Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Battery Swelled up

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: Battery Swelled up
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2151
Teken
Teken
156
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
HobbyJeb
HobbyJeb
Explorer

Posted: ‎2026-09-20 11:29 AM

0 Likes
3
519
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-09-20 11:29 AM

Battery Swelled up

I have a BR1500G that was acting like it had battery issues.

It's one of those that use two CP1290's connected together.

It looks like it's one big battery, but it's actually 2.

I had a spare battery, so I went to swap it out, and had a tough time getting the existing battery pack out of the unit.  After I finally got it out, I noted one of the 2 batteries was swelled up on all sides.

My question is, what does this mean? Was the battery defective? Was it over charging?

Basically is my BR1500G unit ok? Or was it the reason the battery swelled up?

Attachments
Labels
  • Labels:
  • Home & Office - UPS & Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Teken
Teken
Champion

Posted: ‎2026-09-22 05:22 AM

0 Likes
2
517
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-09-22 05:22 AM

The answer depends upon many factors such as how old the UPS is and what firmware is present. As older units would not charge / float the RBC correctly over the long term.


It also depends upon what specific battery was installed in the unit as every cell has a different specification.

 

IE. Some cells have higher tolerances with respect to charging, float, operating temperature, cycles, resistance, and chemistry.

 

None of the photos you uploaded shows the actual battery maker.

 

As it relates to the cell being warped and swelled up. This indicates the system continued to charge the cell while ignoring it had failed.

 

Hence it’s imperative that you never rely on the Self Test as the final indicator as to a good / bad battery! ☝️

 

Only regular maintenance, inspection, and testing can affirm the RBC health.

 

If you had the proper equipment you would be able to measure the internal resistance of the cell. You would probably find the resistance to be extremely high or near a dead short.

 

Generally speaking the cell would show high internal resistance well beyond the manufactures specifications of 12 ~ 25 mOhms depending upon battery maker.

 

At this point your options are to simply replace the battery with a high quality (HR) cells such as CSB.

 

If the unit is more than five years old than it makes a lot more sense to replace the entire unit with a new one. As the operational service life of the current generation of APC Back-UPS is only 2-6 years.

 

NOTE: You must replace both cells that make up the RBC. If you only replace one cell you risk damaging the new cell once it’s been mated together.

 

Questions Ask . . . 👍

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Teken
Teken
Champion

Posted: ‎2026-09-22 05:22 AM

0 Likes
2
517
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-09-22 05:22 AM

The answer depends upon many factors such as how old the UPS is and what firmware is present. As older units would not charge / float the RBC correctly over the long term.


It also depends upon what specific battery was installed in the unit as every cell has a different specification.

 

IE. Some cells have higher tolerances with respect to charging, float, operating temperature, cycles, resistance, and chemistry.

 

None of the photos you uploaded shows the actual battery maker.

 

As it relates to the cell being warped and swelled up. This indicates the system continued to charge the cell while ignoring it had failed.

 

Hence it’s imperative that you never rely on the Self Test as the final indicator as to a good / bad battery! ☝️

 

Only regular maintenance, inspection, and testing can affirm the RBC health.

 

If you had the proper equipment you would be able to measure the internal resistance of the cell. You would probably find the resistance to be extremely high or near a dead short.

 

Generally speaking the cell would show high internal resistance well beyond the manufactures specifications of 12 ~ 25 mOhms depending upon battery maker.

 

At this point your options are to simply replace the battery with a high quality (HR) cells such as CSB.

 

If the unit is more than five years old than it makes a lot more sense to replace the entire unit with a new one. As the operational service life of the current generation of APC Back-UPS is only 2-6 years.

 

NOTE: You must replace both cells that make up the RBC. If you only replace one cell you risk damaging the new cell once it’s been mated together.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

HobbyJeb
HobbyJeb
Explorer

Posted: ‎2026-09-23 05:11 AM

In response to Teken
0 Likes
1
489
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-09-23 05:11 AM

Thank you so much for the information. The unit is a 2018 vintage. The battery back was from 2022. The battery brand is Vision CP1290. Obviously, I know I needed new batteries. But I did not know I would need a full unit. The initial question as to "why" did the batteries swell, is I did NOT want to put the unit back on line if it was overcharging, and they was a risk of damage, fire, etc.  Looks like I need to just get a brand new unit which will come with a new battery. During the life of this unit it has not had a large load on it at all. Thank you for your information.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: ‎2026-09-24 03:52 AM

In response to HobbyJeb
0 Likes
0
483
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2026-09-24 03:52 AM

For the benefit of you and others who would like more information you may review these APC FAQ:

 

Battery Life: https://www.se.com/us/en/faqs/FA158934/

 

Service Life: https://www.se.com/us/en/faqs/FAQ000265093/

 

Let us know what you decide to purchase when all is said and done. Lastly, if my previous replies provided the answer to your query please mark it as a solution to help the next person asking the same.

 

Rock On . . . 🤟

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore