Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Calibrating new battery. Rundown time acceptable?

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: Calibrating new battery. Rundown time acceptable?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2130
UnexpectedBill_apc
Captain UnexpectedBill_apc
88
voidstar_apc
Janeway voidstar_apc
83
Techie_apc
Admiral Techie_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
shaq.blogs_apc
Ensign shaq.blogs_apc
Ensign

Posted: ‎2021-06-29 08:42 PM

0 Likes
12
674
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 08:42 PM

Calibrating new battery. Rundown time acceptable?

This was originally posted on APC forums on 7/30/2013


I am trying to recalibrate my UPS with a new battery. (One of the issues I face is - UPS Triggers a PC shutdown within a minute of going to battery. After searching around, i found recalibrating UPS with the new battery should fix at least one of the issues i am facing. Hope the other issues go away with this!)

UPS is RS 1500VA / 230V (865W).

I used a resistive load on the UPS consisting of two bulbs in parallel, 200W + 100W (35% of 865W)

Runtime came to about 16.30 min (+/- 30 secs). As per the chart here, for 300W load estimated time is 19min. So the rundown time came to about 85-90% of the estimated time.

This is about (10-15)% variation. Is this fine? or should I recalibrate it again after a full charge?

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • 1500
  • apc
  • battery
  • calibration
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:43 PM

0 Likes
0
673
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 08:43 PM

This reply was originally posted by Angela on APC forums on 8/5/2013


Unfortunately, our schematics are proprietary so you would not be able to get them from us. I am not sure if OS native support would have the same problem but that might be worth a try too.

See Answer In Context

Reply
Replies 12
shaq.blogs_apc
Ensign shaq.blogs_apc
Ensign

Posted: ‎2021-06-29 08:42 PM

0 Likes
0
673
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 08:42 PM

This was originally posted on APC forums on 7/31/2013


anyone that could help out?

I have tried the battery recalibration process, yet the estimated time on PowerChute is not shown. PC shuts down with a minute.

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:42 PM

0 Likes
0
673
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 08:42 PM

This reply was originally posted by Angela on APC forums on 7/31/2013


When you calibrated it, did you leave the USB cable connected? When you do a calibration, you should disconnect everything besides that 30% load that does not fluctuate more than -/+ 5% to ensure accuracy.

Another test I would do is see how long the UPS turns (either before another calibration or as your first step) with no USB cable attached. Maybe do this with a non critical load so your computer does not do a hard shutdown but this will help identify if this is because of the USB connection or if there is an issue with USB runtime.

*EDIT* Maybe I misunderstood - it ran 16 minutes initially with or without the USB cable attached? And now it only runs for one minute with USB attached and doesnt report estimated runtime?

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:42 PM

0 Likes
0
673
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 08:42 PM

This reply was originally posted by Angela on APC forums on 7/31/2013


Can you clarify, is the computer gracefully shutting down? I am pretty sure it is because you said its when a shutdown/hibernate command gets executed.

Anyway, can you confirm in PowerChute what you see for settings under Configuration->Runtime please? See below for the screen I am referencing. The behavior you describes makes it sound like it is set to Preserve Battery Power and shutdown the computer when the UPS has been on battery for one minute. You may just need to re-configure the settings on this screen.

1333_runtime.jpg

Reply
shaq.blogs_apc
Ensign shaq.blogs_apc
Ensign

Posted: ‎2021-06-29 08:42 PM

0 Likes
0
673
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 08:42 PM

This was originally posted on APC forums on 7/31/2013


I disconnected all cables during calibration. Only resistive load of 300W connected, which gave 16-17 mins.

I let the calibration recharge cycle complete. If I Connect just the USB cable (no load), and withing 1 minute, a shutdown /hibernate event gets fired.

Edit: Once I tried connecting, with PC & USB connected to UPS. Again, the shutdown event got fired in less than one minute. I aborted the shutdown, and the UPS gave me at least 45 minutes.

Reply
shaq.blogs_apc
Ensign shaq.blogs_apc
Ensign

Posted: ‎2021-06-29 08:42 PM

0 Likes
0
673
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 08:42 PM

This was originally posted on APC forums on 7/31/2013


Yes. Graceful shutdown triggered in one minute.

here are my screen shots.

1337_Capture.PNG

Until just now, the estimated time wasnt even showing 1 minute.

1341_Capture 2.PNG

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:42 PM

0 Likes
0
673
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 08:42 PM

This reply was originally posted by Angela on APC forums on 8/1/2013


OK, we had some discussion here. We believe the UPS is at fault here and is not calibrating properly.

Can you try a higher load than the 35% you did and disconnect the USB per what you did previously and try one more calibration to see if it updates the runtime on the UPS?

P.S. can you confirm exact model of the UPS from the white sticker on the back? I am guessing it is BR1500I but just want to make sure. Also, how old is the UPS? (the first several digits of the serial number will tell us if you have that i.e. JB0405XXXXX)

Reply
shaq.blogs_apc
Ensign shaq.blogs_apc
Ensign

Posted: ‎2021-06-29 08:42 PM

0 Likes
0
673
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 08:42 PM

This was originally posted on APC forums on 8/1/2013


Model number : BR1500 - IN

Serial Number : EB1049000XXX

It is about 2.5 years since i got it

Reply
shaq.blogs_apc
Ensign shaq.blogs_apc
Ensign

Posted: ‎2021-06-29 08:42 PM

0 Likes
0
673
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 08:42 PM

This was originally posted on APC forums on 8/4/2013


All right. I did a 500W load and runtime came to 8:40 (9.3 min is estimated. Variation of about 1 min or 7%. Variation seems acceptable to me)

Now Letting it charge all night on Zero Load. Will check tomorrow if it has calibrated it right.

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:43 PM

0 Likes
0
672
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 08:43 PM

This reply was originally posted by Angela on APC forums on 8/5/2013


I think the beep is indicating low battery state. To me, this is a UPS issue and nothing to do with PowerChute. The UPS is the one that reports the runtime to the software. So, if the calibrations are not working there is no way really beyond what you've been doing to accomplish a calibration for this type of UPS cry - is it still under warranty?

Reply
shaq.blogs_apc
Ensign shaq.blogs_apc
Ensign

Posted: ‎2021-06-29 08:43 PM

0 Likes
0
672
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 08:43 PM

This was originally posted on APC forums on 8/5/2013


I still have the same problem. I let it recharge for about 18hrs.

I also noticed that, The first couple of times today, when i switched it from AC to battery, it beeped continuously even after I aborted the shutdown.

I reset the UPS power button twice. I switched off for about 20 minutes and the annoying beep is gone. Now it just pops the shutdown button as soon as i switch to battery (It shows shutdown message repeatedly 2-3 times even after i abort it).

Is this a hardware or software issue?

Reply
shaq.blogs_apc
Ensign shaq.blogs_apc
Ensign

Posted: ‎2021-06-29 08:43 PM

0 Likes
0
672
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 08:43 PM

This was originally posted on APC forums on 8/5/2013


It is just out of warranty.

Where can I get hold of the internal circuit diagrams? I have somebody at home who can look into it.

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:43 PM

0 Likes
0
674
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-29 08:43 PM

This reply was originally posted by Angela on APC forums on 8/5/2013


Unfortunately, our schematics are proprietary so you would not be able to get them from us. I am not sure if OS native support would have the same problem but that might be worth a try too.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc