Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.
Already have an account? Login
It's your place to connect with experts and peers, get continuous support, and share knowledge.
Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.
You can subscribe to this forum after you log in or create your free account..
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.
Already have an account? Login
Posted: 2021-06-29 10:10 PM
This was originally posted on APC forums on 9/26/2011
Converting Smart UPS into Online UPS (Double Conversion)
Sharing Battery with multiple UPS????
Last night i combined/shared my same batteries among TWO APC Smart UPS of same model (APC Smart-UPS 2700W / 3000VA )
Left one UPS plugged into the socket and the second one was plugged from the socket.The inverter of second UPS continuous run....
My load on 2nd UPS is less than 1000W ( Out Load is two Computers with 21" LCDs and two medical devices)
*Why i did this??*
We have very much problem of power failure in our area i.e about 8hour / day .....so i have to use generator for this propose. But same time is don't need any power interruptions and also need sure sine wave.
So my 1st UPS is getting Power from main supply or Generator .
*Have anybody experience of this?*
*Any problem with mentioned layout?*
*Can it damage it anything... i mean itself (UPS) or Battery or equipment connected to it?*
I am using Car's Wet Battery with my UPS
UPS Model :APC Smart-UPS 2700W / 3000VA (SUA3000RMI2U) 220V
Message was edited by: aar2020
Posted: 2021-06-29 10:10 PM
This was originally posted on APC forums on 5/25/2012
This is a nice idea to convert APC smart UPS to online UPS, By this device we can connect it everywhere. Which inverter you are using for this device?
__________________________________
http://www.backup-power.ca/vaccine_refrigerators.html
Message was edited by: jenifer123
Posted: 2021-06-29 10:10 PM
This was originally posted on APC forums on 9/27/2011
Dear Chris,
Can you tell me is their any inverter difference in my UPS and APC online ups?
Posted: 2021-06-29 10:10 PM
This reply was originally posted by Chris on APC forums on 9/26/2011
Well APC can't speak for this as this of course not how we intend our UPS' used. If anyone does have any experience with this though, feel free to reply.
Posted: 2021-06-29 10:10 PM
This was originally posted on APC forums on 9/27/2011
>
Can you tell me is their any inverter difference in my UPS and APC online ups?
>
Hi Attique,
Every model of UPS that APC produces has an inverter designed specifically for the demands of the UPS. The SmartUPS Line-interactive and Online UPS inverters are almost certainly different designs. For instance, the inverters in UPSes without extended run battery packs (SUA and SMT models) aren't expected to operate beyond a fixed duration, and therefore have thermal design limitations. Extended Run UPSes such as the SMX series have inverters that run longer, but there's no guarantee they would work in an online configuration. Is there a reason you don't want an actual APC Online UPS?
Posted: 2021-06-29 10:10 PM
This was originally posted on APC forums on 9/28/2011
Hi Voidstar,
The reason is very simple …..I just want to use my existing UPS (APC Smart-UPS) & buying new online ups will cost me a lot….and my current UPS will be dumped.
More my load requirement is like below
0. 5~1 kW -- Only Online UPS is acceptable
0.5 kW -- Line Interactive UPS is acceptable
1 kW -- just need power
Power Failure/shut down for Electricity Main Supply is minimum 6 hour and sometimes go to 14 hours. In routine power shut down is split into two hours duration at different fixed timing …. But once a week it is continious
So using only UPS is not suitable+. I tried to use different UPS’s step-up for last two year but my batteries life became every short because they were being recharged about 3~4 times daily ….ultimately its number of life cycle were completed very earlier….I have to shift to generator option.
h2. Now I just want to use what I have and get best out of it
Message was edited by: aar2020
Message was edited by: aar2020
Posted: 2021-06-29 10:10 PM
This was originally posted on APC forums on 9/28/2011
>
The reason is very simple …..I just want to use my existing UPS (APC Smart-UPS) & buying new online ups will cost me a lot….and my current UPS will be dumped.
>
Makes sense. I don't know if your plan to make an online UPS from two line-interactive ones will work. The battery charger on the first UPS might not even be powerful enough to drive the second UPS.
Is there any possibility that your loads where "only online UPS is acceptable" would work on a line-interactive UPS? What do you gain from using an online UPS for those loads?
>
Power Failure/shut down for Electricity Main Supply is minimum 6 hour and sometimes go to 14 hours. In routine power shut down is split into two hours duration at different fixed timing …. But once a week it is continious
So using only UPS is not suitable. I tried to use different UPS’s step-up for last two year but my batteries life became every short because they were being recharged about 3~4 times daily ….ultimately its number of life cycle were completed very earlier….I have to shift to generator option.
>
A generator is the preferred approach if you want longer stay-on times. Alternatively, you could have the computers and the UPSes shut down immediately and conserve battery.
One thing to note on generators: not all produce clean power, and so the UPS may remain on battery while the generator is running. To avoid this, you may want to test the generator under load with the UPS before purchasing. The UPS has a sensitivity setting which can be set to "low" to be less sensitive to the generator. If changing the sensitivity doesn't work, then the only other option I know of is an Online UPS which, by its nature, is less sensitive to generators.
Posted: 2021-06-29 10:10 PM
This reply was originally posted by Dakota on APC forums on 10/6/2011
You Will Kill Your Upses Because The Transformers Aren't Ment To Be Converting Power 24/7
Message was edited by: Wwallender
Posted: 2021-06-29 10:10 PM
This was originally posted on APC forums on 5/11/2012
Its now more than 6months ....and no problem being observed...
in nut shell...the system works
Posted: 2021-06-29 10:10 PM
This was originally posted on APC forums on 5/11/2012
>
Its now more than 6months ....and no problem being observed...
in nut shell...the system works
>
That's awesome!
Posted: 2021-06-29 10:10 PM
This was originally posted on APC forums on 5/25/2012
This is a nice idea to convert APC smart UPS to online UPS, By this device we can connect it everywhere. Which inverter you are using for this device?
__________________________________
http://www.backup-power.ca/vaccine_refrigerators.html
Message was edited by: jenifer123
User | Count |
---|---|
2124 | |
88 | |
83 | |
83 | |
82 | |
79 |
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.