Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Battery plugged in, battery not detected, no error.

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Battery plugged in, battery not detected, no error.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2151
Teken
Teken
156
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Related Products
product field
Schneider Electric
Back-UPS

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS for Home and Office Forum
Start a Topic
TG_1
TG_1
Explorer

Posted: ‎2026-05-05 01:20 PM

0 Likes
5
2093
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-05-05 01:20 PM

Battery plugged in, battery not detected, no error.

Hello all, I recently got a Back-UPS BX1500M from amazon and have been having issues.


The battery (which is installed correctly, green side on top) has not been showing up in the software and no matter how many times I reinstall the battery, it does not get detected. There aren't any warnings or errors showing up either, and don't know what could be causing this.

Attachments
Labels
  • Labels:
  • Home & Office - UPS & Software
  • Tags:
  • english
  • help
  • support
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 5
Teken
Teken
Champion

Posted: ‎2026-05-06 01:12 AM

0 Likes
2
2089
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-05-06 01:12 AM

Are you sure the RBC has been installed correctly as outlined in the user manual 180’ with the power plug facing in?!? Provide a photo of the RBC while inserted inside the unit and another outside showing the RBC battery connector. Provide another photo of the inside of the battery housing with a close up of the internal battery port.

 

As a sanity check flip the unit 180’ and insert the RBC until you feel it bottom out and click.

 

You may consider performing a brain dead reset as outlined here and report the outcome:

 

 https://www.se.com/us/en/faqs/FA158947/

 

Follow up by manually initiating a Self Test as outlined in page 8. Report how the unit behaves and whether it displays a self test pass on the unit (AND) via Power Chute.

 

 https://download.schneider-electric.com/files?p_enDocType=User+guide&p_File_Name=BU+UM+990-5813B+MN0...

 

Please confirm what version of Power Chute you’re using such as v1.4 vs v1.5.

 

Should all the above fail to resolve the issue contact APC Technical Support.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

TG_1
TG_1
Explorer

Posted: ‎2026-05-07 02:41 PM

In response to Teken
0 Likes
1
2045
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-05-07 02:41 PM

Hello,

 

I did what you suggested but it didn't fix the issue.

Firstly, I did assure the battery was installed (took pictures which I'll attach) and did a brain dead reset, then did a self test.

The test did not show any pass on the unit nor through power chute, but I will note one strange thing. Anytime I turn off the UPS, it shows the battery has reconnected, but if I were to turn on the UPS, it would disconnect. It would state the same in the event log of power chute.

As for power chute version, I made sure it was the latest. Checked for updates, but I am up to date.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: ‎2026-05-08 01:01 AM

In response to TG_1
0 Likes
0
2036
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-05-08 01:01 AM

Measure the DC voltage from the RBC and report the same here. Next reinstall the RBC and apply AC Mains and wait a minute.

 

Now remove AC Mains from the wall outlet.


My expectation is if the RBC is healthy and installed correctly the unit will continue to operate normally for several hours while nothing is attached to the rear outputs.

 

If the unit turns off immediately then either the RBC is bad, not installed correctly / damaged, unit is defective.

 

Report the outcome and insure the computer running PCSS is (NOT) connected. Please confirm the version of Power Chute (PCSS) and Windows OS.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

TG_1
TG_1
Explorer

Posted: ‎2026-05-08 07:13 PM

0 Likes
1
1907
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-05-08 07:13 PM

How can I measure DC voltage from the RBC (assuming you mean battery itself there) and how do I apply AC mains?

The OS I use is Windows 11, 23H2, and Power Chute version is 

1.5.0.301
Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: ‎2026-05-11 02:58 AM

In response to TG_1
0 Likes
0
1902
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-05-11 02:58 AM

Assuming the RBC was detected properly the DC voltage could known simply by looking at the LCD, Power Chute.

 

I gather since the RBC isn’t detected the DC voltage won’t be. 

As such you will need a multimeter set to DC Volts and simply place the meter probes on the positive / negative terminals to obtain the voltage and report the same here.

 

AC Mains = Power cord from the unit connected to wall AC outlet. You’ll simply disconnect the UPS power cord from the wall so the unit will run in battery only mode.

 

To simulate a grid down / lights out event . . . 

As stated the expected outcome is the unit will switch to battery only (Inverter Mode) once AC Mains has been removed from the wall outlet. 

In your case it might just turn off immediately as such there’s nothing else to do but contact APC Technical Support to initiate a RMA.

 


Given this is an Amazon purchase it’s probably easier to return the item as defective. Then just purchase another unit to see what happens and report the final outcome.

 

Questions Ask . . . 👍 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore