Modified: ‎2024-03-21 03:36 AM

0 Likes
0
26071
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:35 PM . Last Modified: ‎2024-03-21 03:36 AM

THank you for a response to my question. I have a smartUPS 1000 that has died (I have tried replaing the batteries and it does nothing) so I wanted to purchase new UPS and the backupUPS's are so much less expensive but after reading this, I am thinking that I should just bite the bullet and purchase new SmartUPS...

Thanks again

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 06:36 PM . Last Modified: ‎2024-03-21 03:36 AM

0 Likes
0
26071
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:36 PM . Last Modified: ‎2024-03-21 03:36 AM

Hi,
are there any specific applications, I mean industrial applications where SmartUPS are used? Or what would be some server applications - as you specify - SmartUPS are used in the server applications?
Thanks,
Cory

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore