Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Brand New Back UPS BE650Y-IN "Internal fault" within 24 hrs of purchase

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: Brand New Back UPS BE650Y-IN "Internal fault" within 24 hrs of purchase
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
150
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
BillP
BillP Leader
Leader

Posted: ‎2021-06-29 01:50 AM . Last Modified: ‎2024-03-22 03:02 AM

0 Likes
3
1064
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:50 AM . Last Modified: ‎2024-03-22 03:02 AM

Brand New Back UPS BE650Y-IN "Internal fault" within 24 hrs of purchase

I'm really frustated while typing this post. Bought the UPS on 16th Oct 2009 and charged it for more than 16 hours.Then today 17th Oct 2009 i connected my pc and installed the powerchute software and it displayed "battery charging". The all of a sudden the software displays "There is an internal fault in the battery backup. Call APC customer care and get it replaced ASAP".
I was shocked to see this msg and i called up the customer care number and they told me they will be sending a person to solve the issue after 2 days coz of the weekend. As a past satisfied user of APC i trusted them.But after this issue i may not recommend the product to anyone.

Message was edited by: raj2007

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 01:50 AM . Last Modified: ‎2024-03-22 03:02 AM

0 Likes
0
1064
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:50 AM . Last Modified: ‎2024-03-22 03:02 AM

Hi Raj,
Sorry for the inconvenience caused. I would like to know some basic information of the which will help me resolve the issue. I would suggest you to check the battery connector of the Battery in the UPS is firmly connected to the Battery. This would ensure that the Battery is firmly connected. After confirming the battery connection kindly charge the UPS for 8 Hrs and then run the self test in the Software and let us know the result. Kindly help us with the serial no of the UPS also

Message was edited by: gdevanal

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
BillP Leader
Leader

Posted: ‎2021-06-29 01:50 AM . Last Modified: ‎2024-03-22 03:02 AM

0 Likes
0
1064
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:50 AM . Last Modified: ‎2024-03-22 03:02 AM

got a replacement (brand new) UPS from the dealer and till now everything is fine with no problem.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 01:50 AM . Last Modified: ‎2024-03-22 03:02 AM

0 Likes
0
1064
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:50 AM . Last Modified: ‎2024-03-22 03:02 AM

Please......Waiting for a reply from anyone to cool me down....

Message was edited by: raj2007

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 01:50 AM . Last Modified: ‎2024-03-22 03:02 AM

0 Likes
0
1065
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:50 AM . Last Modified: ‎2024-03-22 03:02 AM

Hi Raj,
Sorry for the inconvenience caused. I would like to know some basic information of the which will help me resolve the issue. I would suggest you to check the battery connector of the Battery in the UPS is firmly connected to the Battery. This would ensure that the Battery is firmly connected. After confirming the battery connection kindly charge the UPS for 8 Hrs and then run the self test in the Software and let us know the result. Kindly help us with the serial no of the UPS also

Message was edited by: gdevanal

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore