Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Could this new battery have been stored for too long (9 months) before it was shipped to me?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Could this new battery have been stored for too long (9 months) before it was shipped to me?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
144
Techie_apc
Techie_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS for Home and Office Forum
Start a Topic
Waho
Waho
Explorer

Posted: ‎2026-05-10 10:51 AM

0 Likes
3
251
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-05-10 10:51 AM

Could this new battery have been stored for too long (9 months) before it was shipped to me?

Hello, everyone,

I've just received from Amazon FR a replacement battery (APCRBC124) for my Back-UPS Pro 1500.
We are the 10th of May 2026 and the numbers on the battery label are 5A2528T80755.
The qualifying tests were held on August 7, 2025.
Battery Qualification test.jpg
Is this battery too old, or has it been sitting in a warehouse for too long?
Should I return it to Amazon?
(I haven’t installed it in the Back-UPS yet.)"
Thank you for your advice

Attachments
Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
Teken
Teken
Champion

Posted: ‎2026-05-11 03:14 AM . Last Modified: ‎2026-05-11 03:17 AM

0 Likes
2
248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-05-11 03:14 AM . Last Modified: ‎2026-05-11 03:17 AM

Generally speaking if the RBC is stored at the correct temperature and environmental setting. A high quality RBC will be fine sitting for 12 months on the shelf without being recharged.

 

You can validate this by completing a crude voltage test and report the DC Voltage here. Expectation is the RBC will show at least 12.8 ~ 12.9 VDC.

 

Anything above, such as 13.XX VDC is perfect and indicates a very high quality cell that has been sitting on the shelf for 9 months.

 

Typically you would reference the battery makers specification data sheet as to resting voltage, internal resistance, charging interval, etc.

 

NOTE: Do not accept any RBC that measures a voltage below 12 VDC for a single cell! 

IE: 11.XX VDC or below 

 

Given this is two cells wired in series the DC Voltage will be at least 24 VDC.

 

Questions Ask . . . 👍

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Waho
Waho
Explorer

Posted: ‎2026-05-12 09:34 AM

In response to Teken
0 Likes
1
228
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-05-12 09:34 AM

Dear Teken,
Thank you for your advice.
II measured the voltage across the two series‑connected cells : 25.4V.
I’m relieved. I will keep it.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: ‎2026-05-13 03:45 AM . Last Modified: ‎2026-05-13 03:46 AM

In response to Waho
0 Likes
0
223
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-05-13 03:45 AM . Last Modified: ‎2026-05-13 03:46 AM

As a gentle reminder please also complete the following action items in sequence to obtain the best outcome.

 

RBC: Allow the new RBC to charge for a minimum of 72 hours before you complete the following action items.

 

Date: Ensure you update the RBC installation date via Power Chute Software. This resets internal counters and adjusts charging tables if applicable.

 

Self Test: Manually initiate a self test either through the user interface or via Power Chute. Let pass and allow the RBC to recover 100% SOC (State of Charge).

 

Calibration: Manually initiate a battery calibration via Power Chute with a minimum of 30% connected load or higher. Once complete allow the RBC to recover to 100% SOC.

 

This will allow the system learn the state of health of the new RBC and better reflect the operational runtime more accurately on the LCD, Power Chute.

 

If the previous reply answered your question please do mark it as a solution to help the next person asking the same.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore