Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Connecting 1 UPS to two PDUs with C19/C20 cables, best practice?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Connecting 1 UPS to two PDUs with C19/C20 cables, best practice?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
144
Techie_apc
Techie_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Related Products
product field
Schneider Electric
Smart-UPS

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS for Home and Office Forum
Start a Topic
jb_dk
jb_dk
Explorer

Posted: ‎2025-11-06 01:48 AM

0 Likes
5
1910
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-11-06 01:48 AM

Connecting 1 UPS to two PDUs with C19/C20 cables, best practice?

Dear forum,

At work we have an APC UPS for our servers, currently it feeds (via a manual transfer switch, MTS) a small horizontal managed PDU.  Power delivery from UPS to MTS to PDU is via standard C19/C20 "cordset" cables.  Now I am looking to design an expansion to have two such PDUs, but the MTS only has a single J (C19) outlet and the question is what is the *correct* way to split the output between 2 PDU C20 inlets here in the EU (230V mains, EU LV directive wiring).

 

Options that seem clear are: A. A C19/C20 Y-cable (seems to be offered by some vendors for the US market, unsure of EU certification).  B. A C13 to C20 cordset if available between an unused C14/F outlet on the MTS (relying on the MTS breaker to limit current to 10A worst case)  C. Purchasing an entirely new unmanaged C19/J PDU to go between the MTS and the managed PDUs.

 

Entire rack setup is multivendor, but the UPS and fixed installation is Schneider/APC products.

One fact was removed because the forum software declared it "banned", even in "Home and Office forum".

Labels
  • Labels:
  • Home & Office - UPS & Software
  • Tags:
  • c20
  • cabling
  • english
  • pdu
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 5
Teken
Teken
Champion

Posted: ‎2025-11-06 04:41 AM

0 Likes
3
1905
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-11-06 04:41 AM

I would suggest you sit down pen to paper and determine the following. As knowing these important facts will dictate what the next steps are:

 

Load: The UPS must not exceed 80% of its rated capacity.

 

Runtime: The extra connected loads will impact the operational runtime. As such you better validate all the servers / VM have enough time to complete their grace full shutdown.

 

Current: This goes hand in hand with the load and must not exceed the 80% threshold. It’s imperative that you measure the inrush current for all new devices.

 

Failure to do so will result in the UPS shutting down / dropping the load.

 

Temperature: If the system is not in a climate controlled and managed environment. You risk shorter battery life and possible shutdown due to elevated internal temperature.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

jb_dk
jb_dk
Explorer

Posted: ‎2025-11-06 08:05 AM

In response to Teken
0 Likes
1
1896
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-11-06 08:05 AM

The 80% rule is a known oddity of the US National Electric Code, not applicable in the rest of the world.  I don't think it is a misfeature of APC UPSes sold in Europe.

The total load is always something to watch and is currently way below 50%, including a temporary PDU solution for most of the devices that will use the second standard PDU.   Temperature regulation is also installed and watched.

 

And once again, the censorship software installed on this forum refuses a completely meaningful sentence that I then had to remove.

 

Now please return to the question asked about wiring up the power cables under EU, not US, rules.

Reply

Link copied. Please paste this link to share this article on your social media post.

jb_dk
jb_dk
Explorer

Posted: ‎2025-11-06 08:07 AM

In response to Teken
0 Likes
0
1896
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-11-06 08:07 AM

Teken's answer is entirely off topic and also seems specific to US electrical code not relevant here in the EU.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: ‎2025-11-06 09:54 AM

In response to jb_dk
0 Likes
0
1886
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-11-06 09:54 AM

The 80% rule is not an oddity of North America.

 

It’s a well established and fundamental understanding of electricity, safety, and operational standards acknowledged world wide! ☝️

 

You don’t have to take my word for it you can refer to this APC FAQ or any electrical code in the world:

 

https://www.se.com/us/en/faqs/FAQ000268376/

 

My initial reply to you are the most basic things that must be considered along with many others.

 

It’s quite obvious to me you’re well past your depth as it relates to these basic concepts. 🤦‍♂️

 

Your fixation on wiring vs performing an energy audit clearly indicates this task be given to someone else with more basic understanding of power management, electrical codes, and conformance with established standards.

 

Feel free to load that UPS to 100% and let me know what the outcome is. 😂

Reply

Link copied. Please paste this link to share this article on your social media post.

jb_dk
jb_dk
Explorer

Posted: ‎2025-11-13 12:13 AM

0 Likes
0
1802
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-11-13 12:13 AM

Just to clarify, I am not asking about the size or capacity of the UPS or other equipment, as those are all well in hand, 80% preference from FAQ000268376 or not.

 

I am asking which of 3 cabling options for connecting two managed PDUs to a single standalone Transfer Switch (powered from a UPS) is best practice IN EUROPE.

  • Option A: Find a C19/C20 Y cable that has CE certifications.
  • Option B: Use a C14/E to C19 cable such as APC model AP9878 to connect the second PDU to a C13/F outlet on the Transfer Switch (or UPS) .
  • Option C: Use an additional unmanaged PDU between the transfer switch (or UPS) single C19/J outlet and the C20 inlets on the managed PDUs .
  • Non-option due to product availability: Find a single managed PDU with 20+ outlets that fits mechanically.

Once again the forum software bans some technical words without linking to specific reasons or rules.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore