Help
  • Explore Community Expore Community
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Explore Community Explore Community
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • EcoStruxure Asset Advisor
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
    • EcoStruxure IT Help Center
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Can an open ground occurring in an APC product cause static discharge?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Can an open ground occurring in an APC product cause static discharge?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2127
UnexpectedBill_apc
Captain UnexpectedBill_apc
88
voidstar_apc
Janeway voidstar_apc
83
Techie_apc
Admiral Techie_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
agreenberg19_apc
Crewman agreenberg19_apc
Crewman

Posted: ‎2021-06-29 10:45 PM

0 Likes
3
959
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:45 PM

Can an open ground occurring in an APC product cause static discharge?

This was originally posted on APC forums on 9/27/2012


I have had a small music studio for about four years, in my home, in a carpeted room, and I have not had any problems with static electricity until now. The relative humidity in the room averages 50%, so I don't suspect that is contributing to the problem much. I hear a quick 'zap' occasionally when I am playing my electric piano. I suspect that this is happening because the sustain pedal is sitting directly on the carpeted floor and I use the pedal quite a bit.

I installed a static dissipative mat and I still hear the 'zap' at random times. Really perplexed, I disconnected everything from the system except one keyboard, the MacBook, and the FP10 audio interface. I played for hours, using only headphones, and heard no zap. I then plugged in the monitors and eventually heard the zap again. But, the volume of the zap is always the same, regardless of the volume setting on the monitors and/or FP10.

So I took my trusty Greenlee circuit tester and plugged it into every wall outlet in the room. The lights indicated correct power and ground in all cases. Then I plugged the tester into my APC Back-UPS ES 350 battery backup/surge protector. And Lo and Behold (does anybody really say that any more?), when I plugged the tester into one of the outlets on the battery backup/surge protection side, both lights indicating a good connection came on -- and a few seconds later, only the center light shined. The legend on the tester labeled that condition "OPEN GROUND". After 10 seconds or so, the other light came back on. I watched the tester for about 30 minutes, and the light went off and on a few more times.

So, is there an electrician reading this post that could confirm or deny that this could be the source of the zap?

The APC was plugged into the same AC wall outlet as my Furman power conditioner, so could that also contribute to the problem, i.e. does proximity have a bearing on this problem?

Labels
  • Labels:
  • Universal Transfer Switch
  • Tags:
  • discharge
  • ground
  • multimeter
  • open
  • static
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
agreenberg19_apc
Crewman agreenberg19_apc
Crewman

Posted: ‎2021-06-29 10:46 PM

0 Likes
0
956
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:46 PM

This was originally posted on APC forums on 9/28/2012


I'm afraid all that is way over my head. I am a retired computer programmer and an amateur musician, so I basically know how to turn electrical appliances on and off.

I just wanted to know if that change in voltage could cause a static discharge that would be audible in my studio. I have removed the APC unit and, so far, have not experienced any static 'zaps'.

I do appreciate your input.

Alan

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
agreenberg19_apc
Crewman agreenberg19_apc
Crewman

Posted: ‎2021-06-29 10:45 PM

0 Likes
0
956
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:45 PM

This was originally posted on APC forums on 9/27/2012


I plugged a multimeter into the APC's outlet that is suspect. It initially read 117 volts, but after 10 seconds it dropped to 82 volts. A few seconds later, it read 117.

Could this cause the static noise I heard? I'm going to reconnect everything ( except the APC) and test, test, test.

Message was edited by: agreenberg19

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:45 PM

0 Likes
0
956
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:45 PM

This reply was originally posted by Angela on APC forums on 9/28/2012


is it a true RMS voltmeter? did you test it when you put the UPS on battery? i guess can you clarify step by step some steps to replicate what readings you are seeing?

i ask because this sounds a lot like what is here:

http://www.apc.com/site/support/index.cfm/faq/ -> search for FA157483

at the time i post this though, ugh, it appears apc.com is experiencing issues 😞

and i don't know if it is related just yet but we have this information regarding a "floating" ground and it just came to mind when reading your issue:

___________________________________________________________________________________

Although many APC UPS’s have a voltage present between Earth and Neutral while unit is on battery it must be pointed out that these units comply with EN and CE standards.

This issue can be explained as follows:

When the unit is online it is obviously has a Neutral from the supply and in the standard TN network, the Earth and Neutral are at the same potential due to the fact of both are connected at the main distribution board.

However when it goes on battery or should the supply be disconnected, both poles will be disconnected from the supply thus creating an IT system. The supply has then no reference to the earth so the first fault is not a safety hazard.

Types of Wiring Networks:_


TN: System where Neutral an Earth (Ground) are connected. There are variations of this system, see below.

TN-C: System where Neutral an Earth (Ground) are common throughout the system.

TN-S: System where Neutral an Earth (Ground) are separate throughout the system.

TN-CS: System where Neutral an Earth (Ground) are common between substation and the building and separate down stream from the main distribution board. This is one of the most common types of electrical networks.

TT: In this system the Neutral (star-point of the transformer) is connected to Earth (Ground) but there are no further connections between Earth and Neutral downstream. The Earth of the building is connected directly to earth by means of an earth-spike or earth-plate. This system is also sometimes known as direct earthing and needs earth leakage protection.

IT: This system is different to the other systems as no part of the secondary side of the transformer is connected to Earth so that there is a floating earth in such systems. As there is no return path this system is very safe if installed properly. It is used in hospitals, mines and other special areas. It should have Earth Leakage Monitors installed as protection.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

agreenberg19_apc
Crewman agreenberg19_apc
Crewman

Posted: ‎2021-06-29 10:46 PM

0 Likes
0
957
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:46 PM

This was originally posted on APC forums on 9/28/2012


I'm afraid all that is way over my head. I am a retired computer programmer and an amateur musician, so I basically know how to turn electrical appliances on and off.

I just wanted to know if that change in voltage could cause a static discharge that would be audible in my studio. I have removed the APC unit and, so far, have not experienced any static 'zaps'.

I do appreciate your input.

Alan

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc