Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Bx950Mi issue with "apcupsd" and "Network UPS Tools (NUT)"

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: Bx950Mi issue with "apcupsd" and "Network UPS Tools (NUT)"
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
150
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS for Home and Office Forum
Start a Topic
abcek
abcek
Explorer

Posted: ‎2026-07-30 06:25 AM

0 Likes
6
347
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-07-30 06:25 AM

Bx950Mi issue with "apcupsd" and "Network UPS Tools (NUT)"

Hi,

 

my APC Back-UPS 950 (IEC) just died (had red "replace battery" led, replaced battery, made 5sec power button reset with battery disconnect and the battery doesn't charge) so i decided to buy a new UPS.

 

as Back-UPS 950 is now discontinued I was inclined to buy a Bx950Mi (IEC).

 

The problem is that I found on different posts in different forums that this new BX___Mi line model allegedly seems to have a flaw in the firmware that makes it unusable with linux using "apcupsd" or "Network UPS Tools (NUT)" because the firmware trough USB report data that push "apcupsd" or "NUT" to trigger a system shutdown event even if the battery is at 95%.

Other user allegedly seems to say that the UPS when start a self test report it in the wrong way trough the usb interface and "apcupsd" or "Network UPS Tools (NUT)" see this as a battery error/battery disconnect.

 

For NUT it seems that developers found some workaround to ignore for a time space of 3 seconds the allegedly wrong data reported by the UPS starting with NUT version 2.8.1 (that ships only with Debian 13 Trixie, If you are on older distro you need to compile yourself).

TrueNAS 25.10.1 is Debian 12 based, so there is no mitigation for NUT on this platform.

 

here is what I'm talking about: https://github.com/networkupstools/nut/issues/2347

 

also allegedly there is this USB data stale issue: https://github.com/networkupstools/nut/issues/2805

 

So I have some question:
1. do you acknowledge your Bx___Mi line has any firmware issue?
2. do you shipped or plan to ship a fixed firmware?

3. it's possible to update the product with the old firmare in the hand of your clients with the new firmware?

4. if NO and I'm buying now the product how can I know it has the new fixed firmware?

4. also if NO, do you plan to issue a recall or a RMA with shipment at your expense to whoever want a unit with the new firmware?

For the value you ask I'd like to buy a product that flawlessy works with "apcupsd" or "Network UPS Tools (NUT)".

I'd like to have an answer and I will not buy a new APC product until these questions find an answer.

 

Please consider users that are using Bx___Mi on linux are allegedly experiencing these issue and are reporting it so if there is an issue with the firmware please don't ignore it, acknowledge it, find a solution and use your PR department to let people know (for example on github NUT issue tracker) you solved this allegedly firmware issue and how to obtain a product with the last firmware.

Thanks.

NUT is not picking up accurate and timely data from APC UPS · Issue #2805 · networkupstools/nut
NUT is not picking up accurate and timely data from APC UPS · Issue #2805 · networkupstools/nut
github.com/networkupstools/nut/issues/2347
I'm using NUT add-on and integration in Home assistant. My UPS is APC BX1200. The integration data is delayed and doesn't update after a certain point. In this situation, the charge level is stuck at 99% while I unplugged the USB and att...
APC Back-UPS BX1600MI spurious LOWBATT/REPLACEBATT events · Issue #2347 · networkupstools/nut
APC Back-UPS BX1600MI spurious LOWBATT/REPLACEBATT events · Issue #2347 · networkupstools/nut
github.com/networkupstools/nut/issues/2805
I have an APC Back-UPS BX1600MI connected by its supplied USB cable. With the version of nut in Debian 10 (2.7.4-8) this was unusable as the usbhid-ups driver kept disconnecting every few seconds. I upgraded to the git HEAD of nut and co...
Labels
  • Labels:
  • Home & Office - UPS & Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
Teken
Teken
Champion

Posted: ‎2026-07-31 05:44 AM

0 Likes
0
340
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-07-31 05:44 AM

Why wouldn’t you simply replace the RBC in the older unit?!?! I’ll assume this specific model APC UPS worked fine on NUT??

 

As to your point about this newer model only hands on testing and validation in your environment will yield the facts.

 

Going off on what’s published on the internet does not offer all the facts or variables at play.

 

Also, the only officially supported software  for any APC UPS is Power Chute Software such as (PCPE, PCSS, PCBE, PCNS).


Any other 3rd party software is based on open source information and the community at large.

 

None of them have standing as it relates to working / not working with a specific APC UPS. As the software is based on what is publicly known and trial / error to break fix issues.

Lastly, it’s highly unlikely you will receive a formal reply to any of your questions in the APC Forum.

 

As an aside, no Back-UPS Series system has field upgradable firmware - None.

 

This ability is present in all current generation of APC Enterprise UPS that encompasses the Smart-UPS Series such as SCL, SMC, SMT, SMX, SRT, SRTL, SRYL, XP, XU.

 

As it relates to a recall based on third party software??? There’s a higher likelihood you’ll be struck by lightning three times in your life before that happens!

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

abcek
abcek
Explorer

Posted: ‎2026-08-17 04:07 AM

0 Likes
1
255
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-08-17 04:07 AM

Thanks for the answer.

 

what do you mean with RBC?

If you meant "Replacement Battery Cartridge" as I already told I already performed a Battery replacement with a new one to fix the issue, but the UPS attached to the main power draw the new battery and turned on the red led "replace battery". This happen because the UPS never start to charge/maintain the battery power.
I read that this issue could be cause by some capacitor on the main board dry out and need to be replaced, as I'm not able to make any soldering, the solution for me was to buy a new one.  On Amazon I found only the new models (and at this point I don't want to buy an older model that now cost more than the new one and has inside a battery that sat on the shelf for a long time)

 

I was using the older unit with apcupsd on Debian.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: ‎2026-08-17 06:44 AM

In response to abcek
0 Likes
0
253
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-08-17 06:44 AM

You haven’t answered the question regarding whether the new UPS operates fine with NUT?!?!

 

As it relates to the old unit not properly charging the RBC. Typically, it’s one or more board level components that are out of tolerance.

 

A quick google search will give you a starting point if you have no board level experience in troubleshooting. Ultimately the model you have is so cheap relative to enterprise hardware it’s easier to just replace the entire unit with new like you did.

 

The only benefit of repairing the old unit is personal knowledge, experience, and restoring something that was broken and using it again.

 

There are several YouTube videos on similar problems and what they found as the problem.

 

It can be as simple as a bad / out of tolerance capacitor, resistor, diode. Capacitors that are out of specification or simply leaking / bursted are easy to identify. Capacitors that are high ESR require a dedicated meter to identify as a basic meter can easily show proper capacitance and still have high ESR.

 

This is why some components must be taken out of circuit and measured with the proper tools and not just a multimeter when the problem is more involved.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

abcek
abcek
Explorer

Posted: ‎2026-08-20 04:19 AM

0 Likes
1
157
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-08-20 04:19 AM

> You haven’t answered the question regarding whether the new UPS operates fine with NUT?!?!

 

What this mean? I never bought a new unit.

Read again my first post: "I was inclined to buy a Bx950Mi (IEC)" ...  "I'd like to have an answer and I will not buy a new APC product until these questions find an answer.".

With these 2 states in my first post I don't see how you assumed I already have a new unit.

 

> "A quick google search will give you a starting point if you have no board level experience in troubleshooting."

 

Thanks that was obvious, I already told you I find what could be the issue.

 

> "Ultimately the model you have is so cheap relative to enterprise hardware it’s easier to just replace the entire unit with new like you did."

 

APC it's not cheap. 120€ for a non pure sine wave UPS without a proper battery slot for easy replacement isn't cheap. Before I buy something I prefer to know if fits my needs (linux compatibility).

 

Please @Teken stop answer to this thread or change attitude as you are not of any help and your comments doesn't add anything to the discussion.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: ‎2026-08-25 04:27 AM

In response to abcek
0 Likes
0
154
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-08-25 04:27 AM

Any lay person reading your initial post would think you had bought a new UPS! Your lack of clarity falls squarely on you.

 

As to the actual fault you haven’t determined what the root cause is because you haven’t even started by measuring the components!

 

Your arrogance is only superseded by your hubris as to laying fault onto others for your lack of understanding and knowledge. ☝️

 

The choices are easy fix the unit if you can.


Buy a new unit that shows wide NUT support or just do nothing and continue to whine about everything.

 

You get what you give and thus far your replies just affirm you’re so out of touch and miserable it’s hard to imagine a positive outcome will be found! 🤦‍♂️👎

Reply

Link copied. Please paste this link to share this article on your social media post.

abcek
abcek
Explorer

Posted: ‎2026-08-25 09:14 AM

0 Likes
0
142
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-08-25 09:14 AM

Your words speak for themselves; instead of stopping posting in this thread, you decided to insult me.

You're the one who's miserable.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore