New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Blinking red light
APC UPS for Home and Office Forum
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Search in
Improve your search experience:
Exact phraseโUse quotes " "(e.g., "error 404")
WildcardโUse * for partial words(e.g., build*, *tion)
AND / ORโCombine keywords(e.g., login AND error, login OR signโin)
Keep it shortโUse 2โ3 relevant words, not full sentences
FiltersโNarrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2026-08-2803:37 PM
Blinking red light
My Backup UPS 650 has a constantly blinking red light. It shows green when first turned on and then immediately goes to red. There is no alarm being sounded and all items plugged in appear to be properly operating.
Is this something I should be concerned about, and if so, what can/should I do?
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2026-08-3104:09 AM
Based on the limited information provided here it would seem the RBC (Battery) is EOL and needs to be replaced.
Typically a blinking red light indicates during the start up process the self test has failed. In your case the most reasonable explanation is the RBC is expired.
You can confirm all of this by the following these action items:
AC Mains: Disconnect AC Mains from the wall outlet. If the system turns off immediately or in a very short period of time the RBC is EOL.
Power Chute: You may confirm the battery installation date. The RBC is designed to provide 2-5 years of service life based on usage, temperature, and environmental conditions. The raw cells inside are built to sustain 260 cycles subjected to the same caveats as above.
Logs: Power Chute (PSCC) will provide you with more information as to active faults and error codes. It will likely indicate the RBC is EOL.