Communication to UPS

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: Communication to UPS
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
123
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-29 01:18 AM . Last Modified: β€Ž2024-03-22 03:27 AM

0 Likes
9
1569
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 01:18 AM . Last Modified: β€Ž2024-03-22 03:27 AM

Communication to UPS

I have a BP700UC. I am aware that there are several parameter that can be read/set using Powerchute Personal Edition from Windows. Unfortunately the versions for Mac are old and don't allow this.

Is there any documentation on the communication protocol between the UPS and the PC? If documented it is likely I could use the terminal to talk to the UPS and read/set these values.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: β€Ž2021-06-29 01:19 AM . Last Modified: β€Ž2024-03-22 03:27 AM

0 Likes
0
1568
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 01:19 AM . Last Modified: β€Ž2024-03-22 03:27 AM

I had thought about running Win XP on my Intel Mac using boot camp but the price is out of site for Win. The next version of Mac OSX "Snow Leopard" is $29.95 (full version not an upgrade).

I guess I'll just wait for my son to visit. Even though he runs XP I still talk to him πŸ˜‰

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 01:18 AM . Last Modified: β€Ž2024-03-22 03:27 AM

0 Likes
0
1568
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 01:18 AM . Last Modified: β€Ž2024-03-22 03:27 AM

Great, keep us updated.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 01:18 AM . Last Modified: β€Ž2024-03-22 03:27 AM

0 Likes
0
1568
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 01:18 AM . Last Modified: β€Ž2024-03-22 03:27 AM

I have a BP700UC. I am aware that there are several parameter that can be read/set using Powerchute Personal Edition from Windows. Unfortunately the versions for Mac are old and don't allow this.

Is there any documentation on the communication protocol between the UPS and the PC? If documented it is likely I could use the terminal to talk to the UPS and read/set these values.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 01:18 AM . Last Modified: β€Ž2024-03-22 03:27 AM

0 Likes
0
1568
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 01:18 AM . Last Modified: β€Ž2024-03-22 03:27 AM

Don't quite understand. The settings in the UPS are nothing more than values in a PROM or similar chip. All I want to do is read the current values and change one of them. A nice GUI would be great but nothing from APC for a Mac.

Before GUI's this type of thing was done from a terminal. I have a terminal app on my Mac and can access Unix shell scripts directly to do many "primitive" things. All I need is the documentation.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: β€Ž2021-06-29 01:18 AM . Last Modified: β€Ž2024-03-22 03:27 AM

0 Likes
0
1571
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 01:18 AM . Last Modified: β€Ž2024-03-22 03:27 AM

Despite documentation for UPSLink being widely available on the internet, APC's policy is that the UPSLink communication protocol is proprietary.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 01:18 AM . Last Modified: β€Ž2024-03-22 03:27 AM

0 Likes
0
1571
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 01:18 AM . Last Modified: β€Ž2024-03-22 03:27 AM

Hello Robert.

bobsenior wrote:
Is there any documentation on the communication protocol between the UPS and the PC? If documented it is likely I could use the terminal to talk to the UPS and read/set these values.
Unfortunately you do really need to use the PCPE software on a Windows based machine to adjust the settings on your battery Back-UPS. Back-UPS wouldn't work as well with terminal programs such as HyperTerminal or PuTTy..

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 01:18 AM . Last Modified: β€Ž2024-03-22 03:27 AM

0 Likes
0
1571
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 01:18 AM . Last Modified: β€Ž2024-03-22 03:27 AM

Thanks. I was told in another thread that the BP700UC sensitivity was adjustable via Powerchute using Win. I know that the "Smart" UPS's are adjustable. Can you verify that the BP700UC is also.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 01:19 AM . Last Modified: β€Ž2024-03-22 03:27 AM

0 Likes
0
1571
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 01:19 AM . Last Modified: β€Ž2024-03-22 03:27 AM

Robert,

Please see the attached image on this post. This is a screenshot of PowerChute Personal Edition(PCPE) running on a Windows XP machine. Using this software you can plug in your BP700UC and set the Sensitivity settings to either High, Medium or Low.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 01:19 AM . Last Modified: β€Ž2024-03-22 03:27 AM

0 Likes
0
1571
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 01:19 AM . Last Modified: β€Ž2024-03-22 03:27 AM

You are welcome Robert, please do let us know if you were able to adjust the settings of your UPS once you get a hold of a Windows machine.

- JonPro

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 01:19 AM . Last Modified: β€Ž2024-03-22 03:27 AM

0 Likes
0
1569
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 01:19 AM . Last Modified: β€Ž2024-03-22 03:27 AM

I had thought about running Win XP on my Intel Mac using boot camp but the price is out of site for Win. The next version of Mac OSX "Snow Leopard" is $29.95 (full version not an upgrade).

I guess I'll just wait for my son to visit. Even though he runs XP I still talk to him πŸ˜‰

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore